Benn:
What kind of generator? If a Generac, and depending on the
controller vintage, it may be possible to install their SMM (smart
management module) load shedding module which does not require
separate control wires.
Down side is they're rated 50A for resistive loads and 40A for
inductive loads. If they work, one would be required for each
SE7600.
http://gens.lccdn.com/GeneracCorporate/media/Library/content/all-products/transfer-switches/residential-transfer-switches/0L1500-B-SMM-Module.pdf
Give Generac a call, or maybe a Wrench who sells/maintains Generacs
can comment on the suitability of this solution. I've used them for
load shedding, bot not for inverter shedding.
I believe one of the 8 settings will always lock out the unit on
grid failure / genset operating, as opposed to be one of the 7
total load based priorities.
Regards,
Gary Willett
Icarus Engineering LLC
On 9/8/16 6:17 PM, Benn Kilburn wrote:
Hey Jerry,
Yeah, hard wiring would require quite
a bit of trenching and wire.
I was hoping someone would be
familiar with a remote relay option or at least a manual reset
relay that would include some sort of indicator for when it has
shut off the inverters.
Earlier today I was considering what
you are suggesting. Seems like it should work.
Anyone care to poke some holes in
this theory?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
Wrenches
Does not sound like there is an option to hard wire a
shut down switch so here is an idea l have used. Program the
genny to run at 58 Hz. not yp this will keep the inverters
ftom starting up. None of the appliances will know but as
long as the inverter programming does not allow for 58 Hz
then it will work
Jerry
Sent via the
Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
-------- Original message --------
From: Benn Kilburn
Date:09/08/2016 7:00 AM (GMT-10:00)
To: RE-wrenches
Subject: [RE-wrenches] Back-up generator/inverter
shut-down relay
Wrenches,
We are installing 2 SolarEdge SE7600A-US
inverters in a grid-tied system that has a 15kw back-up
generator on an auto transfer switch.
The generator is located in a shed about
300' or more away and the feeders to the house are
underground.
Inverters are located in the house basement
mechanial room along with the house electrical panelboard.
We are looking for relay options to shut
down the inverters when there is a power interruption,
before the generator kicks in. This could be a manual
reset.
What are some options you have seen/used
for something like this?
Thanks,
Benn Kilburn
CSA Certified Solar
Photovoltaic Systems Electrician, SkyFire Energy Inc
14515 – 121A Ave NW |
Edmonton, AB | T5L 2T2
![SkyFire Energy
Logo_horizontal]()
WE HAVE
MOVED! Please note our new address above.
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
|
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org