Hello Lones here.
When an ac source is accepted by the inverter. The rely connects the ac input
directly to the ac output. The relay is (should be) protected by a 50 amp
breaker
If there is an ac load of 8KW or 33 ac amps the remaining current is available
to be used by the inverter for battery
Hello Dan and Wrenches
The FNDC can monitor up to 3 shunts. For the FNDC to give correct data all
current into and out of the batteries must go through a shunt.
The standard shunt is 500 amp 50mv. If three shunts are used it may be a good
idea to use one shunt for the two FM 60’s, the second shun
Hello All
The VFX/FX inverters does make use of the X240 transformer.
The transformer itself could act as a step up, a step down, or a load balancing
transformer.
Neither the FXR or the Radian inverters require the transformer as a load
balancing transformer.
The transformer can still be used in
Hello All
The Trace Battery Temp sensor has a 100 k negative coefficient.
The Outback Battery temp sensor has a 10 K negative coefficient.
The Outback temp senor will not work with Trace equipment.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Chris Schaefer
Hello All
And
Hello Jay
I just asked the tech support boss on this as I had no idea.
He has a test setup that allows him to switch individuals lines on the cat5
cables.
We can duplicate Jay's screen shot below by opening the some of the lines to
the cat 5 cable.
[cid:image003.jpg@01D47DA9.
Hello William
Sorry for the issues and troubles. I have forwarded your concerns on to the
responsible parties. I have requested additional bolts which once I receive
them I will send them on to you.
Take Care Sir
From: RE-wrenches On Behalf Of
William Miller
Sent: Saturday, December 1, 2018 1:
Hello Jay and All
Concerning module level shutdown.
Tigo has conducted testing and has validated the FM60/80 charge controllers
with their TS4 Module Platform
Imo's FireRaptor has been tested by OutBack and can be used successfully in
combination with FM60/80/100 the ICS Plus and the Skybox 5
: RE-wrenches
Cc: Lones Tuss
Subject: Re: [RE-wrenches] module level control for offgrid
Lones, Does Outback have any schematic details on the installation of these
devices with the Outback devices? Chris Warfel
On 2019-02-03 02:18, Lones Tuss wrote:
Hello Jay and All
Concerning module
Hello World
I apologize the link below is a dead link.
I will search out the proper link and post it as soon as I am able.
From: RE-wrenches On Behalf Of
Lones Tuss
Sent: Tuesday, February 5, 2019 9:46 AM
To: cwar...@entech-engineering.com; RE-wrenches
Subject: Re: [RE-wrenches] module
Hello
Below is a link to the OutBack rapid shutdown webinar.
https://www.youtube.com/watch?v=k0j9u-u7PRU&;
Sorry for my earlier misdirection.
From: cwar...@entech-engineering.com
Sent: Monday, February 4, 2019 5:49 AM
To: RE-wrenches
Cc: Lones Tuss
Subject: Re: [RE-wrenches] module l
Hello Drake
Yes replacing a single board in an FX is possible. In the case of a lightning
strike it may be advisable to replace all three boards as damage may not be
visible.
Take Care Sir
From: RE-wrenches On Behalf Of
drake.chamber...@redwoodalliance.org
Sent: Tuesday, February 5, 2019 2:52
Hello Jay
Well it seems that I can't leave well enough alone.
Below are some links I have found to the Tigo and IMO products concerning
module level shutdown.
Both have been tested with OutBack products.
I do not think Tigo or IMO have a presence on Wrenches and I know this is
gaining importanc
Hello All
Outback’s Product Warranty is not based or negated by the altitude of the
installation. Altitude ratings ensure full spec operation of the equipment up
to the stated elevation . As noted in several posts due to thinner air cooling
of equipment can be affected. Additional cooling may b
Hi Greg
Yes boards are available for the VFX3648. I would suggest calling into OutBack
Tech support. To get those repaired or replacement PCB’s sent to you.
Below is a link to the OutBack Website.
Technical support contact information is there.
http://www.outbackpower.com/about-outback/contact/con
Hi Andrew
OutBack now has AC Coupling for the Radian using frequency shift.
Below is a link to the Ac Coupling/ Frequency Shift App Note located on the
OutBack website.
http://www.outbackpower.com/downloads/documents/appnotes/acc_freq_app_note.pdf
You also state the client wants to "get solar" in
Hello Drake
This is from the App note
OutBack’s Frequency Shift AC Coupling is only employed in the Radian GS(A)
class inverter at this time. It requires a firmware upgrade on both the Radian
inverter and MATE3s system display and controller. The firmware is only
available by download on the Out
Hi Mac
If you want to contact me off line.
I could give it a look.
Shoot me your phone number
Lones
From: RE-wrenches On Behalf Of Mac
Lewis
Sent: Saturday, August 3, 2019 2:35 PM
To: RE-wrenches
Subject: [RE-wrenches] Pass-through state Dual FXR system
** [EXTERNAL EMAIL] - Please report any
Hi Mac
Thanks for the full site name I found it.
Here is the problem.
The Absorb and the Float timers are at Zero.
Setting a charge timer to Zero negates that charge stage.
So Float timer at zero no Float cycle
Absorb timer at Zero no Absorb cycle
This was first done in the Radian then passed on to
hope this helps.
Take Care All
From: William Miller
Sent: Tuesday, August 6, 2019 6:51 PM
To: RE-wrenches
Cc: Lones Tuss
Subject: Radian AC inputs
** [EXTERNAL EMAIL] - Please report any suspicious attachments, links, or
requests for sensitive information to the Help Desk
Hello all.
Here is some information regarding Module Level Shutdown and OutBack
http://www.outbackpower.com/products-mobile/safety-compliance/item/imo-fireraptor
Tech info:
http://www.outbackpower.com/resources/documents/product-documentation/item/imo-fireraptor-technical-documentation
* UL
Hello All
I will try to answer the original question then address the added concerns.
Question
Can I use an original Mate (rather than a Mate3) to set up basic programming
with a R series inverter, such as charger and LBCO settings?
No the FXRs require a Mate3(s) for programming.
Question
Can A
There are 2 concerns voiced below I will address each.
1 As to the location of OutBack
We are pleased to inform you that OutBack Power is moving our headquarters from
Arlington, WA to Phoenix, AZ. This move, to be completed by July 1, 2020, will
bring us physically closer to the majority of our
Hello All
In regards to this situation.
As an installer if you wish to have access to an new customer or an existing
Optics account.
The quickest and easiest method is to have the account owner invite you to view
their system.
They can also grant you full access.
This can be accomplished by click
Hi Dave
On the Mate
Hit Lock enter the Password (141)
Setting is highlighted press enter (the center button)
Scroll down to Mate3(s) enter
Scroll down to Data Logging
Using the wheel
Sd Card Data Logging Mode instead of disabled select [Excell]
The write interval is adjustable the default is 5 sec
Hi Jay
The FXR inverters do have the ability to run 2 legs of a 3phase system on a
single Mate3(s)and a Hub10.3
Inside the Hub10.3 is a header containing 5 jumpers. These jumpers can be
arranged so the inverters are set to a 3 phase
configuration.
Up to 9 inverters can be used per system, up to
Hi All
On OutBack inverters the EQ process is not temp comped.
The eq timer will not count down until the voltage set point is achieved.
You comment on the issue being somewhat intermittent is interesting.
Could there be a loose cable, bad crimp or corroded connection somewhere in the
system?
Sorr
Hello All
OutBack does offer a RSD solutions.
Please see the links below
http://www.outbackpower.com/products/safety-compliance/rapid-shutdown-kits
We also pair up with the FireRaptor RSD product
http://www.outbackpower.com/products/safety-compliance/fireraptor-rapid-shutdown
In addition the FM100
Hello All
1.I want to avoid AFCI unless mandated. Will this be defeated if I
don’t run the leads through the sense coil? (There is an AFCI and non-AFCI
version but I can’t seem to find the non-AFCI version anywhere.)
* Yes, you can bypass the AFCI by simply not running the PV
Hello, Dana.
OpticRe does allow you to set up email alerts, including low battery voltage
detected on inverter.
However, if the internet service onsite is not reliable, it will interrupt
communications between the MATE3 and OpticsRE.
Lones Tuss
Applications Engineer
OutBack Power Technologies
this is the case lack of fuel may be the gen stop reason.
Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun
Hello sir
You might also want to look into
http://www.mobilesolarpower.net/
I hope this helps
Take Care
Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com<h
.
I hope this helps.
Take Care
Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com<http://www.outbackpower.com/>
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrench
Hello Bill
Doing so presents no problem to the system or the Mate3.
Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com
-Original Message-
From: RE-wrenches [mailto:re
system can
only help.
Unfortunately I don’t think anyone is willing to offer a 100% guarantee of
protection.
Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com<h
might be a good idea to clear the Internal Data
Logs.
Press Lock
Enter the password 141
select Settings then System
Scroll down to
Clear Internal Data Log
Then choose yes.
This should get you up and running.
If it does not help email me directly for further assistance.
Take Care sir
Lones Tuss
will shut down when an update is performed.
Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com<http://www.outbackpower.com/>
From: RE-wrenches [mailto:re-wrenches-boun...@li
Hello
Radian stacking and power save levels are in the Radian Programming Manual
Starting page 36
http://www.outbackpower.com/downloads/documents/Make_the_Power/radian_8048a_4048a/gs_8048a_4048a_operator.pdf
The GS8048A can be stacked with a GS4048A inverter for a 12Kw system.
Lones Tuss
You said one status screen differed from the other. Just a shot of the home
screen on 3.15.3
Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com<http://www.outbackpower.
39 matches
Mail list logo