Henry and all - From Kevin Hall's earlier post:
That being said, the committee is currently working on language for the 2022
edition to clarify this requirement. This is the current language that can
be found in the first draft of the 2022 edition (see nfpa.org/14next to
look at it in TerraView)

8.3.2.4  Supervisory Air.
> 8.3.2.4.1  System piping shall be supervised.
> 8.3.2.4.2  Supervisory air shall be maintained at a minimum pressure of 7
> psi (0.5 bar).
> 8.3.2.4.2.1 Supervisory air pressures shall be permitted to be less than 7
> psi (0.5 bar) in accordance with the manufacturer's instructions.
> 8.3.2.4.3  Supervisory air shall be maintained at a maximum pressure of 20
> psi (1.4 bar).
> 8.3.2.4.3.1 Supervisory air for automatic dry and semiautomatic dry
> systems shall be permitted to exceed 20 psi (1.4 bar) in accordance with
> the manufacturer’s instructions for dry pipe and deluge valves.


This would apply to all dry standpipe systems (automatic, semi-automatic,
and manual). I would encourage everyone to review the change and submit a
public comment if you feel there needs to be further clarification.
Additionally, the entire document was restructured and several new
requirements pertaining to vertical standpipe system zones were added, so
again -- review and submit public comments.

The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the NFPA or its technical committees.
AFSA cannot provide design or consulting engineering services, and this
opinion should therefore not be considered, nor relied upon, as such.

*The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the **AFSA, and/or NFPA or its
technical committees.**AFSA cannot provide design or consulting engineering
services, and this opinion should therefore not be considered, nor relied
upon, as such.*

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*


*Have you visited **afsasafetyportal.com*
<http://r20.rs6.net/tn.jsp?f=001aRsnR7jftY-fvZKW05naPJY5Topx4PlFRvZQtGWitXyKVf2G6k4BeBlx6UwLkUYb00dniF8LXBzaUHL_KwWeUWmG96E4Ykd-tk4K60uhBwmxgMvJ5qwLXxzT9dNq90sXTaqwuzyA9n9-LJNRr18bPRrkmEp-EiqtsaKJ8Ih2Fto=&c=qVEeIWJyEKVNeftO0kwi9eE09kmGkw-_v4yJRgQjwzOGxHbe2u1dng==&ch=mNDt6Mp-ftKRmm_Zzhg8GVT09AdZ088YxZiWvF9d-T-5kX24hdFAMg==>
* yet? *

It's AFSA's member-only safety resource! This virtual library delivers the
accident-prevention and safety-related information you need to educate your
staff, help prevent claims, and create a safe work environment. Click here
<http://www.afsasafetyportal.com/> to learn more.





On Fri, Oct 22, 2021 at 7:48 AM Henry Fontana via Sprinklerforum <
[email protected]> wrote:

> I also believe, and please correct me if I am wrong.  The next edition of
> NFPA 14 will require dry standpipe to be monitored.  I am not sure of the
> requirements but I did hear it talked about in Texas at the convention.
>
> Henry Fontana
> Operations Manager (NYC)
> Johnson Controls Fire Protection
> 100 Lighting Way Secaucus, NJ 07094
> Cell: 201-210-9873
> [email protected]
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Mike Stossel via Sprinklerforum
> Sent: Friday, October 22, 2021 5:31 AM
> To: [email protected]
> Cc: Mike Stossel <[email protected]>; BRUCE VERHEI <
> [email protected]>; Moschello, Joe <[email protected]>
> Subject: RE: Supervised Air Manual Dry Standpipe
>
> In NYC we put a 2 1/2" FHV right next to the FDC with a pressure gauge.
> When they arrive they use the 2 1/2" FHV as a dump valve and can see the
> pressure that is left in the system at a single location.
>
> Mike Stossel SET
>
> 36 Barren Road
> East Stroudsburg, PA 18302
> Office: 973-670-2627
> [email protected]
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of BRUCE VERHEI via Sprinklerforum
> Sent: Friday, October 22, 2021 1:53 AM
> To: [email protected]
> Cc: BRUCE VERHEI <[email protected]>; Moschello, Joe <
> [email protected]>
> Subject: RE: Supervised Air Manual Dry Standpipe
>
> I’m not familiar with NYC’s requirement. I do know FF’s hate waiting for
> air to discharge and they get a constant stream of water. Even flat,
> ostensibly dry hose has a lot of air in it. I mean the lines between the
> engine and the FDC. Then there’s all the air in the standpipe. Pressurize
> the dry standpipe and the wait is longer.
>
> You all seen dry spk system trip test. Even after a decent stream there’s
> a little air spitting. Nozzle reaction from a sprinkler head? Meh. From a
> 200 gpm solid stream nozzle? Nozzle reaction matters, especially if it’s
> bouncing around. Keep at 25? I’d suppose amongst concerns is time to bleed
> line, and start to attack fire.
>
> Best.
>
> Bruce Verhei
>
> > On 10/21/2021 8:30 AM Moschello, Joe via Sprinklerforum <
> [email protected]> wrote:
> >
> >
> > It's an FDNY DOB local law amendment NYC made back in 2010 as a result
> of the Deutsche Bank fire in 2007 where 2 FF's died and 100 FF's were
> injured in a 7 alarm construction site fire.
> >
> > Joseph Moschello
> > Lieutenant/Fire Protection Subcode Official Summit Fire Department
> > 396 Broad Street
> > Summit, NJ 07901
> > 908-277-9360
> >
> >
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:[email protected]] On Behalf Of
> > Failla, Daniel via Sprinklerforum
> > Sent: Thursday, October 21, 2021 10:13 AM
> > To: [email protected]
> > Cc: Failla, Daniel
> > Subject: RE: Supervised Air Manual Dry Standpipe
> >
> > CAUTION: This email has originated from outside of the organization. Do
> not click links or open attachments unless you recognize the sender and
> know the content is safe.
> >
> >
> >
> > Good morning,
> >
> > Can someone please provide the actual NFPA 14, code reference for this
> requirement?
> >
> > Thank you for the assistance.
> >
> > Sincerely,
> >
> > Daniel S. Failla Jr. | Deputy Fire Marshal Charleston Fire Department
> > Fire Marshal Division
> > 2 George Street, Suite 3800 | Charleston, SC 29401
> > T:(843) 724-5960 | F:(843) 720-5857 |  [email protected]  |
> > https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.c
> > harleston-sc.gov%2Ffire&amp;data=04%7C01%7CHenry.Fontana%40jci.com%7C5
> > 87778e280a7459a0d8308d9953ebbce%7Ca1f1e2147ded45b681a19e8ae3459641%7C0
> > %7C0%7C637704919541740419%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAi
> > LCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=OXZH9y
> > vZqa3Rv4cOwFCWNGWvbuZ9Ow7LveZWk4uDtI0%3D&amp;reserved=0
> >
> >
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum <[email protected]>
> > On Behalf Of Henry Fontana via Sprinklerforum
> > Sent: Wednesday, October 20, 2021 10:47 PM
> > To: [email protected]
> > Cc: Henry Fontana <[email protected]>; cw bamford
> > <[email protected]>
> > Subject: Re: Supervised Air Manual Dry Standpipe
> >
> > CAUTION: This email originated outside of the City of Charleston. Do not
> click links or open attachments unless you recognize the sender and know
> the content is safe.
> >
> >
> > If you want the big east coast city rule. Here it is.
> >
> > “ Pressure shall be maintained in the standpipe and cross connections at
> all times and shall not exceed 25 psig (172 kPag) by utilizing nitrogen or
> an air compressor with an air dryer”
> >
> > Henry Fontana
> > Operations Manager (NYC)
> > Johnson Controls Fire Protection
> > 100 Lighting Way| St#402|Secaucus|NJ
> > 07094<x-apple-data-detectors://2/0>
> > Cell: 201-210-9873<tel:201-210-9873>
> > [email protected]<mailto:[email protected]>
> >
> >
> > On Oct 20, 2021, at 9:18 PM, cw bamford via Sprinklerforum <
> [email protected]> wrote:
> >
> > Can somebody on East Coast big city please respond?
> >
> > What about  using a PS15   Nominal System Pressure 15 psi  low pressure
> > switch on the dry system standpipe?
> >
> > On Wed, Oct 20, 2021 at 2:08 PM Mike Morey via Sprinklerforum <
> [email protected]> wrote:
> >
> > I don’t know that their is an express limit other than minimum 7psi.
> That said for safety reasons if you have an air source capable of anything
> close to that I’d come up with something to regulate it.  Doesn’t 13 limit
> air testing to 60 psi for safety?  Air pressure is much more dangerous than
> water as far as amount of energy stored.
> >
> >
> > Mike Morey
> >
> > CFPS 3229 • NICET S.E.T. 123677
> >
> > Project Manager • Fire Protection Group Shambaugh & Son, LP an EMCOR
> > Company
> >
> > 7614 Opportunity Drive • Fort Wayne, IN • 46825
> >
> > direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991 email
> > [email protected]
> >
> > [Image]
> >
> > ________________________________
> > From: Sprinklerforum <[email protected]>
> > on behalf of Matthew J Willis via Sprinklerforum <
> > [email protected]>
> > Sent: Wednesday, October 20, 2021 4:51:07 PM
> > To: [email protected] <
> > [email protected]>
> > Cc: Matthew J Willis <[email protected]>
> > Subject: Supervised Air Manual Dry Standpipe
> >
> >
> > BE ADVISED - This email originated outside EMCOR.
> >
> >
> >
> > Having an interesting discussion with a senior field man.
> >
> > He is concerned that some of the compressors pump to 125 +/-, and was
> asking about an AMD.
> >
> > I have searched, and also from a hands-on standpoint, do not believe one
> is required.
> >
> > It certainly is if we introduce a dry valve or deluge into the standpipe
> system, but then it gets a different name.
> >
> > NFPA 72 only mentions a 10 psi differential for supervisory circuits
> with air.
> >
> > Is an AMD required on this type standpipe?
> >
> > R/
> > Matt
> >
> > Matthew J. Willis
> > Design Manager / Code Compliance
> > 1530 Samco Road, Rapid City, SD 57702
> > Office-605.348.2342 /Direct-605.593.5063/Cell-605.391.2733
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furld
> > efense.com%2Fv3%2F__http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cg
> > i%2Fsprinklerforum-firesprinkler.org__%3B!!FaxH778!Me68QOsN00ZJIIRC_8s
> > OvWRaXf3Z8J8WpecLIJ7HV906Frsxib_TWTneXSPMdVXX%24&amp;data=04%7C01%7CHe
> > nry.Fontana%40jci.com%7Cda4d2db18f414ad7ae8808d99430a759%7Ca1f1e2147de
> > d45b681a19e8ae3459641%7C0%7C0%7C637703758955943749%7CUnknown%7CTWFpbGZ
> > sb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3
> > D%7C1000&amp;sdata=YMgUEsRs3z6IWEbhy7PLTDdeI5CvunD3si1Le6lKTpI%3D&amp;
> > reserved=0
> >
> > This message is for the named person's use only.  It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission.  If
> you receive this message in error, please  immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender.  You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> > .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> > mp;data=04%7C01%7CHenry.Fontana%40jci.com%7Cda4d2db18f414ad7ae8808d994
> > 30a759%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637703758955953706
> > %7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6I
> > k1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=rezWsdRD%2BbllHnICjEicRo2csMcBr
> > Ohdo3fjYAhWS4A%3D&amp;reserved=0
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> > .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> > mp;data=04%7C01%7CHenry.Fontana%40jci.com%7Cda4d2db18f414ad7ae8808d994
> > 30a759%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637703758955953706
> > %7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6I
> > k1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=rezWsdRD%2BbllHnICjEicRo2csMcBr
> > Ohdo3fjYAhWS4A%3D&amp;reserved=0
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> > .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkl&amp;dat
> > a=04%7C01%7CHenry.Fontana%40jci.com%7C587778e280a7459a0d8308d9953ebbce
> > %7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637704919541750376%7CUnk
> > nown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWw
> > iLCJXVCI6Mn0%3D%7C3000&amp;sdata=E8MpiuI9FP8YXamWYxdv%2FXaBwaPlNmYbTAF
> > MI2xzB8U%3D&amp;reserved=0 er.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> > .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkl&amp;dat
> > a=04%7C01%7CHenry.Fontana%40jci.com%7C587778e280a7459a0d8308d9953ebbce
> > %7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637704919541750376%7CUnk
> > nown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWw
> > iLCJXVCI6Mn0%3D%7C3000&amp;sdata=E8MpiuI9FP8YXamWYxdv%2FXaBwaPlNmYbTAF
> > MI2xzB8U%3D&amp;reserved=0 er.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> > .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkl&amp;dat
> > a=04%7C01%7CHenry.Fontana%40jci.com%7C587778e280a7459a0d8308d9953ebbce
> > %7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637704919541750376%7CUnk
> > nown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWw
> > iLCJXVCI6Mn0%3D%7C3000&amp;sdata=E8MpiuI9FP8YXamWYxdv%2FXaBwaPlNmYbTAF
> > MI2xzB8U%3D&amp;reserved=0
> > er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7CHenry.Fontana%40jci.com%7C587778e280a7459a0d8308d9953ebbce%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637704919541750376%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=nkd2YlShIYabcMDGUhN5jM50Pbz%2F0bS7DRCw%2BgOfk1M%3D&amp;reserved=0
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7CHenry.Fontana%40jci.com%7C587778e280a7459a0d8308d9953ebbce%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637704919541750376%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=nkd2YlShIYabcMDGUhN5jM50Pbz%2F0bS7DRCw%2BgOfk1M%3D&amp;reserved=0
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to