Re: [RE-wrenches] Hybrid inverter with no battery

2025-08-01 Thread William Bryce via RE-wrenches
Ill try to find a block diagram to show the design and trade-offs of solar AIO inverters , particularly when it comes to integrating grid, generator, and PV charging into an All-In-One (AIO) system. The high-voltage DC bus that all current Asian made units use simplifies the design and reduces cost

Re: [RE-wrenches] Hybrid inverter with no battery

2025-08-01 Thread William Bryce via RE-wrenches
Midnite AIO fully supports this. It works as a standard string inverter without batteries. Have many units in the field that replaced dead SMA SunnyBoy inverters with the lower voltage strings. On Fri, Aug 1, 2025 at 8:29 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wro

Re: [RE-wrenches] Combining two PowerFlo16 to single Midnite AIO

2025-07-16 Thread William Bryce via RE-wrenches
MNP- PF batteries are designed to allow stacking of two lugs per terminal, providing greater flexibility in system wiring. Also, MNP is excited to welcome a new team member with strong installation experience. He is currently working on revising and improving all of our manuals. Positive changes a

Re: [RE-wrenches] Midnite AIO Battery Low/Lost Behavior

2025-07-15 Thread William Bryce via RE-wrenches
gt; near future a firmware upgrade would make this a selectable feature. > > Much appreciated, > Christopher > > On Tue, Jul 15, 2025 at 4:35 PM William Bryce via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Is this closed loop or open loop? If cl

Re: [RE-wrenches] Midnite AIO Battery Low/Lost Behavior

2025-07-15 Thread William Bryce via RE-wrenches
Is this closed loop or open loop? If closed loop the "rules" require the machine to stay shutdown until the "issue" is identified. On Tue, Jul 15, 2025 at 8:04 AM Tyrone Houck via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > That's my understanding as well. Sure would be cool if the

Re: [RE-wrenches] Midnite Solar / Midnite Power

2025-07-14 Thread William Bryce via RE-wrenches
. On Mon, Jul 14, 2025 at 7:38 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > thanks Bryce, > > One last question, can you tell us why this is happening? > > jay > > On Jul 14, 2025, at 5:31 PM, William Bryce via RE-wrenches < > re-wrenches@lis

Re: [RE-wrenches] Midnite Solar / Midnite Power

2025-07-14 Thread William Bryce via RE-wrenches
help. There should be no laps in warranty support or service support. On Mon, Jul 14, 2025 at 6:12 PM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Thx Bryce > > Who do we call for tech support, warranty etc? > > Jay > > On Jul 14, 2025, at 2:39 PM, Wi

Re: [RE-wrenches] Midnite Solar / Midnite Power

2025-07-14 Thread William Bryce via RE-wrenches
All the Asian made products will now fall under the Midnite Power brand. MNP will have FP16 batteries in stock very soon as they are on the water and on the way. Still have MNS branded inverters, with more inverters on the way. Midnite Solar will focus on the American made products, with a new in

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-07-10 Thread William Bryce via RE-wrenches
>>> This is really needed. The fact that the generator smart load input >>> doesn't turn the inverters on and charge the batteries when a generator is >>> present after a low voltage cutout is really problematic. >>> >>> >>> Jason Szumlanski

Re: [RE-wrenches] Induction Cooktops Off-Grid

2025-06-30 Thread William Bryce via RE-wrenches
No issues, use them at my home with Off Grid on MNPS / MNP AIO. Seamless, even when frequency shifting for AC coupled. On Mon, Jun 30, 2025 at 6:58 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Does anyone have any experience with how high frequency inverters

Re: [RE-wrenches] Solar Assistant and Midnite AIO

2025-05-18 Thread William Bryce via RE-wrenches
nitoring. I can live without the > remote monitoring, but I really really like Discover batteries, and with > those, I can at least see SOC with Lynk Cloud. > > On Sun, May 18, 2025 at 9:39 AM William Bryce via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >&

Re: [RE-wrenches] Solar Assistant and Midnite AIO

2025-05-18 Thread William Bryce via RE-wrenches
Dana I have used and installed plenty of Rosies Inverters, Hawks bay. and Barcelona's Charge controllers, and they are rock solid. They look like the older Outback gear because the same engineers designed them. So why stay with outdated older technology that will be RE-manufactured by who knows w

Re: [RE-wrenches] Solar Assistant and Midnite AIO

2025-05-15 Thread William Bryce via RE-wrenches
I highly recommend using SA with ALL Asian inverters. This will remove the chance of a SolArk screen of death bricking and locking you out of your inverter, and also remove any chance of data or setting manipulation from others. With SA, ALL the data is served and stored on the RPie computer local

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-14 Thread William Bryce via RE-wrenches
Everyone, Please forgive MNS for not promptly responding to the questions. Midnite Solar does not currently have an official poster for the Wrenches List. Per the rules of the list, MNS is working to get a new Rep to work with the installers as we always have. To address the questions that wer

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-14 Thread William Bryce via RE-wrenches
n using raw > voltage? That would solve one issue. > > > Jason Szumlanski > Principal Solar Designer | Florida Solar Design Group > NABCEP Certified Solar Professional (PVIP) > Florida State Certified Solar Contractor CVC56956 > Florida Certified Electrical Contractor EC1301

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-14 Thread William Bryce via RE-wrenches
Certified Solar Professional (PVIP) > Florida State Certified Solar Contractor CVC56956 > Florida Certified Electrical Contractor EC13013208 > > On Wed, May 14, 2025, 10:57 AM William Bryce < > wlbr...@pineridgeproducts.com> wrote: > >> Everyone, Please forgive MNS for

Re: [RE-wrenches] Outback woes

2025-05-11 Thread William Bryce via RE-wrenches
EG4 and most Asian Inverters do not have Conformal coating. That goes directly against any 10 year warrant and long life. There is a reason that old Trace inverters, OutBack inverters, and Schnider inverters, are still operating many years after the warranty has expired. On Sun, May 11, 2025 at

Re: [RE-wrenches] Distributors versus manufacturers providing support

2025-04-22 Thread William Bryce via RE-wrenches
Everyone needs to look at the whole system. The issue is when you have "Installers" and then also have DIY. DIY can eat up Hours and Hours of support time. This time is not free and takes away from supporting customers who purchase more than one time (Installers). (Grid tie "installers" can also ea

Re: [RE-wrenches] Pytes E-Box 48100 batteries with Midnite AIO

2025-04-21 Thread William Bryce via RE-wrenches
The MN AIO will not support the Pytes V5. The V5 has a proprietary protocol. But the Open loop always works!! On Mon, Apr 21, 2025 at 5:29 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I have a client with eight Pytes batteries (not v5) where I am upgrading > t

Re: [RE-wrenches] Generator failure alarm

2025-02-22 Thread William Bryce via RE-wrenches
Control By Web for the win! 100% reliable and easy to configure. On Sat, Feb 22, 2025 at 2:03 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Dan: > > > > The application is an off-grid animal rescue facility with a requirement > for high reliability. We recently

Re: [RE-wrenches] Automatic Dark Start of Depleted Lithium Batteries

2025-02-22 Thread William Bryce via RE-wrenches
Everyone wants to compare the AIO inverters to the older low frequency inverters when it comes to the idle power draw. But everyone now wants all the bells and whistles. Nothing is free, and if you take an older system then add up the charge controllers draw, SCP monitoring system, Gateway device,

Re: [RE-wrenches] Inverter ratings exceeding 25kw fir battery backup

2025-02-18 Thread William Bryce via RE-wrenches
Proceed with caution, feel free to contact me off list. On Tue, Feb 18, 2025 at 5:36 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Don't even get me started on that. I have a library that wants a PV system > and batteries just to operate the elevators in the ev

Re: [RE-wrenches] Midnite Powerflo Questions

2025-02-14 Thread William Bryce via RE-wrenches
There is no issue wall mounting as long as both mounting brackets are used and the wall can support the weight. People do not read manuals and then attach to wall that cannot support the weight. On Fri, Feb 14, 2025 at 6:04 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wr

Re: [RE-wrenches] Midnite Powerflo16 to old OB inverters

2025-02-03 Thread William Bryce via RE-wrenches
Hi Jay The settings for the MNS Batteries are on a sticker on each battery. BMS- LVCO 44.8 HVCO 58V (The HVCO is not on the sticker) LVCO (inverter) 46.0 Float 54V Bulk 56.1V The rest of the you can set to what you want, the battery does not care. All Prismatic cells operate mostly the same, an

Re: [RE-wrenches] Midnite Powerflo16 with Radian

2024-11-09 Thread William Bryce via RE-wrenches
Hi Nick There are PF16's running open loop with Radians. The PF16 has a precharge built in. The key is to have the inverter breaker closed, then close the battery breaker. After that push the BMS power button (3-4 seconds the display will power up) and the battery will slowly ramp up and do a prec

Re: [RE-wrenches] Midnite Solar AIO question

2024-07-22 Thread William Bryce via RE-wrenches
elson via RE-wrenches wrote: > > Jay, > I have not tried it with anything but the Midnite BMS, so no personal > experience. Midnite says it is compatible with others, and I will take > William's word that it is compatible with Pylon protocol. > Howie > > On Sun, Jul

Re: [RE-wrenches] Outback in general

2024-07-21 Thread William Bryce via RE-wrenches
Hi Jay The AIO will work with any battery that uses the Pylon battery protocall. You can find some Youtube videos of it being used with the EG4 wall mount batteries. On Sun, Jul 21, 2024 at 9:29 AM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > HI Howie, > > Does the AIO commu

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread William Bryce via RE-wrenches
Brown > Off-Grid Solar Commander since 2006 > Maverick Solar Enterprises, Inc. > • Solar Commander Remote Power > • SunFlow Systems Cathodic Protection > maver...@mavericksolar.com > 512-460-9825 > > > > On Apr 10, 2024, at 10:54 AM, William Bryce via RE-wrenches &l

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread William Bryce via RE-wrenches
All As a Beta tester and being a part of the development of the MNS All in One, MNS is working to ensure that the current limitations from the use of LA batteries will be addressed and supported. MNS is addressing the concerns of using an AOI inverter because failure will require the R&R of the

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread William Bryce via RE-wrenches
John The New MidNite AIO is completely field serviceable. If you have an issue (say lightning) MNS will stock all the needed boards and everything can be replaced on the wall. On a scale of one to ten, it's a 7 with 10 being the hardest (lots of screws). Only tools needed are an 11in One, pliers,

Re: [RE-wrenches] Well pump with Sol-Ark

2023-10-11 Thread William Bryce via RE-wrenches
For high surge and unbalanced splitphase loads, you can’t beat a Midnite Solar Rosie Inverter. It uses Sic FET’s and is rock solid. I have an early unit and it’s starts my 5hp compressor and still runs other loads without a flicker. Runs loads that even my Schneider XW+ would not. Why complicate

Re: [RE-wrenches] Charger recommendations

2023-09-04 Thread William Bryce via RE-wrenches
People might be scared of them because they are China built. But the EG4 ChargeVerter is outstanding and reliable. 48v 100 amps. Check it out at Signature Solar. This thing take crap generator power and is just works. Has a good price point. On Mon, Sep 4, 2023 at 8:06 PM Starlight via RE-wrenc

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread William Bryce via RE-wrenches
I can also backup what Jim has said, and have seen the same gear destroyed by removing the battery abruptly when the controller is under heavy load. They can die, and sometimes die spectacularly. Have seen SolArk inverters integrated MPPT controllers blow up when lithium battery BMS disconnects. N

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread William Bryce via RE-wrenches
All One thing that no one is talking about is what happens to the MPPT charge controllers when the Battery Disconnect trips when the charge controllers are under full load. Many will blow up. Try turning off the battery breaker on a SolaArk when the charge controllers are maxed, and see if you ge

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-14 Thread William Bryce via RE-wrenches
info, > no spec sheets etc. None of my vendors have them and Midnite is estimating > Apr 2023 as the release date. > > > > On Sat, Jan 14, 2023 at 8:34 AM William Bryce via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> I run the XW6848 in

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-14 Thread William Bryce via RE-wrenches
I run the XW6848 in my shop. When running my CNC plasma table the XW will shutdown due to exceeding its output rating if it is a long cut on metal when the 4HP compressor kicks on. I also have a Midnite Solar Rosey, both are connected to the same battery so it's an equal comparison. The Rosy invert

Re: [RE-wrenches] wireless water tank level monitor

2022-06-17 Thread William Bryce via RE-wrenches
Hi Jay Don’t think anyone else chimed in on this so I will. Have use 2 different units. One is all China and works pretty good. But it’s using China hardware and China servers. Search on eBay for Konlen Smart Controller I have one and it’s been great. For a NA option you have Paremtech PTLev

Re: [RE-wrenches] Array easily adjustable from 30 to 90 degrees

2015-05-20 Thread William Bryce
Try www.mtsolar.us On Wed, May 20, 2015 at 3:04 PM, Richard L Ratico < richard.l.rat...@valley.net> wrote: > Bob Ellison, > Thanks for your quick reply. Checked them out. They only go to 50 degrees > and > require max. 66" high posts. Looks like radical modification of the > recommended > post an