I do not believe one is sufficient. I recall a project where the
specification limited the maximum number of exposed threads to 2 or 3. I'd
have to do some research to find the product/installation standard that was
referenced.


Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE

Coordinator, Engineering and Technical Services

American Fire Sprinkler Association

[email protected]

214-349-5971


On Wed, Jan 5, 2022 at 2:16 AM Dan Arbel via Sprinklerforum <
[email protected]> wrote:

> Dear Forum Members
>
> I have a case where 1.25" NPT pipe nipple was connected to 1.25" BSP (as
> per British standard) pipe.
>
> Sprinkler System in interstitial space.
>
> There was only 2 threads engagement.
>
> After about 15 years somebody touched the a pipe and the connection
> disengaged.
>
> I would appreciated the members opinion on the allegation that even one
> thread engagement is sufficient providing sufficient strength.
>
> Dan Arbel
> Dan Arbel Risk Engineering Ltd
> Mail: [email protected]
> WEB SITE: www.riskmanage.com
> Mobile: +972-52-6611337
> Tel: +972-4-8243337