Re: [RE-wrenches] Outback FM80's connected to Hub

2010-01-04 Thread Walt Ratterman
functional yet, the SOC management, based on the FNDC would “communicate” with the FX inverters and the charge controllers if everything is via the hub. This could be beneficial in systems where you have both solar and generator / grid charging going on. Thanks, Walt Walt Ratterman SunEnergy

Re: [RE-wrenches] DC disconnect placement

2009-12-20 Thread Walt Ratterman
voltage drop, and (b) there IS protection at the equipment room on the homeruns from the combiners to the equipment room (assuming the combiners are at the array) as long as we have individual circuit breakers on the input of each charge controller. Thanks, Walt Walt Ratterman

Re: [RE-wrenches] quality off-grid PV for Africa

2009-12-16 Thread Walt Ratterman
phone then. Thanks, Walt Walt Ratterman SunEnergy Power International 11 Laurel Lane South Washougal, WA 98671 (360)-837-3680 ▪ fax (360)-837-1315 ▪ Skype Walt-Mobile wratter...@sunepi.org ▪ www.SunEPI.org <http://www.sunepi.org/> Fr

Re: [RE-wrenches] Strings and series of batteries

2009-12-02 Thread Walt Ratterman
Two answers, Jay, Actually both. For a lot of systems, we use the ILSCO or POLARIS multi-barrel insulated mechanical compression device that holds up to 8 or more cables up to whatever size you purchase them in. Then, for larger systems, we use standard, 1/4 x 4" copper bus bar with isolating bu

Re: [RE-wrenches] Strings and series of batteries

2009-12-02 Thread Walt Ratterman
Michael: The bus bar solution has to do at least partially, with: - Equal resistance paths to each string of batteries (need to keep the circuit cables the same length). - Ability to remove (isolate) a string more easily. With two strings, if the bus bar capacity exists in the hardware of the

Re: [RE-wrenches] Strings and series of batteries

2009-12-02 Thread Walt Ratterman
Hello Chris, We use the Polaris Insultaps all the time, but we have usually used them for the battery paralleling only. Are you using these for the negative common bus bar as well (in place of the bus bar in the flexware??) And are you doing the same thing for the positive bus bar? Thanks W

Re: [RE-wrenches] Other's thoughts on Autonomy? was concord batteries, EQUALIZE Them!

2009-12-01 Thread Walt Ratterman
Hello Travis, Just for my $.02.. I gave up a while ago on the textbook 3 days of autonomy, but for a slightly different reason (including yours). We would give a battery bank 3 days of autonomy, and then place all kinds of alarms and load shedding at 50% SOC, but nothing to tell folks w

Re: [RE-wrenches] concord batteries

2009-11-29 Thread Walt Ratterman
It seems you are saying that the batteries are 12V batteries. And, as there are 40 of them, this would indicate you have about 10 parallel strings. It would have been difficult to keep this battery bank properly charged even if the charging parameters were appropriate. One string is best, two

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Walt Ratterman
Glenn: This is correct on the battery bank separation. You don't split out the battery banks until you reach a "cluster". For example, one three phase setup is a cluster. If you have two, three-phase setups - you have two clusters - and two battery banks. And.I think if you check thro

Re: [RE-wrenches] prevailing wages for PV work

2009-10-12 Thread Walt Ratterman
– confirming that prevailing wages are required, and giving what tasks need to be done under what labor classification. Walt Walt Ratterman SunEnergy Power International 11 Laurel Lane South Washougal, WA 98671 (360)-837-3680 ▪ fax (360)-837-1315 ▪ Skype Walt-Mobile

Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays

2009-10-10 Thread Walt Ratterman
Hello guys... I believe (but I can be wrong) that the code is pretty clear on this. . No problem with the metal conduit. . Use bonding bushing on the ends (to be sure that the conduit is bonded) . No problem with the ground wire touching the conduit - in fact the b

Re: [RE-wrenches] Sunny Island DC Load Centers, Sealed Batteries

2009-10-07 Thread Walt Ratterman
PM To: RE-wrenches Cc: Walt Ratterman Subject: Re: [RE-wrenches] Sunny Island DC Load Centers, Sealed Batteries Walter, Kirpal, Nice install in Burundi! I'm wondering about the battery cables - how did you connect the battery lugs on the 2/0 (?) cable to the SI's? Is this an SM

Re: [RE-wrenches] Sunny Island DC Load Centers, Sealed Batteries

2009-10-07 Thread Walt Ratterman
back boxes restricted for "vertical installation only"? I've got my own 3 phase Sunny Island thing coming up (maybe) so I look forward to these answers. Mick Abraham, Proprietor www.abrahamsolar.com Voice: 970-731-4675 On Wed, Oct 7, 2009 at 7:26 PM, Walt Ratterman wrote: Hello Kirpal

Re: [RE-wrenches] Sunny Island DC Load Centers, Sealed Batteries

2009-10-07 Thread Walt Ratterman
Hello Kirpal, Walt Ratterman here. I can respond to at least the first part. In Burundi, we used three 5 KW Sunny Island 5048's in a three phase configuration. For all of the DC and AC breakers, wireways, etc., etc., we used the Outback Flexware equipment. We put the DC o

Re: [RE-wrenches] Charging AGM Batteries

2009-09-15 Thread Walt Ratterman
Peter, The DEKA charging manual that I have been working from for their sealed batteries (AGM and Gel) quote 30% of C20. And….DEKA’s literature also has a maximum charging voltage of 2.35 VPC. Not sure about the other brands. Thanks, Walt From: re-wrenches-boun...@lists.re-w

Re: [RE-wrenches] Solar 12 volt DC lighting for school in Haiti

2009-08-23 Thread Walt Ratterman
list if you are interested. Maybe we can compare notes. See ya, Walt Walt Ratterman SunEnergy Power International 11 Laurel Lane South Washougal, WA 98671 (360)-837-3680 ▪ fax (360)-837-1315 ▪ Skype Walt-Mobile wratter...@sunepi.org ▪ www.SunEPI.org

Re: [RE-wrenches] Solar 12 volt DC lighting for school in Haiti

2009-08-17 Thread Walt Ratterman
Hello Lee, Walt here. I will be leaving for Haiti in about a week, and be there for three…. We have done lots of schools. If you are strictly 12V, your choices primarily are 12V CF and LED lights. There are lots of pros and cons to both. The real question is what you intend to us

Re: [RE-wrenches] Charge controller recommendation

2009-06-30 Thread Walt Ratterman
I would recommend the Morningstar controller. There is a model (I don't have the catalog here) with a good timer, and LVD and good environmental controls, and electronic circuit protection. Walt -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun

Re: [RE-wrenches] Solar Boost Controller in Senegal

2009-06-30 Thread Walt Ratterman
998 Shari Ave Yuma, AZ 85365 On Jun 30, 2009, at 2:43 PM, Walt Ratterman wrote: Hello, Why do you say that AGM batteries are a better choice? I have been reading about the differences, and all I see (comparing DEKA Gel versus DEKA AGM is that the cycle life of the AGM (at 50

Re: [RE-wrenches] Solar Boost Controller in Senegal

2009-06-30 Thread Walt Ratterman
http://www.wind-sun.com/ForumVB/ .. - Original Message - From: Walt Ratterman <mailto:wratter...@sunenergypower.com> To: 'Rick <mailto:r...@blueskyenergyinc.com> Cullen -

Re: [RE-wrenches] Solar Boost Controller in Senegal

2009-06-30 Thread Walt Ratterman
ailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Walt Ratterman Sent: Friday, June 26, 2009 3:22 PM To: 'RE-wrenches' Subject: [RE-wrenches] Solar Boost Controller in Senegal Hello, I am in a very remote part of Senegal, (near the Guinea and Mali borders…) and I have

Re: [RE-wrenches] Solar Boost Controller in Senegal

2009-06-29 Thread Walt Ratterman
_ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Walt Ratterman Sent: Friday, June 26, 2009 3:22 PM To: 'RE-wrenches' Subject: [RE-wrenches] Solar Boost Controller in Senegal Hello, I am in a very remote part

Re: [RE-wrenches] Solar Boost Controller in Senegal

2009-06-27 Thread Walt Ratterman
. >> Northern Arizona Wind & Sun - Electricity From The Sun Since 1979 >> Online Store: http://store.solar-electric.com/ >> Solar Discussion Forum: http://www.wind-sun.com/ForumVB/ >> .... ...

[RE-wrenches] Solar Boost Controller in Senegal

2009-06-26 Thread Walt Ratterman
Walt Ratterman SunEnergy Power International 11 Laurel Lane South Washougal, WA 98671 (360)-837-3680 ▪ fax (360)-837-1315 ▪ Skype Walt-Mobile wratter...@sunepi.org ▪ www.SunEPI.org <http://www.sunepi.org/> ___ List spo

Re: [RE-wrenches] Sunny Island 5048 & Enphase

2009-05-18 Thread Walt Ratterman
Island to let it know whether it is working on the Grid parameters or on the Generator parameters. If the parameters are the same, I guess it doesn't matter. Thanks, Walt Walt Ratterman SunEnergy Power International www.sunepi.org -Original Message- From: r

Re: [RE-wrenches] Long MC Cable Mid String

2009-04-22 Thread Walt Ratterman
Drake: The voltage lost between the two points is the product of the current flowing in the wire, and the resistance of that section of wire (times 2 depending on how you figure the distance.). Walt From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wre

Re: [RE-wrenches] Ishaq M. Shahryar passing - Memorial

2009-04-15 Thread Walt Ratterman
, and last year. In some ways (in many ways) they need help more now than they did in late 2001. The difficulty is doing things in large quantities effectively, and working through governments. In most cases neither is feasible. Thanks a lot for your thoughts. Walt Walt Ratterman

Re: [RE-wrenches] Odd Outback FNDC/Mate issue

2009-03-27 Thread Walt Ratterman
Howie, I can only add that we have installed all of our FNDC voltage sensing wires to the busses in the FW1000 can and have no problem. That is kind of a reverse affirmation, I guess. Walt Ratterman SunEnergy Power International www.sunepi.org -Original Message- From: re-wrenches

Re: [RE-wrenches] grid tie sync with big stiff genny?

2009-03-13 Thread Walt Ratterman
work with PV only? (no generator, no grid, no batteries??) Thanks, Walt Ratterman SunEnergy Power www.sunepi.org -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Darryl Thayer Sent: Friday, March 13, 20

Re: [RE-wrenches] grid tie sync with big stiff genny?

2009-03-11 Thread Walt Ratterman
Max, I would like to learn from this as well. I do a good bit of off-grid systems connected to large generators. Thanks, Walt Ratterman Walt Ratterman SunEnergy Power International 11 Laurel Lane South Washougal, WA 98671 (360)-837-3680 ▪ fax (360)-837-1315 ▪

Re: [RE-wrenches] Backup generator labor (was How large is too large?)

2009-03-03 Thread Walt Ratterman
– large grid = pv / diesel hybrid, at least in my book. Walt Ratterman SunEnergy Power International www.sunepi.org From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Joel Davidson Sent: Tuesday, March 03, 2009 6:07 PM To: jry

[RE-wrenches] Stand-Alone DC Relays?

2009-02-23 Thread Walt Ratterman
, but the tricky part is being able to set the voltage on and off points. We are dealing with both 48V and 24VDC systems. Thanks, Walt Walt Ratterman SunEnergy Power International 11 Laurel Lane South Washougal, WA 98671 (360)-837-3680 ▪ fax (360)-837-1315 ▪ Skype

Re: [RE-wrenches] Buck/Boostr tranformer for phase conversion, 3 phase generator to outback split phase quad stack

2009-01-14 Thread Walt Ratterman
Nick: I am pretty sure you can put two of the inverters on Phase A, one on Phase B, and one on Phase C Will this make any difference to the owner? Walt Ratterman SunEnergy Power International www.sunepi.org -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org

Re: [RE-wrenches] Trojan L-16 Uber Model #'s

2008-12-31 Thread Walt Ratterman
don't have any experience with the Trojan L-16's yet, but probably will soon... Take care, Walt Ratterman SunEnergy Power International www.sunepi.org -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behal

Re: [RE-wrenches] mate issues AND MORE ISSUES

2008-12-23 Thread Walt Ratterman
Walt Ratterman here. All of my work is done overseas, but I gave up on automatic generator starting years ago. I now make extensive use of the relays for alarms, and load shedding, but not automatic generator starting. I am a firm believer that this needs to remain a people-thing for

Re: [RE-wrenches] voltag drop

2008-12-08 Thread Walt Ratterman
Round trip... (unless you are using a table that has already counted this in) Take care, Walt From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Marco Sent: Monday, December 08, 2008 2:13 PM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] voltag drop I feel

Re: [RE-wrenches] Best Off-Grid Equalize Charging Method

2008-10-23 Thread Walt Ratterman
th no generator (the smaller systems) installations with many days of autonomy simply almost never get charged back to full after the first few days of clouds, unless the PV array is oversized AND the users cut way back on their loads. Sorry about no documentation.... Take care, Walt Ratterman

Re: [RE-wrenches] Charging with "no contact" systems

2008-09-30 Thread Walt Ratterman
2 of > the 4448 inverters will each put about 60 amps DC into a battery bank with > only 17 amps in @ 240 volts or 34 amps ac @ 120 volts. > > > Just another wrenches opinion, > Bob > > On Tue, Sep 30, 2008 at 10:57 AM, Walt Ratterman <[EMAIL PROTECTED]> wr

Re: [RE-wrenches] Micro Hydro control

2008-09-30 Thread Walt Ratterman
There are mechanical control systems that automatically control the flow (such as the old fly-ball mechanisms), but these are very expensive, and generally not such a good idea until you get up to the larger sizes. The introduction of electronic load control (where you accept all of the flow and p

[RE-wrenches] Charging with "no contact" systems

2008-09-30 Thread Walt Ratterman
, Walt Walt Ratterman SunEnergy Power International 11 Laurel Lane South Washougal, WA 98671 (360)-837-3680 ▪ fax (360)-837-1315 ▪ Skype Walt-Mobile <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED] ▪<http://www.sunepi.org/> ww

Re: [RE-wrenches] evergreen panels diode problems

2008-09-23 Thread Walt Ratterman
/lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org Walt Ratterman Sent Wirelessly ___ List sponsored by Home Power m

[RE-wrenches] Low Voltage Disconnect

2008-09-22 Thread Walt Ratterman
coming in from the panels (if we are forced to stay with 12V) is right at 60 amps. To get the low voltage disconnect function, do you see any problem going with multiple PS-30M charge controllers, and using just one of them for the 40W load? Thanks, Walt Walt Ratterman SunEnergy

Re: [RE-wrenches] Wireless control of off-grid pumps

2008-09-03 Thread Walt Ratterman
to learn more about the wireless solutions (but our spplications are not candidates for digital cell phones, or wireless internet...) Thanks Walt SunEnergy Power www.SunEPI.org Walt Ratterman Sent Wirelessly -Original Message- From: "Allan Sindelar" <[EMAIL PROTECTED]&g

Re: [RE-wrenches] battery reference gen start module

2008-08-28 Thread Walt Ratterman
et at either 46 V or higher. Walt Ratterman SunEnergy Power International www.sunepi.org From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tump Sent: Thursday, August 28, 2008 12:54 PM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] battery reference gen start m

Re: [RE-wrenches] Braided grounding wire

2008-08-22 Thread Walt Ratterman
i.org Walt Ratterman Sent Wirelessly -Original Message- From: "Wind-sun.com" <[EMAIL PROTECTED]> Date: Fri, 22 Aug 2008 08:46:28 To: RE-wrenches Subject: Re: [RE-wrenches] Braided grounding wire ___ List sponsored by Home Power

Re: [RE-wrenches] Tax Deductible RE Donations (inspired by Inverter for Switch to GT)

2008-08-06 Thread Walt Ratterman
. All that being said, keeping the above caveats in mind, I know we would always entertain donations of good equipment, and I would think most folks doing the kind of work we do would also. Hope that helps, Walt Ratterman SunEnergy Power International From: [EMAIL PROTECTED] [mailto

Re: [RE-wrenches] ESL light bulbs

2008-08-03 Thread Walt Ratterman