[RE-wrenches] Multiple inverters

2019-02-25 Thread William Miller
Friends: I have an NEC code question on an upcoming project. It is a home that has an existing 8 kW ground-mounted grid-tied system. The owner wants to add another 10 kW of grid-tied PV. My question is about 705.12, point of connection. Specifically section (D)(1). That section states: *

Re: [RE-wrenches] Multiple inverters

2019-02-25 Thread Dave Tedeyan
Here in upstate NY, we have certainly had multiple inverter breakers land in the main panel. In a situation like yours, we have also left the old system as a load side connection, and then turned the new system in to a supply side connection so that the bus bar in the main panel is not overloaded.

Re: [RE-wrenches] Multiple inverters

2019-02-25 Thread Christopher Warfel
Just reading more slowly, each inverter has to be on its on separate disconnect means. You cannot put multiple inverters on the same disconnecting means unless there are individual disconnecting means upstream. On 2/25/2019 10:53 AM, William Miller wrote: Friends: I have an NEC code questio

Re: [RE-wrenches] Multiple inverters

2019-02-25 Thread Rebekah Hren
Hi Chris and William There was certainly no intention to mandate that all inverters connect to one OCPD/disconnect.But 705.12(B)(1) in 2017 clarifies that systems like Enphase could have multiple inverters on one breaker, certainly not that all inverters in a building have to be on breaker. If

Re: [RE-wrenches] Multiple inverters

2019-02-25 Thread Rebekah Hren
I should follow up to say that yes Chris is correct - each inverter does require its own equipment disconnects (AC and DC) per 690.15, but those can be connectors, like for Enphase, or any number of other things, as detailed in 690.15. If you try to keep system and equipment disconnect rules separa

Re: [RE-wrenches] Multiple inverters

2019-02-25 Thread Christopher Warfel
Yes, microinverters and now I would think other typologies will be included with module level disconnects becoming more common and I guess required. So, as long as you can disconnect each non microinverter individually, and microinverter strings by one disconnect, you should meeting the intent.