eleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Sunday, March 27, 2011 8:38 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Generator and Enphase
Larry,
Ther
org] On Behalf Of Kent Osterberg
Sent: Saturday, March 26, 2011 5:56 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Generator and Enphase
Mark,
I agree it is best to wire the inverters on the utility side of
the transfer switch. When th
From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
Sent: Saturday,
March 26, 2011 5:56 PM
T
he contactor
>>>>> solution because of the potential for the NC contactor failing to open,
>>>>> keeping the inverters “online” when transferred to generator power. While
>>>>> unlikely, this is a possibility that must be considered.
>>>>
lists.re-wrenches.org] On Behalf Of Kent Osterberg
Sent: Saturday,
March 26, 2011 5:56 PM
To: RE-wrenches
Subject: Re:
[RE-wrenches] Generator and Enphase
Mark,
I agree it is best to wire the inverters on the utility side of the
transf
ww.berkeleysolar.com
From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Sunday, March 27, 2011 11:37 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Generator and Enphase
Larry,
Situations va
re is that the inverters will shut down every
>>> time the generator exercises.
>>>
>>> The only sure-fire way seems to be wiring the inverter on the utility side
>>> of the transfer switch, as Kent said.
>>>
>>> Jason Szumlanski
>>&g
s-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Sunday, March 27, 2011 11:37 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Generator and Enphase
Larry,
Situations vary so much that this might not be very useful. But here you go.
The at
7 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Generator and Enphase
Larry,
Situations vary so much that this might not be very useful. But here you
go. The attached sketch shows how we recently connected a customer that
had a backup generator and transfer switch that wasn't service rated
ch 27, 2011 7:11 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Generator and Enphase
Kent, Jason, or anyone else
Would you a have a simple one-line you could share for wiring the inverter
on the utility side of the transfer switch?
Thank you.
Larry Liesner
Wirewiz
Westport, CT
Phone: 203-644-2
Frye
> Berkeley Solar Electric Systems
> 303 Redbud Way
> Nevada City, CA 95959
> (530) 401-8024
> www.berkeleysolar.com
>
>
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Eric Thomas
> Sent: Saturday
system need battery
charging, when no one around no need ,solar and batteries are fine.
DT
From: Eric Thomas
To: re-wrenches@lists.re-wrenches.org
Sent: Sat, March 26, 2011 4:09:15 PM
Subject: [RE-wrenches] Generator and Enphase
I have a customer with a
Jason Szumlanski
Fafco Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Saturday, March 26, 2011 5:56 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Generator and Enphase
Mark,
I agree it
y, March 26, 2011 2:09 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Generator and Enphase
I have a customer with a "30A Mechanically Interlocked Breaker" for
their generator feed at the main panel. My question is: If the home
power is transferred from utility
9
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Eric Thomas
Sent: Saturday, March 26, 2011 2:09 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wren
Boy.. Seems I recall someone telling me this is bad... good way to take out your Genny's control board.. never tried it..Dan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44
Original Message
Subject: [RE-wrenches] Gene
I have a customer with a "30A Mechanically Interlocked Breaker" for their
generator feed at the main panel. My question is: If the home power is
transferred from utility to generator power, will the backfed PV see the
generator as grid power and sync up and produce? This is a nice Honda
Generator s