Kent,

Situations vary but this one line helps a lot, thanks.

So,  "To PV System" would go to the output of a grid tie inverter and "To 
Backed Up Loads" would go to the AC IN (transfer switch) of a battery inverter. 

I have been going to homes with existing 100A gen/utility ATS and wondering if 
I could keep it as is and be able to add a grid tie battery backup to it (using 
same backup loads). This schematic would work in that situation as well but 
wouldn't have the "To Non-Backed UP Loads" tap.


Larry Liesner
Wirewiz
Westport, CT
Phone: 203-644-2404
Fax: 203-557-0556
wire...@gmail.com
www.wire-wiz.com



On Mar 27, 2011, at 2:36 PM, Kent Osterberg wrote:

> Larry,
> 
> Situations vary so much that this might not be very useful. But here you go. 
> The attached sketch shows how we recently connected a customer that had a 
> backup generator and transfer switch that wasn't service rated. There were 
> nice gutters existing from the original install so accessing points to tap 
> conductors wasn't difficult. We could have connected the inverters to the 
> non-backed upped loads panel instead, but the utility requires an accessible 
> disconnect by the meter so it was more convenient to just get into the gutter.
> 
> Kent Osterberg
> Blue Mountain Solar
> 
> 
> 
> wire...@gmail.com wrote:
>> 
>> Kent, Jason, or anyone else
>> 
>> Would you a have a simple one-line you could share for wiring the inverter 
>> on the utility side of the transfer switch? 
>> 
>> Thank you.
>> 
>> Larry Liesner
>> Wirewiz
>> Westport, CT
>> Phone: 203-644-2404
>> Fax: 203-557-0556
>> wire...@gmail.com
>> www.wire-wiz.com
>> 
>> 
>> 
>> On Mar 26, 2011, at 6:04 PM, Jason Szumlanski wrote:
>> 
>>> We’ve explored this strategy many times due to all of the whole house and 
>>> critical load generators in Florida. We’ve stayed away from the contactor 
>>> solution because of the potential for the NC contactor failing to open, 
>>> keeping the inverters “online” when transferred to generator power. While 
>>> unlikely, this is a possibility that must be considered.
>>>  
>>> The other issue presented here is that the inverters will shut down every 
>>> time the generator exercises.
>>>  
>>> The only sure-fire way seems to be wiring the inverter on the utility side 
>>> of the transfer switch, as Kent said.
>>>  
>>> Jason Szumlanski
>>> Fafco Solar
>>>  
>>>  
>>> From: re-wrenches-boun...@lists.re-wrenches.org 
>>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent 
>>> Osterberg
>>> Sent: Saturday, March 26, 2011 5:56 PM
>>> To: RE-wrenches
>>> Subject: Re: [RE-wrenches] Generator and Enphase
>>>  
>>> Mark,
>>> 
>>> I agree it is best to wire the inverters on the utility side of the 
>>> transfer switch. When that isn't easy, a normally closed contactor that is 
>>> opened by generator voltage, will isolate the inverters from the generator 
>>> and allow automatic return to utility operation when the generator is off.
>>> 
>>> Kent Osterberg
>>> Blue Mountain Solar
>>> 
>>> 
>>> 
>>> Mark Frye wrote:
>>> Eric,
>>>  
>>> I do not have direct experience with this but have been exploring the issue 
>>> for a project I am currently doing.
>>>  
>>> My response will be to take the trouble to interconnect the Enphase 
>>> inverters on the line side of the tranfer switch so that the inverters can 
>>> never be connected to the generator.
>>>  
>>> Here are the reasons why:
>>>  
>>> 1 - Enphase states that any such application is considered an "off-grid" 
>>> application which voids their warrenty. As I am installing under the 
>>> California CSI program, I am required to provide a 10 year manufacture 
>>> equipment warranty so I cannot afford to install the inverters in a 
>>> dis-allowed manner.
>>>  
>>> 2 - Enphase states that the waveform of the generator may be "clean" enough 
>>> such that the inverter may attempt to syncornize and connect to it as if it 
>>> were the utility. If this were to happen Enphase believes the inverters 
>>> will ruin the generator regulator before the generator ruin the inverter. I 
>>> don't want to be the one to run the experiment to find out which would be 
>>> which.
>>>  
>>> 3 - I considered a contactor on the output of the inverters, such that the 
>>> inverters would isolated by a loss of line voltage, requiring some form of 
>>> reset. Ulitmately my customer agreed with me that this was an undesirable 
>>> constraint on the operation of an otherwise reliable grid-tied system and 
>>> it was not clear that this would satify the warranty issue.
>>>  
>>> Mark Frye 
>>> Berkeley Solar Electric Systems 
>>> 303 Redbud Way 
>>> Nevada City,  CA 95959 
>>> (530) 401-8024 
>>> www.berkeleysolar.com 
>>>  
>>>  
>>> From: re-wrenches-boun...@lists.re-wrenches.org 
>>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Eric Thomas
>>> Sent: Saturday, March 26, 2011 2:09 PM
>>> To: re-wrenches@lists.re-wrenches.org
>>> Subject: [RE-wrenches] Generator and Enphase
>>> 
>>> I have a customer with a "30A Mechanically Interlocked Breaker" for their 
>>> generator feed at the main panel. My question is: If the home power is 
>>> transferred from utility to generator power, will the backfed PV see the 
>>> generator as grid power and sync up and produce? This is a nice Honda 
>>> Generator so the power should be fairly clean. Any experiences are 
>>> appreciated.
>>> 
>>> Take Care,
>>> 
>>> 
>>> Eric Thomas
>>> Solar Epiphany LLC
>>> (206) 919-3014
>>> www.solarepiphany.com
>>> 
>>>  
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>>   
> <OneLine.JPG>_______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to