Just reading more slowly, each inverter has to be on its on separate disconnect means. You cannot put multiple inverters on the same disconnecting means unless there are individual disconnecting means upstream.

On 2/25/2019 10:53 AM, William Miller wrote:

Friends:

I have an NEC code question on an upcoming project.  It is a home that has an existing 8 kW ground-mounted grid-tied system.  The owner wants to add another 10 kW of grid-tied PV.  My question is about 705.12, point of connection. Specifically section (D)(1).  That section states:

/The source interconnection of one or more inverters installed in one system shall be made at a dedicated circuit breaker or fusible disconnecting means./

So if there are going to be two inverters on premise, do the outputs have to be aggregated to connect via one circuit breaker?  This might be difficult to do as the exiting inverter is connected via a different sub-panel than the one that is planned to receive the new inverter output.

This article <https://iaeimagazine.org/magazine/2014/01/16/load-side-pv-connections/> addresses the question.

I would be very grateful if any of you can share any experience you might have in interpreting this section of the code.

Thanks in advance.

William


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to