8.15.7.1 boiled down says projections over 4' have to be sprinklered underneath 
unless they're the stuff outlined after, non combustible construction, or 
non-combustible facings with sprinklers inside or 1 of the three exceptions 
noted.

8.15.7.2 is a standalone, regardless of what you've had to do to this point, if 
combustibles are stored below and it's over 2' wide you must put in sprinklers. 
 Construction type isn't relevant.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of James Crawford via Sprinklerforum
Sent: Tuesday, October 5, 2021 7:41 PM
To: [email protected]
Cc: James Crawford <[email protected]>
Subject: NFPA #13 (2013) Exterior Projections 8.15.7

 
BE ADVISED - This email originated outside EMCOR. 
 

We have been discussing exterior projections in the office and with an AHJ on 
when sprinklers are required.

Section 
https://urldefense.com/v3/__http://8.15.7.1__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmht3zZzix$
  Unless the requirements of 
https://urldefense.com/v3/__http://8.15.7.2__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmhmDCYIS-$
 , 
https://urldefense.com/v3/__http://8.15.7.3__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmhrxqVNRf$
 . or 
https://urldefense.com/v3/__http://8.15.7.3__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmhrxqVNRf$
  are met, sprinklers shall be installed under exterior projections exceeding 
4'-0" in width.

Section 
https://urldefense.com/v3/__http://8.15.7.5__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmhveUcgnP$
  Sprinklers shall be installed under exterior projections greater than 2'-0" 
wide over areas where combustibles are stored.

Canopy is less than 4'-0" in width, No vehicle storage, non-combustible 
construction, not a corridor, so all items are met for 
https://urldefense.com/v3/__http://8.15.7.1__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmht3zZzix$
 , no sprinklers required.

But 
https://urldefense.com/v3/__http://8.15.7.5__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmhveUcgnP$
  seems to requires them because the canopy is over 2'-0"

Normally we worked on the assumption less than 4'-0" and non-combustible, no 
storage, no sprinklers required and the 2'-0" was for combustible construction, 
over 2'-0" you required sprotection.

What are we missing

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: 
https://urldefense.com/v3/__http://www.phaserfire.ca__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmhnQ8qaQ0$
 
<https://urldefense.com/v3/__http://www.phaserfire.ca__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmhnQ8qaQ0$
 >

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!Il4gkwPQ9UvJcoxmiGqOG67e7B6ukqsJLo_PohkUo8bPuswBi35_dDAmhuQIzuLO$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • NFPA #13... James Crawford via Sprinklerforum
    • Re:... Skyler Bilbo via Sprinklerforum
      • ... Jones, William - Fire Plans Examiner/Inspector via Sprinklerforum
        • ... Ken Wagoner via Sprinklerforum
          • ... Jones, William - Fire Plans Examiner/Inspector via Sprinklerforum
    • RE:... Mike Morey via Sprinklerforum

Reply via email to