The depth of engagement to form a leakproof connection is dependent on the pipe 
diameter and system pressure.

For general talking purposes per ASME B1.20.1, for NPT pipes, a 1.25" pipe is 
shown as having 11.5 threads per inch with the typical hand tightening 
limitation at 4.5 turns for a depth of 0.42 inches (<5 threads).  Past that to 
get to full engagement requires the use of a wrench.  Effective length of 
thread is shown as 0.707 inches.

So it's amazing that with only two threads for engagement it didn't come apart 
under the pressure test and stayed in place for 15 years. I would wonder if 
there are any other connections in a similar condition.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Wednesday, January 5, 2022 9:42 AM
To: [email protected]
Cc: Matt Grise <[email protected]>; Kevin Hall <[email protected]>
Subject: [EXTERNAL] RE: Thread connection holding on one thread only

If I recall from my book-learning days, there is a pretty well established 
minimum thread engagement that provides the full strength of a threaded 
connection. (maybe 3?). That may also only apply to bolts though.

Matt


-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Kevin Hall via Sprinklerforum
Sent: Wednesday, January 05, 2022 8:33 AM
To: [email protected]
Cc: Kevin Hall <[email protected]>
Subject: Re: Thread connection holding on one thread only

I do not believe one is sufficient. I recall a project where the specification 
limited the maximum number of exposed threads to 2 or 3. I'd have to do some 
research to find the product/installation standard that was referenced.


Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE

Coordinator, Engineering and Technical Services

American Fire Sprinkler Association

[email protected]

214-349-5971


On Wed, Jan 5, 2022 at 2:16 AM Dan Arbel via Sprinklerforum < 
[email protected]> wrote:

> Dear Forum Members
>
> I have a case where 1.25" NPT pipe nipple was connected to 1.25" BSP
> (as per British standard) pipe.
>
> Sprinkler System in interstitial space.
>
> There was only 2 threads engagement.
>
> After about 15 years somebody touched the a pipe and the connection
> disengaged.
>
> I would appreciated the members opinion on the allegation that even
> one thread engagement is sufficient providing sufficient strength.
>
> Dan Arbel
> Dan Arbel Risk Engineering Ltd
> Mail: [email protected]
> WEB SITE:
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> s*3a*2f*2fwww.riskmanage.com__;JSUl!!B5cixuoO7ltTeg!XkU8cH2TMBKLQ2ZlRo
> 1tisvmulk98nUEHNhgQ5Y2N2mjqKrtgbiQDgiMg-yghiPIMw$
> &c=E,1,rOBCJWaUiWX-Zi-j03j48v-ojODJ4zDjCTCn-XcTQUWSVSZzQRanv2vrdqlUogX
> nkOECEYOqMT2eMuzN6PVEfyuVyVF6Hoz4BiV1VyGvBRCcljgZH2U,&typo=1
> Mobile: +972-52-6611337
> Tel: +972-4-8243337
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> *3a*2f*2flists.firesprinkler__;JSUl!!B5cixuoO7ltTeg!XkU8cH2TMBKLQ2ZlRo
> 1tisvmulk98nUEHNhgQ5Y2N2mjqKrtgbiQDgiMg-zXS7SC2A$
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,RvPpy3ldS
> C8kzu280ouAOq2QKBzNGfMu7REiocN-XOdCtouKzXB4EaUtnbHa1UoPns-R2H1fzQj-fW-
> oIX3YW0Doh9ZL84fg3cNaQ0q1OQ,,&typo=1
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org&c=E,1,wikZY07kLJSV87o86Ivs1Jsxm4l75jKdQbbfbZ7tVZifvQRGY33Wh20_IAQ7wACFTF9yFLpxM-xqELTjxDST6UJ7dCl0WTqJP_LkvfP8qA,,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!XkU8cH2TMBKLQ2ZlRo1tisvmulk98nUEHNhgQ5Y2N2mjqKrtgbiQDgiMg-w4GyP2OA$
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!XkU8cH2TMBKLQ2ZlRo1tisvmulk98nUEHNhgQ5Y2N2mjqKrtgbiQDgiMg-w8lV3Y3w$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to