Another approach is to add a relay. Use a 240 V relay with the coil
connected between the two phase wires of the generator (assuming
single phase). Use 2 fuses to protect the tapped wiring. Piercing
connectors can be useful to get the signal current from the phase
wires. Follow the rules on
3 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum AGS with Kohler RES 8.5
Tump, Dave,
This is very timely info for us. Could you pass the diagrams along?
Thanks,
Mario
[EMAIL PROTECTED]
- Original Message -
From: Tump <mailto:[EMAIL PROTECTED]>
To: 'RE-wrenches' &
MessageTump, Dave,
This is very timely info for us. Could you pass the diagrams along?
Thanks,
Mario
[EMAIL PROTECTED]
- Original Message -
From: Tump
To: 'RE-wrenches'
Sent: Monday, November 03, 2008 10:51 AM
Subject: Re: [RE-wrenches] Magnum AGS with Kohl
-wrenches
Subject: Re: [RE-wrenches] Magnum AGS with Kohler RES 8.5
Hi Dave,
Try the oil pressure wire, it probably is live when running but I have seen
some shut down systems that go to ground to stop, might not work there.
Don't give up on them yet, I expect that I know who that was at tec
Hi Dave,
Try the oil pressure wire, it probably is live when running but I have seen
some shut down systems that go to ground to stop, might not work there.
Don't give up on them yet, I expect that I know who that was at tech and he
still has some learning to do.
He once told me that he would not
ED]
> [mailto:[EMAIL PROTECTED] Behalf Of boB Gudgel
> Sent: Friday, October 31, 2008 4:45 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Magnum AGS with Kohler RES 8.5
>
>
>
>
> Hi David.
>
> Gary Baxter says he apologizes for not having that exact w
What we have done a couple times is to install a 15 amp breaker in the epanel
and wire in an outlet then plug a 12 vdc transformer into it.
when the generator kicks in the transformer turns on and it all fits neatly
inside the epanel.
Alternative Energy Systems of Maine
57 Hemlock Rd
Corinna, Me
t: Re: [RE-wrenches] Magnum AGS with Kohler RES 8.5
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: h
If switched 12V isn't readily available from the generator as
configured, couldn't you add a relay with 120 or 240 volt coil across
the generator outputs, whose contacts (or solid state outputs) would
switch 12V battery power as a signal line to the AGS? I realize it's
more stuff to wire in bu
AHHA, OK, Now I see...
Sorry. Nevermind.
Say no more !! Wink Wink... Nudge Nudge...
Thanks,
boB
David said:
Hi boB,
The Kohler RES is is a very simple 2 wire start as are all of the Kohler's
that I know of. These Kohler's have worked very easily with OutBack and
Trace inverters ov
lto:[EMAIL PROTECTED] Behalf Of boB Gudgel
> Sent: Friday, October 31, 2008 4:45 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Magnum AGS with Kohler RES 8.5
>
>
>
>
> Hi David.
>
> Gary Baxter says he apologizes for not having that exact wiring diagram
> fo
el
Sent: Friday, October 31, 2008 4:45 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum AGS with Kohler RES 8.5
Hi David.
Gary Baxter says he apologizes for not having that exact wiring diagram
for the Kohler RES generator
and the answer you got over the phone. (we gotta get him on thi
Hi David.
Gary Baxter says he apologizes for not having that exact wiring diagram
for the Kohler RES generator
and the answer you got over the phone. (we gotta get him on this list
too soon)
Magnum Energy does rely somewhat on customers to help with different
generator wiring if they hav
Wrenchsters,
We have a new 3.4kW PV off grid installation that includes a Magnum ME-AGS
Auto Gen Start module, Magnum ME-RC50 Remote Control, MS4448AE inverter and
a Kohler 8.5 RES lp gas generator for automatic backup battery charging (16
L-16G's).
We have successfully used a Magnum AGS control