Ask the client if he is willing tho try the $120 experiment. If it doesn't
work, I'll give you $60 for the SMM.
On Sep 15, 2016 15:50, "Benn Kilburn" wrote:
> A couple of wrenches have suggested the Generac SMM (link in email below)
> but a call to generac resulted in them saying they only test
A couple of wrenches have suggested the Generac SMM (link in email below) but a
call to generac resulted in them saying they only test it with their own
generators and cannot say if it will work properly and will not offer support
if connected with generators other than Generac.
Have any of yo
Hi Benn,
I assume the transfer switch is not over by the generator. If that's the
case, there are typically many ways to do it utilizing a contactors that
senses the utility side of the transfer switch. You can also use the
control signal that sends the signal to the generator to start. That is
Wire them to the utility side of the transfer switch, Auto restart and probably
manufacture recommended method of connection when used in conjunction w/ gen
set. T
> On Sep 8, 2016, at 1:00 PM, Benn Kilburn wrote:
>
> Wrenches,
> We are installing 2 SolarEdge SE7600A-US inverters in a grid-tied
Greenfield, MA 01302-1227 USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com
Date: Thu, 8 Sep 2016 11:00:09 -0600
From: Benn Kilburn
To: RE-wrenches
Subject: [RE-wrenches] Back-up generator/inverter shut-down relay
Wrenches,
We are installing 2 SolarEdge SE7600A-US inverters in a grid
--- Original message
From: Benn Kilburn
Date:09/08/2016 7:00 AM (GMT-10:00)
To: RE-wrenches
Subject: [RE-wrenches] Back-up generator/inverter
shut-down relay
Wrenches,
Generac offers a Smart Management Module.
http://gens.lccdn.com/GeneracCorporate/media/Library/content/all-products/transfer-switches/residential-transfer-switches/0L1500-B-SMM-Module.pdf
I used one of these at a grid-tie job where the customer was simultaneously
having a Generac unit installed.
Generac Smart Management Module
http://gens.lccdn.com/GeneracCorporate/media/Library/content/all-products/transfer-switches/residential-transfer-switches/0L1500-B-SMM-Module.pdf
It will sense that the power is coming from a generator and open a
contactor. You can adapt that to disconnect your solar
he Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
>
>
> Original message
> From: Benn Kilburn
> Date:09/08/2016 7:00 AM (GMT-10:00)
> To: RE-wrenches
> Subject: [RE-wrenches] Back-up generator/inverter shut-down relay
>
> Wrenches,
> We are
58 Hz then it will work
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message From: Benn Kilburn
Date:09/08/2016 7:00 AM (GMT-10:00)
To: RE-wrenches
Subject: [RE-wrenches] Back-up generator/inverter shut-down relay
Wrenches,
We are instal
Wrenches,
We are installing 2 SolarEdge SE7600A-US inverters in a grid-tied system
that has a 15kw back-up generator on an auto transfer switch.
The generator is located in a shed about 300' or more away and the feeders
to the house are underground.
Inverters are located in the house basement mech
11 matches