Hello all,

 

While this may be excellent advice, I think it would be good to clarify that 
this may apply primarily to grid tied systems.  

 

In Off Grid systems we have different considerations, such as (a) we are 
working with lower voltages and need to limit the size of the wire and the 
voltage drop, and (b) there IS protection at the equipment room on the homeruns 
from the combiners to the equipment room (assuming the combiners are at the 
array) as long as we have individual circuit breakers on the input of each 
charge controller.

 

Thanks,

 

Walt

 

 

Walt Ratterman

SunEnergy Power International

 

11 Laurel Lane South     Washougal, WA   98671

(360)-837-3680   ▪   fax (360)-837-1315   ▪   Skype  Walt-Mobile

wratter...@sunepi.org   ▪   www.SunEPI.org <http://www.sunepi.org/> 

 

 

 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Matt Lafferty
Sent: Sunday, December 20, 2009 4:10 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] DC disconnect placement

 

William,

 

Put the inverters at the array. Run the AC underground. If the AC feeder gets 
dug up by some rowdy backhoe operator in the future, the breaker (or series of 
breakers) will open, de-energizing the circuit immediately (and maybe the main 
to the residence at the same time).

 

If you are dead-set on putting the inverters in the pump shed, put any 
combiner(s) at the inverters. This affords the maximum overcurrent protection 
for the underground feeders. Install DC disconnecting means in each string 
before leaving the array if you go this route.

 

For maximum protection of conductors and to minimize arc hazards, The SAFEST 
location for a combiner is ALWAYS at the inverter. All conductors on the 
inverter (load) side of a fused combiner are unprotected by anything other than 
their ampacity rating. If a fault occurs on the load side of a combiner, it 
will burn until it clears or welds to a dead short. 

 

Cheers,

 

Matt Lafferty


 

  _____  

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Sunday, December 20, 2009 11:02 AM
To: RE-wrenches
Subject: [RE-wrenches] DC disconnect placement

Friends:

I am embarking on a 10 Kw ground mount grid-tie installation.  The client 
prepared for this installation some time ago by stubbing a PVC conduit 
underground towards the future location of the PV array.  Prior to beginning 
this job, an excavation contractor intercepted the empty conduit with a backhoe.

No harm was done because this conduit was empty.  Had this conduit been filled 
with PV feeders, it would have been very necessary to be able to disconnect the 
PV arrays, both for safety and to prevent a brush fire in our very dry climate.

The inverters will be located in a pump house about 130 feet from the PV 
arrays.  I would not normally put disconnects at the array and they are not 
required.  This scenario, however, has caused me to reconsider.  The design now 
calls for a disconnect at each row of modules.  I feel that it would not be 
prudent to delete this important safety item.

I wish there were a better selection of  compact, low profile disconnects 
suitable for a roof-top installation.  I have put external handle disconnects 
on roof but they look terrible.  I may specify touch-safe fuse holders inside 
of a Sola Deck for future comp roof jobs.  I am not sure what we will do with 
tile roofs.

It seems to me that every source of power should have a means of disconnection 
as close to the source as possible.  This is just common sense.

William Miller




Please note new e-mail address and domain:

William Miller 
Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com <http://millersolar.com/> 
License No. C-10-773985

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to