Change in 2017 to “functional grounded” was to clarify this - it’s not solid 
when it is thru a fuse or breaker than can be interrupted either in the event 
of a ground-fault or if the breaker is intentionally opened. 2017 makes it 
clear that there are very few solidly grounded systems (2 or less PV source 
circuits, not touching a building the only case it is allowed). Pardon any 
incorrect language as I don’t have my code book, but I do think the 2017 NEC® 
makes it very clear, including in the definition of function grounded, that 
those conductors cannot be white or gray, regardless of if the system has a 
transformer-based or TL inverter or a CC with integrated or an external GF 
breaker/fuse. 

Brian

> On Jun 13, 2020, at 3:05 PM, greg egan <g...@remotepowerinc.com> wrote:
> 
> Jim,  Hope all is well with you and yours.  on white wires in circuits, In 3 
> ph. circuits you can get killed breaking into a neutral that's common to 
> other circuits.  One example, working on 277 lighting, you throw the breaker 
> or light switch on the one circuit you're working so the hot isn't hot 
> anymore.  It's standard practice for 3 ph. lighting ckts to share a neutral.  
> The white wire in your ckt is wire nutted in the j-box up in the ceiling to 
> the common neutrals.  Those neutrals are hot to ground when their respective 
> ckts are hot and they're carrying current.
> 
> Just thought it was worth mentioning on this list that there's no hard fast 
> rule that all white wires are dead.  It depends on the ckt.
> 
> Best,
> Greg Egan
> Remote Power Inc.
> 
> 
> Message: 11
> Date: Fri, 12 Jun 2020 15:17:19 -0500
> From: James Jarvis<j...@aprsworld.com>
> To: RE-wrenches<re-wrenches@lists.re-wrenches.org>
> Subject: [RE-wrenches] White wire for DC- after ground fault breaker
> Message-ID:
>    <CAFWEuYVMACXebixHtyRVYQ5Xnmaur=ugtv6etu5tnepm00n...@mail.gmail.com>
> Content-Type: text/plain; charset="utf-8"
> 
> Hello Wrenches,
> 
> I have an off-grid install where I was recently red-tagged by the state
> inspector. System is 24 volt with battery, Magnum inverters, some Magnum
> charge controllers, and a Morningstar charge controller. It is permitted
> under NEC 2017.
> 
> One of the inspectors issues was that my DC- conductors to the array /
> rapid shut down box are black color. He wants them to be white because he
> says they are solidly grounded. I reason that they are only solidly
> grounded when they are solidly grounded. As soon as the ground fault
> protection breaker opens, they are floating at array voltage. I think it is
> misleading and unsafe to have a white conductor that can have hundreds of
> volts of potential on it when a breaker trips.
> 
> I haven't dug into the code yet. I'm just working on the logic that one of
> my mentors put into me which is white wires better not have voltage
> potential on them. "That's the sort of sh*t that kills electricians" is
> what he repeatedly said ... and it's stuck with me.
> 
> Thoughts? I'm backed into the corner with the state, so I will be changing
> them to white even if it is unsafe ... unless I have some code backing.
> 
> <rant>Changing the wires to white will get interesting up on the roof. I
> wonder if they want me to cut off the black MC on the modules and replace
> them with white? This is mostly just an exercise in the State of Minnesota
> only wanting to know about and allow micro inverters. They brought in a
> state inspector from three hours away who kept repeating that he was a
> "highly qualified individual", but was unable to identify or recognize a
> charge controller. He kept referring to the charge controllers as
> inverters.</rant off>
> 
> Thanks,
> 
> -James Jarvis
> APRS World, LLC
> +1-507-454-2727
> http://www.aprsworld.com/
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20200612/5cd338c8/attachment-0001.html>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to