If you want the big east coast city rule. Here it is.

“ Pressure shall be maintained in the standpipe and cross connections at all 
times and shall not exceed 25 psig (172 kPag) by utilizing nitrogen or an air 
compressor with an air dryer”

Henry Fontana
Operations Manager (NYC)
Johnson Controls Fire Protection
100 Lighting Way| St#402|Secaucus|NJ 07094<x-apple-data-detectors://2/0>
Cell: 201-210-9873<tel:201-210-9873>
[email protected]<mailto:[email protected]>


On Oct 20, 2021, at 9:18 PM, cw bamford via Sprinklerforum 
<[email protected]> wrote:

Can somebody on East Coast big city please respond?

What about  using a PS15   Nominal System Pressure 15 psi  low pressure
switch on the dry system standpipe?

On Wed, Oct 20, 2021 at 2:08 PM Mike Morey via Sprinklerforum <
[email protected]> wrote:

I don’t know that their is an express limit other than minimum 7psi.  That
said for safety reasons if you have an air source capable of anything close
to that I’d come up with something to regulate it.  Doesn’t 13 limit air
testing to 60 psi for safety?  Air pressure is much more dangerous than
water as far as amount of energy stored.


Mike Morey

CFPS 3229 • NICET S.E.T. 123677

Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company

7614 Opportunity Drive • Fort Wayne, IN • 46825

direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]

[Image]

________________________________
From: Sprinklerforum <[email protected]> on
behalf of Matthew J Willis via Sprinklerforum <
[email protected]>
Sent: Wednesday, October 20, 2021 4:51:07 PM
To: [email protected] <
[email protected]>
Cc: Matthew J Willis <[email protected]>
Subject: Supervised Air Manual Dry Standpipe


BE ADVISED - This email originated outside EMCOR.



Having an interesting discussion with a senior field man.

He is concerned that some of the compressors pump to 125 +/-, and was
asking about an AMD.

I have searched, and also from a hands-on standpoint, do not believe one
is required.

It certainly is if we introduce a dry valve or deluge into the standpipe
system, but then it gets a different name.

NFPA 72 only mentions a 10 psi differential for supervisory circuits with
air.

Is an AMD required on this type standpipe?

R/
Matt

Matthew J. Willis
Design Manager / Code Compliance
1530 Samco Road, Rapid City, SD 57702
Office-605.348.2342 /Direct-605.593.5063/Cell-605.391.2733



_______________________________________________
Sprinklerforum mailing list
[email protected]

https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org__%3B!!FaxH778!Me68QOsN00ZJIIRC_8sOvWRaXf3Z8J8WpecLIJ7HV906Frsxib_TWTneXSPMdVXX%24&amp;data=04%7C01%7CHenry.Fontana%40jci.com%7Cda4d2db18f414ad7ae8808d99430a759%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637703758955943749%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=YMgUEsRs3z6IWEbhy7PLTDdeI5CvunD3si1Le6lKTpI%3D&amp;reserved=0

This message is for the named person's use only.  It may contain
confidential, proprietary or legally privileged information. No
confidentiality or privilege is waived or lost by any mistransmission.  If
you receive this message in error, please  immediately delete it and all
copies of it from your system, destroy any hard copies of it and notify the
sender.  You must not, directly or indirectly, use, disclose, distribute,
print, or copy any part of this message if you are not the intended
recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]

https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7CHenry.Fontana%40jci.com%7Cda4d2db18f414ad7ae8808d99430a759%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637703758955953706%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=rezWsdRD%2BbllHnICjEicRo2csMcBrOhdo3fjYAhWS4A%3D&amp;reserved=0

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7CHenry.Fontana%40jci.com%7Cda4d2db18f414ad7ae8808d99430a759%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C637703758955953706%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=rezWsdRD%2BbllHnICjEicRo2csMcBrOhdo3fjYAhWS4A%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to