Re: [RE-wrenches] outback GSLC parts

2017-11-09 Thread Lones Tuss
this helps Take Care All Lones Tuss Applications Engineer OutBack Power Technologies 17825 59th Ave NE, Suite B, Arlington, WA 98223 360.618.4383 Office | 425.213.8794 Cell www.outbackpower.com -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On

Re: [RE-wrenches] Radian throughput power

2018-02-24 Thread Lones Tuss
Hello Lones here. When an ac source is accepted by the inverter. The rely connects the ac input directly to the ac output. The relay is (should be) protected by a 50 amp breaker If there is an ac load of 8KW or 33 ac amps the remaining current is available to be used by the inverter for battery

Re: [RE-wrenches] Outback OpticsRE and FlexNet DC shunts monitoring question

2018-03-19 Thread Lones Tuss
Hello Dan and Wrenches The FNDC can monitor up to 3 shunts. For the FNDC to give correct data all current into and out of the batteries must go through a shunt. The standard shunt is 500 amp 50mv. If three shunts are used it may be a good idea to use one shunt for the two FM 60’s, the second shun

Re: [RE-wrenches] Xfmr's job?

2018-07-08 Thread Lones Tuss
Hello All The VFX/FX inverters does make use of the X240 transformer. The transformer itself could act as a step up, a step down, or a load balancing transformer. Neither the FXR or the Radian inverters require the transformer as a load balancing transformer. The transformer can still be used in

Re: [RE-wrenches] battery temp sensors for older Trace/Xantrex inverters

2018-08-06 Thread Lones Tuss
Hello All The Trace Battery Temp sensor has a 100 k negative coefficient. The Outback Battery temp sensor has a 10 K negative coefficient. The Outback temp senor will not work with Trace equipment. From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Schaefer

Re: [RE-wrenches] mate 3s locking

2018-11-16 Thread Lones Tuss
Hello All And Hello Jay I just asked the tech support boss on this as I had no idea. He has a test setup that allows him to switch individuals lines on the cat5 cables. We can duplicate Jay's screen shot below by opening the some of the lines to the cat 5 cable. [cid:image003.jpg@01D47DA9.

Re: [RE-wrenches] Radian orders hardware problems

2018-12-03 Thread Lones Tuss
Hello William Sorry for the issues and troubles. I have forwarded your concerns on to the responsible parties. I have requested additional bolts which once I receive them I will send them on to you. Take Care Sir From: RE-wrenches On Behalf Of William Miller Sent: Saturday, December 1, 2018 1:

Re: [RE-wrenches] module level control for offgrid

2019-02-02 Thread Lones Tuss
Hello Jay and All Concerning module level shutdown. Tigo has conducted testing and has validated the FM60/80 charge controllers with their TS4 Module Platform Imo's FireRaptor has been tested by OutBack and can be used successfully in combination with FM60/80/100 the ICS Plus and the Skybox 5

Re: [RE-wrenches] module level control for offgrid

2019-02-05 Thread Lones Tuss
: RE-wrenches Cc: Lones Tuss Subject: Re: [RE-wrenches] module level control for offgrid Lones, Does Outback have any schematic details on the installation of these devices with the Outback devices? Chris Warfel On 2019-02-03 02:18, Lones Tuss wrote: Hello Jay and All Concerning module

Re: [RE-wrenches] module level control for offgrid

2019-02-05 Thread Lones Tuss
Hello World I apologize the link below is a dead link. I will search out the proper link and post it as soon as I am able. From: RE-wrenches On Behalf Of Lones Tuss Sent: Tuesday, February 5, 2019 9:46 AM To: cwar...@entech-engineering.com; RE-wrenches Subject: Re: [RE-wrenches] module

Re: [RE-wrenches] module level control for offgrid

2019-02-05 Thread Lones Tuss
Hello Below is a link to the OutBack rapid shutdown webinar. https://www.youtube.com/watch?v=k0j9u-u7PRU&; Sorry for my earlier misdirection. From: cwar...@entech-engineering.com Sent: Monday, February 4, 2019 5:49 AM To: RE-wrenches Cc: Lones Tuss Subject: Re: [RE-wrenches] module l

Re: [RE-wrenches] Outback Boards

2019-02-06 Thread Lones Tuss
Hello Drake Yes replacing a single board in an FX is possible. In the case of a lightning strike it may be advisable to replace all three boards as damage may not be visible. Take Care Sir From: RE-wrenches On Behalf Of drake.chamber...@redwoodalliance.org Sent: Tuesday, February 5, 2019 2:52

Re: [RE-wrenches] module level control for offgrid

2019-02-08 Thread Lones Tuss
Hello Jay Well it seems that I can't leave well enough alone. Below are some links I have found to the Tigo and IMO products concerning module level shutdown. Both have been tested with OutBack products. I do not think Tigo or IMO have a presence on Wrenches and I know this is gaining importanc

Re: [RE-wrenches] High altitude off-grid systems

2019-04-12 Thread Lones Tuss
Hello All Outback’s Product Warranty is not based or negated by the altitude of the installation. Altitude ratings ensure full spec operation of the equipment up to the stated elevation . As noted in several posts due to thinner air cooling of equipment can be affected. Additional cooling may b

Re: [RE-wrenches] Outback VFX 3648 tech support and parts

2019-04-15 Thread Lones Tuss
Hi Greg Yes boards are available for the VFX3648. I would suggest calling into OutBack Tech support. To get those repaired or replacement PCB’s sent to you. Below is a link to the OutBack Website. Technical support contact information is there. http://www.outbackpower.com/about-outback/contact/con

Re: [RE-wrenches] AC/DC coupling on conext

2019-06-24 Thread Lones Tuss
Hi Andrew OutBack now has AC Coupling for the Radian using frequency shift. Below is a link to the Ac Coupling/ Frequency Shift App Note located on the OutBack website. http://www.outbackpower.com/downloads/documents/appnotes/acc_freq_app_note.pdf You also state the client wants to "get solar" in

Re: [RE-wrenches] AC/DC coupling on conext

2019-06-25 Thread Lones Tuss
Hello Drake This is from the App note OutBack’s Frequency Shift AC Coupling is only employed in the Radian GS(A) class inverter at this time. It requires a firmware upgrade on both the Radian inverter and MATE3s system display and controller. The firmware is only available by download on the Out

Re: [RE-wrenches] Pass-through state Dual FXR system

2019-08-03 Thread Lones Tuss
Hi Mac If you want to contact me off line. I could give it a look. Shoot me your phone number Lones From: RE-wrenches On Behalf Of Mac Lewis Sent: Saturday, August 3, 2019 2:35 PM To: RE-wrenches Subject: [RE-wrenches] Pass-through state Dual FXR system ** [EXTERNAL EMAIL] - Please report any

Re: [RE-wrenches] Pass-through state Dual FXR system

2019-08-04 Thread Lones Tuss
Hi Mac Thanks for the full site name I found it. Here is the problem. The Absorb and the Float timers are at Zero. Setting a charge timer to Zero negates that charge stage. So Float timer at zero no Float cycle Absorb timer at Zero no Absorb cycle This was first done in the Radian then passed on to

Re: [RE-wrenches] Radian AC inputs

2019-08-08 Thread Lones Tuss
hope this helps. Take Care All From: William Miller Sent: Tuesday, August 6, 2019 6:51 PM To: RE-wrenches Cc: Lones Tuss Subject: Radian AC inputs ** [EXTERNAL EMAIL] - Please report any suspicious attachments, links, or requests for sensitive information to the Help Desk

Re: [RE-wrenches] Module-Level Shutdown for off grid systems

2019-09-27 Thread Lones Tuss
Hello all. Here is some information regarding Module Level Shutdown and OutBack http://www.outbackpower.com/products-mobile/safety-compliance/item/imo-fireraptor Tech info: http://www.outbackpower.com/resources/documents/product-documentation/item/imo-fireraptor-technical-documentation * UL

Re: [RE-wrenches] Outback VFX upgrade question

2020-03-09 Thread Lones Tuss
Hello All I will try to answer the original question then address the added concerns. Question Can I use an original Mate (rather than a Mate3) to set up basic programming with a R series inverter, such as charger and LBCO settings? No the FXRs require a Mate3(s) for programming. Question Can A

Re: [RE-wrenches] Optics systems ghost reprogramming

2020-03-17 Thread Lones Tuss
There are 2 concerns voiced below I will address each. 1 As to the location of OutBack We are pleased to inform you that OutBack Power is moving our headquarters from Arlington, WA to Phoenix, AZ. This move, to be completed by July 1, 2020, will bring us physically closer to the majority of our

Re: [RE-wrenches] Optics systems ghost reprogramming

2020-03-19 Thread Lones Tuss
Hello All In regards to this situation. As an installer if you wish to have access to an new customer or an existing Optics account. The quickest and easiest method is to have the account owner invite you to view their system. They can also grant you full access. This can be accomplished by click

Re: [RE-wrenches] Mate3 not saving data

2020-03-27 Thread Lones Tuss
Hi Dave On the Mate Hit Lock enter the Password (141) Setting is highlighted press enter (the center button) Scroll down to Mate3(s) enter Scroll down to Data Logging Using the wheel Sd Card Data Logging Mode instead of disabled select [Excell] The write interval is adjustable the default is 5 sec

Re: [RE-wrenches] magnum question

2020-04-02 Thread Lones Tuss
Hi Jay The FXR inverters do have the ability to run 2 legs of a 3phase system on a single Mate3(s)and a Hub10.3 Inside the Hub10.3 is a header containing 5 jumpers. These jumpers can be arranged so the inverters are set to a 3 phase configuration. Up to 9 inverters can be used per system, up to

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Lones Tuss
Hi All On OutBack inverters the EQ process is not temp comped. The eq timer will not count down until the voltage set point is achieved. You comment on the issue being somewhat intermittent is interesting. Could there be a loose cable, bad crimp or corroded connection somewhere in the system? Sorr

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-07 Thread Lones Tuss
Hello All OutBack does offer a RSD solutions. Please see the links below http://www.outbackpower.com/products/safety-compliance/rapid-shutdown-kits We also pair up with the FireRaptor RSD product http://www.outbackpower.com/products/safety-compliance/fireraptor-rapid-shutdown In addition the FM100

Re: [RE-wrenches] Outback FM100

2020-05-18 Thread Lones Tuss
Hello All 1.I want to avoid AFCI unless mandated. Will this be defeated if I don’t run the leads through the sense coil? (There is an AFCI and non-AFCI version but I can’t seem to find the non-AFCI version anywhere.) * Yes, you can bypass the AFCI by simply not running the PV

Re: [RE-wrenches] Remote monitor of an Outback system location

2015-12-21 Thread Lones Tuss
Hello, Dana. OpticRe does allow you to set up email alerts, including low battery voltage detected on inverter. However, if the internet service onsite is not reliable, it will interrupt communications between the MATE3 and OpticsRE. Lones Tuss Applications Engineer OutBack Power Technologies

Re: [RE-wrenches] Outback programing question

2016-05-09 Thread Lones Tuss
this is the case lack of fuel may be the gen stop reason. Lones Tuss Applications Engineer OutBack Power Technologies 17825 59th Ave NE, Suite B, Arlington, WA 98223 360.618.4383 Office | 425.213.8794 Cell www.outbackpower.com -Original Message- From: RE-wrenches [mailto:re-wrenches-boun

Re: [RE-wrenches] Mobile solar trailer

2016-05-09 Thread Lones Tuss
Hello sir You might also want to look into http://www.mobilesolarpower.net/ I hope this helps Take Care Lones Tuss Applications Engineer OutBack Power Technologies 17825 59th Ave NE, Suite B, Arlington, WA 98223 360.618.4383 Office | 425.213.8794 Cell www.outbackpower.com<h

Re: [RE-wrenches] Optics RE with two hubs.

2016-05-10 Thread Lones Tuss
. I hope this helps. Take Care Lones Tuss Applications Engineer OutBack Power Technologies 17825 59th Ave NE, Suite B, Arlington, WA 98223 360.618.4383 Office | 425.213.8794 Cell www.outbackpower.com<http://www.outbackpower.com/> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrench

Re: [RE-wrenches] Mate3

2016-07-13 Thread Lones Tuss
Hello Bill Doing so presents no problem to the system or the Mate3. Lones Tuss Applications Engineer OutBack Power Technologies 17825 59th Ave NE, Suite B, Arlington, WA 98223 360.618.4383 Office | 425.213.8794 Cell www.outbackpower.com -Original Message- From: RE-wrenches [mailto:re

Re: [RE-wrenches] Made three shut down

2016-08-29 Thread Lones Tuss
system can only help. Unfortunately I don’t think anyone is willing to offer a 100% guarantee of protection. Lones Tuss Applications Engineer OutBack Power Technologies 17825 59th Ave NE, Suite B, Arlington, WA 98223 360.618.4383 Office | 425.213.8794 Cell www.outbackpower.com<h

Re: [RE-wrenches] MATE3 restart

2016-11-04 Thread Lones Tuss
might be a good idea to clear the Internal Data Logs. Press Lock Enter the password 141 select Settings then System Scroll down to Clear Internal Data Log Then choose yes. This should get you up and running. If it does not help email me directly for further assistance. Take Care sir Lones Tuss

Re: [RE-wrenches] Firmware, Firmware, Firmaware was Outback Programming Ghost

2016-11-14 Thread Lones Tuss
will shut down when an update is performed. Lones Tuss Applications Engineer OutBack Power Technologies 17825 59th Ave NE, Suite B, Arlington, WA 98223 360.618.4383 Office | 425.213.8794 Cell www.outbackpower.com<http://www.outbackpower.com/> From: RE-wrenches [mailto:re-wrenches-boun...@li

Re: [RE-wrenches] Load Management vs Multiple Inverters and OutBack Radian vs Flexware systems

2016-12-16 Thread Lones Tuss
Hello Radian stacking and power save levels are in the Radian Programming Manual Starting page 36 http://www.outbackpower.com/downloads/documents/Make_the_Power/radian_8048a_4048a/gs_8048a_4048a_operator.pdf The GS8048A can be stacked with a GS4048A inverter for a 12Kw system. Lones Tuss

Re: [RE-wrenches] FXR , Mate 3, AGS and Must Run

2017-02-13 Thread Lones Tuss
You said one status screen differed from the other. Just a shot of the home screen on 3.15.3 Lones Tuss Applications Engineer OutBack Power Technologies 17825 59th Ave NE, Suite B, Arlington, WA 98223 360.618.4383 Office | 425.213.8794 Cell www.outbackpower.com<http://www.outbackpower.