I wonder if the afci disturbances are caused (in part) at all from the wire 
size used on the AC side in the inverter?
I just noticed the Sunny Tripower, which has a max AC output current of 14.5A, 
states in the manual that it requires #8 or #6. ? 
That is pretty big wire for 14A, don't ya think? What is the reasoning behind 
requiring such a large wire size?
With our 4 inverters being within 15' of the AC panelboard, voltage drop is not 
an issue and first thought is to go with #12. 
I suspect it has to do with the terminal block in the inverter. I checked and 
the #12 holds pretty tight, but that doesn't mean it was approved for #12. 
 
benn

> On Jun 25, 2014, at 10:46 AM, Steve Jefferson 
> <steve.jeffer...@sma-america.com> wrote:
> 
> Bill,
>  
> For the 6 years I have been with SMA, I (and Service as a whole) will always 
> advise against using wire nuts.
>  
> For the 13 years I have been in the solar industry, there are only a handful 
> of systems that I have installed that I used wire nuts.
>  
> There is no cover up. This has been in our manuals since the beginning of SMA.
>  
> The AFCI circuit is really sensitive to noise, therefore eliminating most 
> possibilities of issues that installers may come across is our goal.
> Wire nuts is a simple thing to not use, and there are many alternatives.
>  
> SMA America, LLC
> Steve Jefferson
> Service Line Supervisor
> 3925 Atherton Ave
> Rocklin, CA 95765 - 3714
> U.S.A.
> Tel:  +1 916 625 3185 (direct)
> Fax: +1 916 625 0871
> Mobile: +1 916 622 4253
> Email: steve.jeffer...@sma-america.com
> www.SMA-America.com
>  
> <image001.png>
>  
> This email and any attachments thereto may contain SMA America, LLC 
> confidential, privileged and private material for the sole use of the 
> intended recipient. Any review, copying, or distribution of this email (or 
> any attachments thereto) by others is strictly prohibited. If you are not the 
> intended recipient, please contact the sender immediately and permanently 
> delete the original and any copies of this email and any attachments thereto. 
> Thank you.
>  
>  
>  
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
> Behalf Of Bill Hoffer
> Sent: Wednesday, June 25, 2014 9:13 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] AFCI disturbances.
>  
> William
>  
> I agree with Bob-O, wire nuts are not the best choice for DC connections, for 
> all the reasons he mentioned,  but SMA claiming that wire nuts are causing 
> arc faults seems like a long shot at covering up an arc fault detection 
> nuisance tripping problem.  IMHO AFCI protection circuits are far from 
> perfected at this time and Inverters and optimizers have enough inherent 
> switching noise to cause nuisance tripping ( and there is ample evidence 
> supporting numerous inverter manufacturers having issues).  I believe we are 
> going to have similar growing pains as we did in the beginning of requiring 
> ARC Fault panel mounted breakers for bedrooms.  I have since replaced all my 
> Square D Arc Fault breakers due to failure, ie nuisance tripping.  I 
> understand the intent of adding arc fault to the 2014 code, but I am 
> concerned that as installers we will again become the guinea pigs in this 
> crazy experiment!  Don't gt me started on the fact that they are required to 
> only detect series faults and that opening the circuit on a  parallel fault 
> will likely make the arc increase rather than extinguish!  
>  
> Bill
>  
> 
> On Wed, Jun 25, 2014 at 8:40 AM, William Miller <will...@millersolar.com> 
> wrote:
> Richard:
> 
> Possibly. I think I prefer din mount connector blocks. However, if a wire nut 
> can arc internally a connector block might also. I am still wondering about 
> this concept.
> 
> William
> 
> Miller Solar
> 
> > On Jun 25, 2014, at 6:09 AM, richard.l.rat...@valley.net (Richard L Ratico) 
> > wrote:
> >
> > William,
> > Would UL listed crimp sleeves be an acceptable substitute where you would
> > otherwise use wirenuts?
> >
> > Dick Ratico
> > Solarwind Electric
> >
> >
> > --- You wrote:
> > Bob-O:
> >
> >
> >
> > When you say verboten, what does that mean?  Not kosher?  Frowned upon?
> > Disallowed by law???
> >
> >
> >
> > I am quite curious about this subject.  Here is what I have learned so far:
> >
> >
> >
> > This is a unique case where we are replacing 3 dead SMA U series inverters
> > with 2 US series inverters.  The U series seem to all be dying at about 12
> > to 14 years of age.  We have about a dozen of these to swap on our calendar
> > and expect more.  It may be that to do this right requires that we pull new
> > wire from the arrays.  This makes the job a lot more expensive.
> >
> >
> >
> > We have never used a wire nut on a PV lead until this project.  It's not
> > that we disapprove of wire nuts in general, it is because we know that if we
> > were to use them regularly we would eventually have failures and call backs.
> > We allow only one splice in a PV lead: between the cable provided by the
> > manufacturer of the module and a bulkhead mounted MC4 connector direct to
> > THWN in conduit
> > (http://millersolar.com/MillerSolar/practices/PV_wiring/PV_Cable_wiring/_PV_
> > Cable_Wiring.html).
> >
> >
> >
> > We checked the manufacturer's listing and the wire nuts are rated for 600
> > volts.  We do use wire nuts on AC circuits, such as switch and receptacle
> > circuits in a power room.
> >
> >
> >
> > A tech at SMA told me that wire nuts "arc internally to the spring" causing
> > the AFCI faults.  I am not aware of any process of "internal arcing."  To
> > me, arcing means, as per the dictionary definition: "a luminous bridge
> > formed in a gap between two electrodes."  The same tech told me to solder
> > the leads and apply shrink tubing.  I don't believe this is an approved
> > method.  By the way, we have spliced leads on both US series inverters and
> > only one is exhibiting AFCI disturbances.
> >
> >
> >
> > I do favor mounted terminal blocks, either screw or tubular type. I need to
> > check if the Amp model we stock are 600 volt rated.
> >
> >
> >
> > I was told by another representative from SMA that on a ground-mount system
> > it is legal to disable the AFCI protection.
> >
> >
> >
> > I will be troubleshooting this job tomorrow and I will let you all know what
> > I learn.
> >
> >
> >
> > William Miller
> > --- end of quote ---
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: 
> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
> 
>  
> --
> William Hoffer
> 161 SE Fourth Ave
> P.O. Box 1823
> White Salmon, WA 98672-1823
> suneng...@gmail.com
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to