Dick:

Regardless, the code requires that all portions of the circuit accommodate the sum of the over current devices supplying the circuit. The citation is below.

I am not defending the code, I am telling you what I believe it says. You don't need to sell your view point to me, you need to sell it your local building officials. My goal is to interpret the code such that my designs are unassailable by building officials. I don't want unpleasant surprises after I have signed a contract and begun work for a fixed price.

690.64(B)(2) The sum of the ampere ratings of overcurrent devices in circuits supplying power to a busbar or conductor shall not exceed the rating of the busbar or conductor. (2002).

William Miller


At 01:15 PM 8/2/2009, you wrote:
Wlliam,

If there were to be a short circuit in the feeder or the main service panel (
the one with no extra breaker spaces ), the solar's maximum 50 amp contribution would be about the last thing to be concerned about. A short is going to result
in perhaps 1000s of amps coming from the grid into the short. The service 100
amp breaker will trip immediately and clear the fault. The inverter will lose
the grid and drop offline. End of story.

Dick

--- You wrote:
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to