I think that the only pipe allowed in a stairwell has to be associated with the 
stairwell IE: standpipe or piping supplying sprinklers for the stairwell.  We 
are on the 2015 IBC and I was flagged by the state reviewer for running a bulk 
pipe in the stairwell. Had to move it out into a closet.

From: Brian Harris <[email protected]>
Sent: Monday, January 15, 2024 1:03 PM
To: [email protected]
Subject: [Sprinklerforum] Backflow In Stairwell

Is there anything inherently wrong with putting the backflow & riser in a 
stairwell as along as all clearance requirements are met? I don't see anything 
in NFPA-13 and don't currently have access to the Building Code.

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://link.edgepilot.com/s/99ea33f9/J28ei1wxLESB5IcTaotl0w?u=http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935