er 01, 2008 3:51 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] DLO wires in PV systems
Mike,
The RHH/RHW-2 do not cross to USE-2 because they do not have any rating for
UV exposure.
If these conductors are run outside of conduit on the array, you need USE-2
or PV conductor.
: 'RE-wrenches'
Subject: Re: [RE-wrenches] DLO wires in PV systems
Mike,
The RHH/RHW-2 do not cross to USE-2 because they do not have any rating for
UV exposure.
If these conductors are run outside of conduit on the array, you need USE-2
or PV conductor.
Mark Frye
Berkeley Sola
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Michael Cook
Sent: Monday, December 01, 2008 12:47 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] DLO wires in PV systems
We have a 4KW pv system install
We have a 4KW pv system installed and the local inspector wants to use this
as a test case so he is crossing all T's and dotting all I's. Which I am
happy to help him out with training his other inspectors We are running
into an issue on the module output wires. USE-2 or PV rated is how the cod