Friends:
I have an NEC code question on an upcoming project. It is a home that has an existing 8 kW ground-mounted grid-tied system. The owner wants to add another 10 kW of grid-tied PV. My question is about 705.12, point of connection. Specifically section (D)(1). That section states: *The source interconnection of one or more inverters installed in one system shall be made at a dedicated circuit breaker or fusible disconnecting means.* So if there are going to be two inverters on premise, do the outputs have to be aggregated to connect via one circuit breaker? This might be difficult to do as the exiting inverter is connected via a different sub-panel than the one that is planned to receive the new inverter output. This article <https://iaeimagazine.org/magazine/2014/01/16/load-side-pv-connections/> addresses the question. I would be very grateful if any of you can share any experience you might have in interpreting this section of the code. Thanks in advance. William
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org