Wrenches,
I'm sure i read a thread on this list about dealing with this, i've
searched but cannot find it. If anyone recalls the subject line, please
let me know.
We are dealing with setting up Enphase monitoring in neighborhoods with
other Enphase systems nearby and these 'other' systems are bei
directly to the Envoy, without need for
> a device scan. Not sure if this is worth it at the $450 retail price for
> the scanner, but if you can find one used, it might be. I recently was able
> to pick one up for about $250 used.
>
> Haven't yet had issues serious enough to requ
Al,
Not sure what you mean by "zero lot building"?
Can you design/construct a ballasted "wall/structure" at the back of the
array that could accommodate the inverters and load center on its
'out-of-the-sun' side. It could be a covered/vented cabinet.
Are micro-inverters an option? That would ma
The painter's elbow grease, of course.
benn
> On Jun 4, 2014, at 4:50 PM, Ray Walters wrote:
>
> I believe most manus approve mild dish soap and water. Geez, it would
> probably come off with just water and some elbow grease. :-)
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified P
To those who have used the suction cups to help with handling these mods, did
you purchase or rent the suction cups?
Any insights to share regarding your choices?
I have a 19kw vertical wall install coming up in a couple weeks.
benn
> On Jun 13, 2014, at 1:42 PM, Corey Shalanski
> wrote:
>
I wonder if the afci disturbances are caused (in part) at all from the wire
size used on the AC side in the inverter?
I just noticed the Sunny Tripower, which has a max AC output current of 14.5A,
states in the manual that it requires #8 or #6. ?
That is pretty big wire for 14A, don't ya think?
I believe CanadianSolar offers made in canada mods as well as their overseas
ones.
He province of Ontario has a FIT program (feed-in tariff) that has a certain
percentage of domestic content requirement, meaning if mfgrs want their
products used in Ontario then they must produce that produce
Kirk,
Yes they are.
http://www.canadiansolar.com/about_us.aspx?id=1
As i mentioned a few emails ago on this thread, several top PV BOS
manufacturers are manufacturing products in Canada, so that said products
may be used at least in Ontario, to satisfy Ontario's feed-in tariff's
domestic content r
Marco,
I've used SparQ micro-inverters a couple times. 2-3 years ago installed
about 8.5kW and last year about 2kW. Had a couple issues with the
communication hub, which they readily sent replacements for, no charge, but
no issues with the inverters themselves, yet.
Benn
On Mon, Jul 21, 2014 at
How high are you wanting to get the conduit (EMT?) off the roof?
I have been using Kinetic flashings and rails for mounting PV these days. Great
stuff.
There is a base that mounts directly onto the shingle and then a flashing goes
over it. The base that goes under the flashing has two holes for
We were given the go-ahead from a home builder whom we are doing lots of work
for, to cover attic vents on their roofs, if necessary. These are typically
about 4" off the roof.
I suspect covering plumbing vents may be ok as well but I'd be doubtful about
combustion vents.
Did you mean 1.5" or
says that we can cover them with modules,
> >>>>>> since the modules will be at least 4' above the roof. They have
> >>>>>> not yet provided any building code references to say that this
> >>>>>> is ok. Do any of you know if t
options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.or
James,
This looks like a pretty nice lanyard w/ shock-absorber, rope-grab and rope.
What type/style harness did he bring along?
Re: OSHA approved...great question. Prior to looking into it further I'd
suspect it falls in a "grey area".
Benn Kilburn
SkyFire Energy Inc.
780-
You can check with Conergy.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Feb 16, 2015, at 5:30 PM, Carl Adams wrote:
>
> I have a customer who insists he must have Yingli modules. So far I can't
> find them in distribution anywhere. Anyone have a source?
>
&
that do this and I'd also think that
you could buy/rent what you need to do it yourself, onsite.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Mar 30, 2015, at 10:03 AM, "frenergy" wrote:
>
> Fellow Wrenches,
>
> I just called Tap Plastics hoping the
ust double it over to make a tight fit?
Or make cuts in the corners...?
Thanks,
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Mar 30, 2015, at 10:26 AM, Allan Sindelar wrote:
>
> Bill,
> We have lined plywood boxes with either EPDM roofing membrane or vinyl pond
>
a great work-around to the overheating issue of having the gen inside.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Apr 3, 2015, at 9:11 AM, "d...@solarwork.com" wrote:
>
> At our high elevation installs the generator gets installed indoors with the
> balance of
Piss valve...aka yard hydrant. For the sake of Google searching ;)
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Apr 9, 2015, at 6:03 AM, Tump wrote:
>
> That is certainly one way of doing this but up here in the north country we
> install a "piss valve" a
Yeah, i jumped the gun on that one. A yard hydrant was the first thing
that came to mind but realized as soon as i hit send that they were
completely different.
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P
,
not sure if I'd spend the $ on a manufactured one?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Apr 29, 2015, at 3:31 PM, Lou Russo wrote:
>
> Wrenches,
>
> Anybody out there using the GEDA Solarlift (or any other lift for that
> matter)? If so what is your op
facturing costs within reason, then we just
may see them on the market sometime down the road.
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: ema
ooking for.
Thanks,
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: email] [image: facebook]
<https://www.facebook.com/SkyFireEnergy> [image:
, but it is a
minute amount of shading, so the loss is negligible.(?)
I would appreciate any feedback from any other module manufacturers on
this, if we have any on this list?
Benn
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton,
what was the proper
torque. (i've done this before, but it is something that needs to be self
"re-calibrated" often.
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5
Good points Ray.
I always warn the crews of galling and to avoid spinning the SS hardware to
fast. Another tip is to try to keep the SS hardware out of direct sun prior to
using it.
Kinetic tells me that their threaded hardware comes with a clear coat of
anti-seize.
Benn Kilburn
SkyFire
ery string is laid out so the end terminals are close together
and close to the inverter, but this isn't always the case.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Jun 29, 2015, at 10:28 AM, jarmo.venalai...@schneider-electric.com wrote:
>
> Hi:
>
> From the co
40degC. Their spec sheet
states it is good btwn -34.4degC to 149degC. So for me to even try it would
not be within the mfgr's specs :(
What products have you used? What did you like/dislike about them?
Cheers,
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFi
obably get some good ideas from them.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Jul 22, 2015, at 1:17 PM, Andrew Truitt wrote:
>
>
> Wrenches - What is your take on conduit across walkways on commercial
> rooftops?
>
>
>
>
>
> The 2012 IFC s
the
why's, how's and expected productions and so on... but i know the designer
and i'm pretty sure he already has a good idea what range the production
output of each different facing wall will fall in.
I can inquire if he has any articles or insight he would be willing to
share with t
Jason mentioned S-5 clamps... adding to that, it might be interesting to
have samples of many different racking system components. It would be
interesting to see all the different rail profiles and attachment methods
(racking system to roof and module to rail) that are out there.
*Benn Kilburn
eer for wind loading. Although they
may provide some info on their design and structural tolerances.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 5, 2015, at 2:49 PM, "Chris Daum" wrote:
>
> Wrenches:
>
> I'm trying to help a student who's doi
ak path I've ever seen is not a result of the flashing not being wide
enough but from not being tall enough, however, this is easily remedied by not
locating the base/flashing too high on the course/row of shingles and, if the
row is wavy/uneven, having to trim the shingle around the raises po
are better ways or at least improvements that can be made this
initial suggestion, but it's my day off, sort of ;)
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 7, 2015, at 4:00 PM, Wayne Irwin wrote:
>
> We have a customer with a ground mount system that would like
If you have attic access between the two roofs or separated arrays then install
a Soladeck at each array and run the interconnecting wires thru the attic. If
it is a DC circuit then Teck cable, or AC90 would be my choice of (armoured)
cable for running through the attic.
Benn Kilburn
SkyFire
Nope. I was trying to imagine what they would look like. It doesn't appear to
be a "typical" "channel nut" design. Maybe an inverted t-head bolt type?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 13, 2015, at 9:00 PM, "William Dorsett"
> w
the direct
shipped rails we are using.
Side note... 24 of 37 of the mystery rails are badly damaged, while only 5 of
the 33 rails we ordered were damaged.
Feel free to starts new topic on receiving damaged rails or other materials.
(Our replacement rails are on their way)
Benn Kilburn
SkyFire
of being set up, or have any useful information regarding
this then please share the contact info or link with me.
Sunny Regards,
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www
Ray,
Two quick suggestions...
1. Have you considered "leapfrogging" the battery connections? This would avoid
the long negative cable run and have both positive and negative runs closer to
the inverters.
2. Could you locate the Birdhouse inside a lockable box or cabinet?
Benn Kilbu
that there have been no leaks?
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: email] [image: facebook]
<https://www.facebook.com/SkyFireEnergy&g
ating around the edges.
What about using Lumos frameless modules?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 31, 2015, at 4:22 PM, William Miller wrote:
>
> Friends:
>
> I thought I had sent a message about this to the list but I believe not. My
> apolog
could be
sufficient, otherwise the separation could easily be a layer of dirt or
perhaps a pressure treated plank.
Good Luck.
*Benn Kilburn *
Partner, CSA Certified Solar Photovoltaic Systems Electrician, SkyFire
Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
M: 780-906-780
in Alberta. Similarly to what you described, the modules were mounted
almost completely flat and in that case the hail was reported to be at least
golf ball size as well.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Oct 8, 2015, at 11:47 PM, Allan Sindelar wrote:
>
> Wrenc
APS microinverters will work. Each YC500A handles two modules each and each
YC1000 handles 4 modules.
https://usa.apsystems.com/
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843
Looks like Sunmodo.
Only used it once... not a fan.
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: email] [image: facebook]
<ht
has to be manually
switched off (as per the manual) and then the switch for the SPS turned on for
it to operate and then flip both switches again when grid power is back on
before the inverter will operate in grid-connected mode again.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On
here...
so again, you need to rely on your professional judgement to use the proper
material and methods to secure any and all wires.
This is not a task to be given to someone without an eye for detail and
workmanship.
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Ener
opposite side from the "L-foot" attachment channel. It can
accommodate up to two RPVU90 wires.
I'll post a pic...
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.sk
considering the $ value of the potential kwh lost.
Our general consensus is that if removing the snow presents any challenge,
especially to safety, then it is best to just leave it to melt.
Not really an answer to your question... but another perspective to
consider.
*Benn Kilburn *
CSA Certif
cular "massive snow fall event" prior to this happening?
Thanks,
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: email] [image: f
Chris,
I've used these a few times. I would say they were successful.
What sort of questions do you have?
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenerg
Wrenches,
Of our residential installs, i would guess that at least 80% are done on
composite asphalt shingle roofs typically ranging from 13 to 33deg pitch.
The rest are made up of various metal roofs, cedar shake, rubber shingles,
concrete tile, etc...
Obviously, we require roof anchors for fall p
x27;t even see the sealant (which is
black and barely noticeable from the ground anyway)
I wish more homes around here used ridge vent caps. It would limit the number
of roof vents spread out across the roof.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Jan 8, 2016, at 9:02 AM, Dave
g PV systems or are simply not doing their job
properly and have no place inspecting anything.
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: email] [
So you just sit the frame of the module onto the black bar at the top of
the SP100?
It gravity alone holding the module in place?
Is mounting it onto the SP100 a one man job or do you need someone to put
it on there for you?
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician
Wrenches,
I received some modules lately (and it has happened in the past) that have
some degree of silicon on the front glass. It is usually either some
spatter or a smear of sorts.
These are from a distributor warehouse and in most cases i've seen the
modules removed directly from the manufactur
anyone interpret it
differently or know of another rule in the CEC that may be a work-around?
For the NEC'ers... i only have a copy of the 2011 NEC and haven't read it
cover to cover yet ;) but is there a similar rule in there regarding
storage battery voltage FOR dwellings?
Thanks
*Benn
roof
bracket. The name of it escapes me at the moment. Maybe FixT?
We are attaching to purlins which are 2"x6". I wouldn't think 1"x anything
would provide enough pull-out?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Apr 29, 2016, at 9:09 AM, August Goers wro
I dont recall the specific rule off the top of my head, but I'm sure Canadian
Electrical Code says that panelboards are specifically not allowed to be
installed in closets.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On May 30, 2016, at 6:08 PM, AE Solar wrote:
>
>
fully
decline and use whatever you wish, as long as it is done properly, and to code.
Not that here is anything wrong with metal battery boxes.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On May 31, 2016, at 11:40 AM, Dave Tedeyan wrote:
>
> Hi All,
>
> We have a local ins
ones would be nice for much larger
jobs. And i like that some have articulating sections that can flatten out
to run parallel with some roofs. But i've seen how much room they take up.
You need an empty van or trailer just to move the pieces themselves.
*Benn Kilburn *
CSA Certified Solar Ph
Wow!
How old is that array?
Might be a good idea to contact any other clients of yours in the area, to give
them a heads up and maybe push the rodent guard up-sell.
Sent from my iPhone
> On Jul 13, 2016, at 3:36 PM, Kirk Herander wrote:
>
>
> I got a call from a customer saying there wa
Din rail mounted terminal blocks Weidmuler WDU6 or WDU10, depending on the
wire size you are using.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 8, 2016, at 12:49 PM, Jason Szumlanski
> wrote:
>
> I'm looking to bring 8 Enphase 240V circuits in multiple
We've been using Polar Racking which is pretty light (without ballast).
...from my mobile
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 16, 2016, at 12:58 PM, Nik Ponzio, Building Energy
> wrote:
>
> Wrenchers,
>
> Ironridge just pulled plug on the
ng because they are exposed to
the elements.
We are in the process of designing a cover for them that would provide at least
as much protection as a module would.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 26, 2016, at 3:58 PM, Peter Giroux wrote:
>
> Andrew
>
>
ardly an issue, you might think?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 28, 2016, at 7:43 PM, jay wrote:
>
> Hi Bill and Benn,
>
> Those micros are rated nema 6, which is submersible rated.
>
> I”m curious which element/s they are referring
Nick,
Yes, there would be some direct sun exposure midday as well.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 28, 2016, at 10:27 PM, Nick Soleil wrote:
>
> Hi Wrenches.
>
>
> Yes, our product is NEMA 6, so is pretty robust once the DC and AC cables are
/edmonton.html
Midday sun on a north wall in Panama??? Now that is another story.
http://www.gaisma.com/en/location/panama.html
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 29, 2016, at 8:03 AM, Benn Kilburn wrote:
>
> Nick,
> Yes, there would be some direct sun exposure mi
Jerry,
Can you confirm that this was caused by a failure of the wire nut, itself, and
not due to user error (not properly stripping enough jacket, inserting even
length wires and sufficiently twisting on the wire nut)
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Sep 6, 2016, at 12
place.
I've always questioned the why wire nuts are cautioned against, especially
considering how many wire nuts are used in residential and commercial
jobs. I'm sure if there was a legit issue with them then insurance
companies would insist they not be used, such as aluminum wiring?
*Ben
August, et al,
Do you have any issues with crimping the fine wires that are typically on a
microinverter cable, to a coarse stranded or solid wire?
Or, do you know if there is an issue with using these crimps with fine stranded
wire?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Se
ement mechanial room along with the
house electrical panelboard.
We are looking for relay options to shut down the inverters when there is a
power interruption, before the generator kicks in. This could be a manual
reset.
What are some options you have seen/used for something like this?
Thanks,
what you are suggesting. Seems like it should
work.
Anyone care to poke some holes in this theory?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Sep 8, 2016, at 4:57 PM, jerrysgarage01 wrote:
>
>
> Wrenches
> Does not sound like there is an option to hard wire a shut
You guys should really cut one of those swelled up ones and share the photos
with us :)
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Sep 14, 2016, at 11:14 AM, Jerry Shafer wrote:
>
> The 190's had component issues which case them to balloon up
> Jerry
>
>
>
hence the need
for a way to shut down the inverters when the generator is running.
The SMM that was suggested sounds great, but I don't want our client to be a
guinea pig to see if it will work properly with a non-Generac generator.
Thanks,
Benn Kilburn
SkyFire Energy Inc.
780-906-7
Ya know whati'll echo Ron's comment. Check the leads. I was also
questioning an intermittent working Fluke...switched out the leads with one
that was working fine and found that one of the leads was the problem.
FWIW, I found the loose connection was where the wire went into the moulded
sect
It is direct burial rated, as per the Canadian Electrical Code, Table 19.
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
14515 – 121A Ave NW | Edmonton, AB | T5L 2T2
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: email] [image
Could you use one of those insulated Ilsco terminal blocks (sorry, don't have a
part number handy) to transition the #6 to short length of #8/10 then put your
#8/10 connector on the short piece?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Oct 6, 2016, at 4:22 PM, Corey Shalansk
ther suitable material so
not to scratch the glass.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Oct 13, 2016, at 4:20 PM, Darren Anderson wrote:
>
> In light of Hurricane Matthew and the loss of some of our PV systems on South
> Coast of Haiti (despite being designed for 120
the rails perfectly perpendicular? (keeping in
mind the length...32.8m (110')
Much Thanks,
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
14515 – 121A Ave NW | Edmonton, AB | T5L 2T2
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image:
case the days are getting shorter quicker around
here).
I agree that some use of a laser will probably work for us, I just thought
i'd throw this out there to see if anyone on this list has tackled
something similar and see if they have any insights to share.
Thanks,
*Benn Kilburn *
CSA
Chris,
It's s Kinetic rail and they have given the go-ahead.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Oct 18, 2016, at 4:41 AM, Chris Schaefer wrote:
>
> Hey Benn,
> Just curious as to who's rail you're using that is rated for such a steep
> angle?
were initially being terminated. The ones that did strip, did so with
noticeably less (hand torque) pressure than was applied to other terminals in
same inverters that snugged up just fine.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
___
List
Mark,
Not being familiar with NEC...are you still required to have rapid shutdown
when using microinverters?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Jan 30, 2017, at 10:25 AM, ma...@berkeleysolar.com wrote:
>
> Folks,
> Clearly residential rapid shutdown boxes will
effect on a systems annual production.
Here is a link to a great ongoing project that is assessing the effects of
module tilt and snow cover.
https://solaralberta.ca/content/alberta-solar-performance-data
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Feb 4, 2017, at
Wrenches,
I'm looking for a discontinued Fronius DataManager 1.0.
If anyone has one they'd part with or if you can suggest a possible source then
please reply to me off-list.
Much thanks,
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
__
Jason,
Contact Firestone yourself and tell them the roofers claim and if it's true
then get it in writing. If it's not, get it in writing.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Mar 22, 2017, at 7:40 PM, jerrysgarage01 wrote:
>
> Wrenches
> Our parent co
in, creates a lot of wasted label material.
Cheers,
Benn Kilburn
SkyFire Energy Inc.
780-906-7807___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wre
e mesh and J-hooks??? I'm not confidant that the j-hooks are robust enough
to last very long. We often have several on each install that the washer simply
will not hold tight.
(See the prior post below for some other suggestions)
Thanks!
Benn
SkyFire Energy
> On Jul 22, 2015
Brian,
I have used the SnapNRack and i do like their clips more than the J-hooks.
Thanks
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
14515 – 121A Ave NW | Edmonton, AB | T5L 2T2
P: 780-474-8992 | F: 888-405-5843
www.skyfireenergy.com
[image: email
Tom,
I commented on a few different products on a thread with a similar subject line
as this one, none of which would impede airflow significantly, IMO.
However they will require maintenance similar to cleaning out your
gutters/eavestroughs as wind-blown debris gets trapped along the upper rows
Jessie,
Dan with Exeltech just gave some good insight to cold weather inverter
capacitor tolerances in the thread "Electrolytic Caps vs. Thin Film Caps".
We had -26C here (Edmonton) today and the next couple of days are looking like
minimum -30C with windchill on top of that. This is p
boB,If this concept were to become a working option for the Classic, would the
modules have to be modified in any way? Why are the diodes not blocking the
reverse current?benn
DayStar Renewable Energy Inc. benn@daystarsolar.ca780-906-7807 HAVE A SUNNY DAY
Date: Mon, 16 Jan 2012 13:14:36 -
ng to the question...
Why did the glass shatter?
I don't want to just assume, but if there is no sign of impact, I'm wondering
if this could be a warranty issue? Frame expansion/contraction due to
temperature swing maybe?
Any experiences, thoughts or advice?
Module is a Sanyo HIT N215A
I was told a few days ago that a PV module will likely never produce the energy
it took to make it I bit my lip, disagreed and wished i could recall in
detail what i had read in one of the reports/articles i had read in the past on
this topic. From what i can remember it is about 2-3 yrs.
Never mind Jim, i found the attachment in your original post, under a different
'subject' title.Thanks,benn
DayStar Renewable Energy Inc. benn@daystarsolar.ca780-906-7807 HAVE A SUNNY DAY
From: b...@daystarsolar.ca
To: re-wrenches@lists.re-wrenches.org
Date: Thu, 15 Mar 2012 14:37:41 -0600
Jeremy,Is the inspector citing a specific code rule, necessitating a "listed"
battery enclosure? If no such code rule exists then he is likely unfamiliar
with the requirement and is shooting for 'something'.I have not seen or heard
of such an enclosure, but there are requirements for proper ve
Veto Pro Pac XL
Love it! Except the outside measuring tape holder needs a holding strap
otherwise the tape easily gets knocked off and if you're lucky if you see
when/where it happens.
There are different models with different capabilities, like a pocket for
a laptop, so to each their own.
benn
Wrenches,I have an off-grid client who is going to be connecting to the grid.
Since the system (~9 kW of PV and ~2400 Ah battery) is already well suited for
the loads, I am wondering about the necessity of an essential loads panelboard.
I'm not sure if I see the need since the battery is alre
ustry), at least this way you can referee. Good
Luck. db
Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44
Original Message ----
Subject: [RE-wrenches] Off-Grid to Grid-Connected -essential loads
From: benn kilbur
101 - 200 of 250 matches