Behalf Of Chris Worcester
Sent: Thursday, August 11, 2016 10:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
When we have the Enphase 240 VAC trunk line branching in two directions we
use these 300V rated Alumiconn 3 port connectors, to make them
be for someone else to confirm.
>
> Glenn
> --
> From: Ray Walters
> Sent: 8/11/2016 12:55
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
>
> So this may be a dumb question, but I'm assuming wire nu
Glenn
-Original Message-
From: "Ray Walters"
Sent: 8/11/2016 12:55
To: "RE-wrenches"
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
So this may be a dumb question, but I'm assuming wire nuts are not
suitable for Fine strand wire? I agree t
PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
How about these?
https://idealind.com/us/en/products/wire-termination/set-screw-connectors/se
t-screw-connectors/set-screw-wire-connectors.aspx
Jeremy Rodriguez
Solar Installation And Design Expert
All
ady.
Best,
August
Luminalt
From: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>]
On Behalf Of Glenn Burt
Sent: Wednesday, August 10, 2016 8:44 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pass through/transition box for
es
*Subject:* Re: [RE-wrenches] Pass through/transition box for Enphase
The Ideal website for the Buchanan splice has a link to the UL listing
for the product. It does not list it for use with anything other than
standard stranded conductors.
If it is not part of the listing, it is not approved f
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Glenn Burt
*Sent:* Wednesday, August 10, 2016 8:44 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Pass through/transition box for Enphase
The Ideal website for the Buchanan splice has a link to the UL listing for
the product. It does
the NEC says, and what the UL listing says and the UL
specification for their listing says.
-Original Message-
From: "Brian Teitelbaum"
Sent: 8/10/2016 22:48
To: "RE-wrenches"
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
Jeremy,
Without di
] Pass through/transition box for Enphase
How about these?
https://idealind.com/us/en/products/wire-termination/set-screw-connectors/set-screw-connectors/set-screw-wire-connectors.aspx
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
How about these?
https://idealind.com/us/en/products/wire-termination/set-screw-connectors/set-screw-connectors/set-screw-wire-connectors.aspx
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorth
Mike Nelson
Sent: Wednesday, August 10, 2016 7:07 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
I don't know what they're listed for but I know that they are very effective.
Michael D Nelson
MD Electric & Solar, Inc.
707-684-0064 mobile
listed to be used with greater stranded conductors than class B
> or C (7 or19)?
> From: Carl Adams
> Sent: 8/10/2016 17:37
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
>
> I second Mike Nelson's approach, simple, easily ins
But are they listed to be used with greater stranded conductors than class B or
C (7 or19)?
-Original Message-
From: "Carl Adams"
Sent: 8/10/2016 17:37
To: "RE-wrenches"
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
I second Mike Nelso
ke Polaris are also not listed for use with
> fine stranded conductors. NSI has a special Polaris terminal that is grey
> that is listed for use with fine stranding, and can safely be used.
> I saw a few incorrect Polaris blocks pulled from an installation recently
> that had melted.
has a special Polaris terminal that is grey
>>> that is listed for use with fine stranding, and can safely be used.
>>> I saw a few incorrect Polaris blocks pulled from an installation recently
>>> that had melted...
>>> From: Michael Morningstar
>>> Sent
tallation
recently that had melted...
From: Michael Morningstar <mailto:mjmornings...@gmail.com>
Sent: 8/8/2016 15:23
To: RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches]
installation recently
> that had melted...
> From: Michael Morningstar
> Sent: 8/8/2016 15:23
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
>
> I use DIN rail mount "feed through" terminal blocks. There's all kinds an
.
I saw a few incorrect Polaris blocks pulled from an installation recently that
had melted...
-Original Message-
From: "Michael Morningstar"
Sent: 8/8/2016 15:23
To: "RE-wrenches"
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
I use DIN rail
Din rail mounted terminal blocks Weidmuler WDU6 or WDU10, depending on the
wire size you are using.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 8, 2016, at 12:49 PM, Jason Szumlanski
> wrote:
>
> I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an
> enc
Soladeck.
Michael D Nelson
MD Electric & Solar, Inc.
707-684-0064 mobile
707-884-1862 office
www.mdelectricsolar.com
Sent from my iPhone
> On Aug 8, 2016, at 8:49 AM, Jason Szumlanski
> wrote:
>
> I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an
> enclosure inside the
I use DIN rail mount "feed through" terminal blocks. There's all kinds and you
will find some constructed such that no live parts exposed.
Michael
> On Aug 8, 2016, at 8:49 AM, Jason Szumlanski
> wrote:
>
> I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an
> enclosure
I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an
enclosure inside the attic where I can transition to Romex. I'd rather use
some kind of rail mounted terminals in an enclosure or something rather
than making splices in a generic j-box. I'm not looking to combine circuits
-