Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread Glenn Burt
Behalf Of Chris Worcester Sent: Thursday, August 11, 2016 10:33 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Pass through/transition box for Enphase When we have the Enphase 240 VAC trunk line branching in two directions we use these 300V rated Alumiconn 3 port connectors, to make them

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread Jerry Shafer
be for someone else to confirm. > > Glenn > -- > From: Ray Walters > Sent: ‎8/‎11/‎2016 12:55 > To: RE-wrenches > Subject: Re: [RE-wrenches] Pass through/transition box for Enphase > > So this may be a dumb question, but I'm assuming wire nu

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread Glenn Burt
Glenn -Original Message- From: "Ray Walters" Sent: ‎8/‎11/‎2016 12:55 To: "RE-wrenches" Subject: Re: [RE-wrenches] Pass through/transition box for Enphase So this may be a dumb question, but I'm assuming wire nuts are not suitable for Fine strand wire? I agree t

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread Chris Worcester
PM To: RE-wrenches Subject: Re: [RE-wrenches] Pass through/transition box for Enphase How about these? https://idealind.com/us/en/products/wire-termination/set-screw-connectors/se t-screw-connectors/set-screw-wire-connectors.aspx Jeremy Rodriguez Solar Installation And Design Expert All

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread Nick Soleil
ady. Best, August Luminalt From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Glenn Burt Sent: Wednesday, August 10, 2016 8:44 PM To: RE-wrenches Subject: Re: [RE-wrenches] Pass through/transition box for

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread Ray Walters
es *Subject:* Re: [RE-wrenches] Pass through/transition box for Enphase The Ideal website for the Buchanan splice has a link to the UL listing for the product. It does not list it for use with anything other than standard stranded conductors. If it is not part of the listing, it is not approved f

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread August Goers
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Glenn Burt *Sent:* Wednesday, August 10, 2016 8:44 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Pass through/transition box for Enphase The Ideal website for the Buchanan splice has a link to the UL listing for the product. It does

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread Glenn Burt
the NEC says, and what the UL listing says and the UL specification for their listing says. -Original Message- From: "Brian Teitelbaum" Sent: ‎8/‎10/‎2016 22:48 To: "RE-wrenches" Subject: Re: [RE-wrenches] Pass through/transition box for Enphase Jeremy, Without di

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-10 Thread Brian Teitelbaum
] Pass through/transition box for Enphase How about these? https://idealind.com/us/en/products/wire-termination/set-screw-connectors/set-screw-connectors/set-screw-wire-connectors.aspx Jeremy Rodriguez Solar Installation And Design Expert All Solar, Inc. 1463 M St Penrose Colorado 81240

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-10 Thread Jeremy Rodriguez
How about these? https://idealind.com/us/en/products/wire-termination/set-screw-connectors/set-screw-connectors/set-screw-wire-connectors.aspx Jeremy Rodriguez Solar Installation And Design Expert All Solar, Inc. 1463 M St Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorth

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-10 Thread Glenn Burt
Mike Nelson Sent: Wednesday, August 10, 2016 7:07 PM To: RE-wrenches Subject: Re: [RE-wrenches] Pass through/transition box for Enphase I don't know what they're listed for but I know that they are very effective. Michael D Nelson MD Electric & Solar, Inc. 707-684-0064 mobile

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-10 Thread Mike Nelson
listed to be used with greater stranded conductors than class B > or C (7 or19)? > From: Carl Adams > Sent: ‎8/‎10/‎2016 17:37 > To: RE-wrenches > Subject: Re: [RE-wrenches] Pass through/transition box for Enphase > > I second Mike Nelson's approach, simple, easily ins

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-10 Thread Glenn Burt
But are they listed to be used with greater stranded conductors than class B or C (7 or19)? -Original Message- From: "Carl Adams" Sent: ‎8/‎10/‎2016 17:37 To: "RE-wrenches" Subject: Re: [RE-wrenches] Pass through/transition box for Enphase I second Mike Nelso

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-10 Thread Carl Adams
ke Polaris are also not listed for use with > fine stranded conductors. NSI has a special Polaris terminal that is grey > that is listed for use with fine stranding, and can safely be used. > I saw a few incorrect Polaris blocks pulled from an installation recently > that had melted.

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-10 Thread Mike Nelson
has a special Polaris terminal that is grey >>> that is listed for use with fine stranding, and can safely be used. >>> I saw a few incorrect Polaris blocks pulled from an installation recently >>> that had melted... >>> From: Michael Morningstar >>> Sent

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-09 Thread Ray Walters
tallation recently that had melted... From: Michael Morningstar <mailto:mjmornings...@gmail.com> Sent: ‎8/‎8/‎2016 15:23 To: RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org> Subject: Re: [RE-wrenches]

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-08 Thread Jay
installation recently > that had melted... > From: Michael Morningstar > Sent: ‎8/‎8/‎2016 15:23 > To: RE-wrenches > Subject: Re: [RE-wrenches] Pass through/transition box for Enphase > > I use DIN rail mount "feed through" terminal blocks. There's all kinds an

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-08 Thread Glenn Burt
. I saw a few incorrect Polaris blocks pulled from an installation recently that had melted... -Original Message- From: "Michael Morningstar" Sent: ‎8/‎8/‎2016 15:23 To: "RE-wrenches" Subject: Re: [RE-wrenches] Pass through/transition box for Enphase I use DIN rail

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-08 Thread Benn Kilburn
Din rail mounted terminal blocks Weidmuler WDU6 or WDU10, depending on the wire size you are using. Benn Kilburn SkyFire Energy Inc. 780-906-7807 > On Aug 8, 2016, at 12:49 PM, Jason Szumlanski > wrote: > > I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an > enc

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-08 Thread Mike Nelson
Soladeck. Michael D Nelson MD Electric & Solar, Inc. 707-684-0064 mobile 707-884-1862 office www.mdelectricsolar.com Sent from my iPhone > On Aug 8, 2016, at 8:49 AM, Jason Szumlanski > wrote: > > I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an > enclosure inside the

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-08 Thread Michael Morningstar
I use DIN rail mount "feed through" terminal blocks. There's all kinds and you will find some constructed such that no live parts exposed. Michael > On Aug 8, 2016, at 8:49 AM, Jason Szumlanski > wrote: > > I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an > enclosure

[RE-wrenches] Pass through/transition box for Enphase

2016-08-08 Thread Jason Szumlanski
I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an enclosure inside the attic where I can transition to Romex. I'd rather use some kind of rail mounted terminals in an enclosure or something rather than making splices in a generic j-box. I'm not looking to combine circuits -