OK, you wise guys.
I am upgrading my home off grid system from two FM 80s to two FM 100s.
The FM 80s were able to share the negative wire so you didn’t have to pull a
second negative wire.
I wired the FM 100 typical of how my FM 80s were wired with a number four
battery negative assuming and yes,
Hi All,
This will likely be an easy answer for this group.
I have a radian 4048 installation and am unable to get the programming
correct. What i want it to do is sell to the grid when the batteries are
full, but draw from the batteries at night or during cloudy periods until
hitting a set SOC o
Dana
I have always wired the PV negative all the way to the charge controller. That
way, the battery negative of the charge controller that happens to go to a
shunt has a proper representation of the current flow. I guess you could put
that PV negative at the same side of the shunt as the batt
As far as I know, the only mode that will export power is grid tied mode. If you want to sell during the day and Support in the evening, you can use the MATE3S (or via OpticsRE) function called Flex Time.Radian/FXR: FLEXtime Scheduleyoutu.beThank you,MaverickMaverick BrownOff-Grid Solar Commander s
Which Mate are you using? I know the FM100 is only compatible with the Mate
3s. If you are using a Mate 3, this mismatch could possibly be the cause of
these issues.
On Sat, Sep 7, 2024 at 7:25 PM Maverick Brown via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Dana
>
> I have always
Mate 3s
Dana Orzel
C: 208.721.7003
E- d...@solarwork.com
On Sep 7, 2024, at 7:07 PM, Chris Sparadeo via RE-wrenches
wrote:
Which Mate are you using? I know the FM100 is only compatible with the Mate 3s.
If you are using a Mate 3, this mismatch could possibly be the cause of these
issues.
O