Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-15 Thread Barton Churchill
Thanks Hans, we look forward to meeting you there! From: RE-wrenches on behalf of Kent Osterberg Sent: Monday, June 15, 2020 4:06 PM To: RE-wrenches Subject: Re: [RE-wrenches] White wire for DC- after ground fault breaker William, This is new for the 2017

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-15 Thread Kent Osterberg
William, This is new for the 2017 code: 2017 NEC 690.13(D) An equipment disconnecting means shall simultaneously disconnect all current carrying conductors that are not solidly grounded. Yet Schneider, Outback, Midnite, Magnum, and ... all still have a single PV wire disconnected at the charge

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-15 Thread Ray
It also seems like there should be some sort of wire marking to indicate functional grounding.  This code change makes sense, but it unleashes many new questions as well.  My vote is that is that PV is already current limited, so I don't see good reason to add fusing to the "functionally ground

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-15 Thread William Miller
Wrenches: Well now that the NFPA has acknowledged that GFDI protected circuits do not solidly ground the “grounded“ conductor, and we know they can’t be white in color, it begs the next question: Should these sort-of-grounded grounded conductors be switched and over-current protected? The

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-15 Thread Benn Kilburn
James, where is the CT located? If it’s in a panelboard/loadcenter, I understand that they are not “certified” to allow CT’s inside so the work-around is to pass the conductors thru a jbox before the panelboard and locate the CTs there. Benn Kilburn SkyFire Energy 780-906-7807 > On Jun 14

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-14 Thread Mac Lewis
James, I might open the ground fault breaker and show him with the ohmmeter that this is not a solidly grounded system. You are absolutely correct with this and if he gets tough just let him know you need him to sign off personally that you had informed him of this exact code reference. Or he ma

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-13 Thread Kent Osterberg
James, Here's the code reference: 2017 690.31(B)(1). Only solidly grounded PV system conductors shall be marked in accordance with 200.6 (white or gray). Kent Osterberg Blue Mountain Solar On 6/13/2020 5:56 PM, James Jarvis wrote: Brian, thank you very much. With your hint of "functional gro

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-13 Thread James Jarvis
Brian, thank you very much. With your hint of "functional ground" I can clearly see that I am not allowed to have those be white wires. Now time for me to incur the full wrath by daring to question the infinite wisdom of the "highly qualified individual" from the state. (all kinds of fun stuff fr

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-13 Thread Brian Mehalic
Change in 2017 to “functional grounded” was to clarify this - it’s not solid when it is thru a fuse or breaker than can be interrupted either in the event of a ground-fault or if the breaker is intentionally opened. 2017 makes it clear that there are very few solidly grounded systems (2 or less

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-12 Thread Jerry Shafer
James, Wrenches Traditionally we oy use black + and white - for a grounded PC system enen with RSD, Systems that are not grounded are red + and black - which can be confusing. White is associated with neutral and connected to earth, black hot and red hot and we always use either USE-ll or PV wire,

Re: [RE-wrenches] White wire for DC- after ground fault breaker

2020-06-12 Thread Dave Angelini Offgrid Solar
I take it he will not allow you to tape the wiring with white tape and put a warning sign on the JB? You have to do what he wants but I feel your pain. Good Luck! I would think a good electrician would measure first:) Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.st