Dick: I do not desire to find building official who insist on a strict interpretation of the code, but it is a reality in our jurisdictions. We have to be pro-active and know the code better than they do, or we lose money when we are assessed corrective actions that increase our costs. Bruc

Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread Richard L Ratico
William, You may well find inspectors and others who will agree with you on this. I remain firmly unconvinced. Yes, the code may be taken literally. . . . .and also, sometimes, be taken out of context. I believe you are doing that here. It is impossible to use words in such an airtight manner that

[RE-wrenches] down-sizing main breaker

2009-08-02 Thread Nick Vida
Dick, I think im in William's camp and you may have gathered from my earlier post in this thread. The actual logic and safety concerned in reality and practice may be totally true and valid from your perspective (and in reality), however the wording of the code allows for you to get a out of th

Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread William Miller
Dick: Regardless, the code requires that all portions of the circuit accommodate the sum of the over current devices supplying the circuit. The citation is below. I am not defending the code, I am telling you what I believe it says. You don't need to sell your view point to me, you need to

Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread Richard L Ratico
ny) scenario. So why would you have to increase >conductor size? > >Thanks, Allan > >-- >From: re-wrenches-boun...@lists.re-wrenches.org >[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller >Sent: Saturday, August 01, 2009 11:13 PM >To: RE-wr

Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread William Miller
, August 01, 2009 11:13 PM To: RE-wrenches Subject: Re: [RE-wrenches] down-sizing main breaker Allan: I whipped up three drawings that indicate three overload scenarios possible with incorrectly sized distribution equipment. They are on our web site at: http://millersolar.com/case_studies

Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread Allan Sindelar
On Behalf Of William Miller Sent: Saturday, August 01, 2009 11:13 PM To: RE-wrenches Subject: Re: [RE-wrenches] down-sizing main breaker Allan: I whipped up three drawings that indicate three overload scenarios possible with incorrectly sized distribution equipment. They are on our web site at: ht

Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread William Miller
Sent: Saturday, August 01, 2009 6:11 PM To: RE-wrenches Subject: Re: [RE-wrenches] down-sizing main breaker Dick: Your logic is correct but incomplete. Consider it like this: The buss bars in the service panel can handle 100 amps (they are rated for that amount). The main breaker feed

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread Richard L Ratico
Brian, William & Allan, Perhaps I've misunderstand the specific distribution equipment involved. I have assumed the main SERVICE consisted of a meter and single, 100 amp main breaker, as a combo unit or as separate enclosures, but with no busbar provision for additional breakers there at the pedes

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread Allan Sindelar
: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Saturday, August 01, 2009 6:11 PM To: RE-wrenches Subject: Re: [RE-wrenches] down-sizing main breaker Dick: Your logic is correct but incomplete. Consider it like this:

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread William Miller
Dick: Your logic is correct but incomplete. Consider it like this: The buss bars in the service panel can handle 100 amps (they are rated for that amount). The main breaker feeds 100 amps into that buss, maximizing it's capabilities. If you feed an additional 40 amps into that buss bar, yo

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread Richard L Ratico
William, I don't know if I've solved Brian's dilemma yet either. But, with regard to your example below, if the 100 amp meter main is accepting 20 amps, or even all of the 50 amps of PV, that would mean that the house, at that moment, presented no load at all, and that all the PV would be backfeed

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread William Miller
Dick: In my last post, I meant to cite 690.64(B). William ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread William Miller
Dick: I don't believe you have solved Brian's dilemma yet. It is my understanding that if one is going to install a load side tape, the back feed calculations need to work for every link of the distribution system upstream to the meter. In the scenario you suggest, that will not be the case

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread Kurt Albershardt
On 8/1/09 11:08 , William Miller wrote: Our best solution would be to install a 200 amp meter panel with a 100 amp breaker. The application is an agricultural based residence, so based on how one interpreted this, the back feed allowance would be either 100 amps or 120 amps, enough to cover ou

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread Richard L Ratico
William, I stand corrected. Thank you. This is not a supply side tap. I should have said it was a tap on the supply side of the panelboard main breaker. That said , I think it works and meets code, provided the conductors spliced to the feeder are properly sized. The panelboard busbar is protect

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread William Miller
Dick: I disagree with your plan. To qualify as a supply side tap, the tap needs to be on the supply side of the main disconnecting means, If I understand your plan correctly, your suggestion does not achieve this. Bruce: Your inspector is correct -- not in his interpretation of the code --

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread Richard L Ratico
Hi Nick, I may not be entirely clear on your situation, but I interpret 690.64(B)(2), literally or otherwise, as meaning a busbar, or a conductor used in the SAME WAY as a busbar, rather than as a feeder. By that, I mean the conductor would have the solar breaker's energy tapped into it in such a

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread Richard L Ratico
Bruce, This sounds like a good situation for a line side tap, rather than going to all the work of replacing the panel. Turn off main breaker at the pedestal, no need to touch the meter. At the house, pull the feeder out of the panel. Put it into a proper new junction box. Splice one set of ne

[RE-wrenches] down-sizing main breaker

2009-07-31 Thread Nick Vida
if you read 690.64b it does mention both the buss rating AND conductors. for years and years I thought it was just for the buss rating until i got called recently for the feeders being undersized and unable to accommodate the solar within 120%. I see a lot of sentiments in this thread that it is

[RE-wrenches] down-sizing main breaker

2009-07-31 Thread Nick Vida
if you read 690.64b it does mention both the buss rating AND conductors. for years and years I thought it was just for the buss rating until i got called recently for the feeders being undersized and unable to accommodate the solar within 120%. I see a lot of sentiments in this thread that it is

Re: [RE-wrenches] down-sizing main breaker

2009-07-31 Thread Bill Brooks
-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mendocino Solar Service Sent: Friday, July 31, 2009 9:57 AM To: RE-wrenches Subject: [RE-wrenches] down-sizing main breaker Hi Folks, Can anyone provide code reference or advice on this question? Our customer has 100 amp service at the meter

Re: [RE-wrenches] down-sizing main breaker

2009-07-31 Thread Matt Lafferty
ject: [RE-wrenches] down-sizing main breaker Hi Folks, Can anyone provide code reference or advice on this question? Our customer has 100 amp service at the meter pedestal, 100 amp main breaker feeding 200 foot underground run to a 100 amp panel at the house. We need to land a 40 amp breake

Re: [RE-wrenches] down-sizing main breaker

2009-07-31 Thread Mark Frye
sts.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mendocino Solar Service Sent: Friday, July 31, 2009 9:57 AM To: RE-wrenches Subject: [RE-wrenches] down-sizing main breaker Hi Folks, Can anyone provide code reference or advice on this question? Our customer has 100 amp s

[RE-wrenches] down-sizing main breaker

2009-07-31 Thread Mendocino Solar Service
Hi Folks, Can anyone provide code reference or advice on this question? Our customer has 100 amp service at the meter pedestal, 100 amp main breaker feeding 200 foot underground run to a 100 amp panel at the house. We need to land a 40 amp breaker, so are proposing to replace main panel at