19,000 feet? Is that three or four conductors in an overall run for 4-5k
feet? Pulling vaults every 3-500'? 4,000' distance is Medium voltage
(15Kv) territory. 1/0 becomes #4. If your not set up for big pulls, most of
the wire suppliers in the Bay Area will put your runs on Wemco's. Those are
mult
I'm getting calls almost weekly. "Hi, I bought an EcoFlow home back up
system, I'm looking for someone to install solar panels for it". I've
convinced a couple of clients to take a hit and sell the EcoFlow, Bluetti,
Anker units at a loss and let me install a permanent system. Anyone else
getting th
We've been using manual transfer switches with the Midnite AIO's
On Fri, Jan 17, 2025 at 7:29 AM Stuart Kriendler via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Many thanks again Mac and Wrenches,
>
> This is now put to bed with confirmation the only listed 200A ATS that
> will wor
I wish I didn't know what you guys were talking about :) !!! Both SS and
S-A. As I've been going through my learning curve with Midnite's AIO and
PF16, both Logan and Rick (and Richard at NAZ) have been there immediately
for me and have held my hand the whole time.
On Fri, Dec 13, 2024 at 1:43 PM
Discover and Sol-Ark pair well together in closed loop. Minimal fuss with
programing. My understanding is that the Midnite battery is best used with
their AIO.
On Tue, Dec 10, 2024 at 2:48 PM MDElectricSolar via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Sol-ark 15k easy.
> Michael
The Discover Helios battery that's being released soon is what you want for
those systems. I'm liking the Midnite AIO/Powerflow combo also.
On Mon, Dec 9, 2024 at 12:23 PM MDElectricSolar via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> We just started using the Discover rackmount ba
Thanks Bob-O. That's exactly what I needed to know.
On Fri, Nov 15, 2024 at 8:34 AM Bob-O via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> They also offer an SQF-25 which I use and like. Unlike the smaller SQF
> pumps, it is a multi-stage centrifugal which can be disassembled and
>
ww.sunpumps.com/Category/SCS%20-%20Submersible%20Pumps> should
> do what you need.
>
> Kent Osterberg
> Blue Mountain Solar
> 541-975-3930
>
>
> On 11/14/2024 1:27 PM, Michael Morningstar via RE-wrenches wrote:
>
> Wrenches,
> Any recommendations for a "high vol
Wrenches,
Any recommendations for a "high voltage" Array Direct surface pump.
Pumping from a creek. 150' head. Looking for as many gpm's as possible.
Large array is fine. If I remember correctly, Dankoff pumps are fairly low
voltage.
Thanks,
Michael
--
Michael Morningstar
Morningstar Electric
Same with the Midnite AIO. They are very explicit in the instruction
manual.
On Sun, Nov 10, 2024 at 9:23 AM James Jarvis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> There isn't. It's a cultural thing. All of our Japanese machines have
> completely different grounding schemes th
I wish I didn't know what you were talking about! : )
On Sat, Nov 9, 2024 at 7:16 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I wrote in another thread about an off-grid quad Sol-Ark system that was
> shutting down due to parallel stop when one of the four in
Which Cummins?
On Sat, Nov 9, 2024 at 4:59 AM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi Jim,
>
> I think the voltage regulator on the generator is the issue, but you may
> be able to fix it by trying a different AC input mode. What is the AC
> input mode are you
Polarwire's Arctic Ultraflex and the lugs they sell are made for each
other. No errant strands to deal with. Insulation cuts easily with any
knife. I cut lengths with a small cordless bandsaw. I crimp with a cheap
Chinese hydraulic crimper. I used the Milwaukie on a job and it was nice,
but I've ne
Just installed an AIO/Pflo16. The build quality and attention to detail
make Sol-Ark look like what I've always considered them to be, CCC. Had one
glitch and Rick and Logan were there for me immediately. There's nothing
like talking to an engineer that designed their gear. We'll be installing a
fe
Even the industrial Generac ATS's use plastic gears now. They're awful and
parts like the gears, CPU's and sensors have been unobtanium. My preference
has been Eaton first and then Asco.
On Fri, Sep 20, 2024 at 3:24 PM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> We ra
My pump guy (he's 82 and worked in the business since he was a kid) likes
them. He tears pumps apart for fun and says they are built well but has
only about three years with them. I might give one a go since the price is
good.
On Mon, Jul 22, 2024 at 2:01 PM jay via RE-wrenches <
re-wrenches@lists
Because I work mostly alone, I'm digging the rack mounts. Dealing with 200
lb batteries takes me so much time, from receiving, loading, unloading,
schlepping, and mounting Egyptian style.
On Wed, Jul 17, 2024 at 8:19 AM Dave Angelini Offgrid Solar via RE-wrenches
wrote:
> Awesome reliability on
al?
> Thanks
> Howie
> Sun Catcher
>
>
> On Wed, Jul 17, 2024 at 9:55 AM Michael Morningstar via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I am. EG4=Yugo and AES=Mercedes.
>>
>> On Wed, Jul 17, 2024 at 5:58 AM Jeremy Rodriguez v
I am. EG4=Yugo and AES=Mercedes.
On Wed, Jul 17, 2024 at 5:58 AM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Greetings,
> Whose using the new Discover
> Rack mounted batteries?
> They look like the EG4 line up
> Pros and Cons ?
> Thanks
>
>
> Jeremy Rodriguez
>
I’ve years of experience running vfds on generator power. No issues.
Personally, I run numerous old cast iron woodworking machines that all have
5 and 10hp 3p motors with VFDs from a 15kw Kubota open frame generator. 15
second ramp up time. And my generator is single phase.
On Thu, Jul 11, 2024 at
*Dave Angelini Offgrid Solar
> "we go where powerlines don't"
><http://members.sti.net/offgridsolar/>https://offgridsolar1.com/
> <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>
> e-mail offgridso...@sti.net
> text 209 813
Hey Everybody,
I wanted to circle back on the Discover AES explosion that I reported a few
weeks ago. As far as we know, there was a thermal runaway situation. Gas
from the battery filled the power room and then ignited causing an
explosion. It was hot enough that anything plastic melted. The stee
That's all we use. High altitude, Severe conditions. Might be the best
modules we've installed.
On Fri, May 17, 2024 at 10:38 AM Sam Haraldson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Our experience with REC is similar to previous respondents. We almost
> solely installed RE
//offgridsolar1.com/
> <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>
> e-mail offgridso...@sti.net
> text 209 813 0060*
>
>
> On 2024-05-03 8:21 am, Michael Morningstar via RE-wrenches wrote:
>
> Two days ago, one of my clients came home to find the d
Two days ago, one of my clients came home to find the door of his powershed
blown off its hinges and a smoldering Discover AES. The case was still
intact and the entire room is coated with a fine graphite-like powder. The
fire department was unable/unwilling to do anything to cool the battery
down
Go back to V1.11. I had the same thing happen with an XWPRO and a Central
Maine Diesel with a DynaGen controller. Frequency and Peak to Peak was less
than perfect and the inverter, IF it would qualify the power, sounded like
a garbage disposal. Eric B at Schneider suggested reverting back to the ol
even complete. He's already had to dark
> start them several times, and now they won't even stay operational for more
> than a few minutes. The cheapo BMS lears its ugly head once again. All
> we're doing lately is fixing stuff less than 5 years old.
>
> Ray Walters
Here's a different take. Just food for thought and not necessarily a
suggestion. Those 1st or 2nd Gen 12V systems were/are for me the most
reliable and trouble free systems. I'd install one and never hear back from
my customer for a decade or more. I regularly see "rats nest" wired
12V/Trace DR/UX
Sol-Ark's applications engineers are your friends : )
On Wed, Mar 27, 2024 at 3:13 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> William,
>
> Thanks for the information on grid peak shaving. That is what I thought
> could be done. The description is a misnomer
We gave EG4 and Signature another chance after promises from their dealer
oriented support department that we could expect better service from them.
We had an EG4 BMS crap out a couple months ago after only a few months.
Lots and lots of communications with Signature and we still don’t have a
BMS o
I've been having the same thoughts about Li and off-grid systems. It used
to be that I would install a system and then hear back from the clients a
decade later when it was time for new batteries. Now, almost every other
week I'm dealing with Li related issues (that I feel obligated to pay for).
Sa
Doh!, We ran into this several months ago and no one at Schneider could
explain it. So we had to tell our client to pick their preferred generator
as there apparently could only be one. Connected to AC 2. Now I know.
On Wed, Oct 25, 2023 at 4:17 PM Kevin Pegg via RE-wrenches <
re-wrenches@lists.re
Vince,
You'll want to register with them and get the "special number". You'll
also get the grid code password. I tried reaching them two weeks ago and
last week and couldn't get through. Kinda bummed as Schneider has been my
go to for several years.
On Mon, Oct 23, 2023 at 5:29 PM Vince McClellan
Funny you should say that. One that I just installed is acting weird and
sounds horrible. Waited an hour on the phone for tech support to no avail.
Will be a really long drive back to sort things out. Never had an XW with
issues before.
On Thu, Oct 12, 2023 at 9:29 PM Kevin Pegg via RE-wrenches <
h I’m not sure how to do in a code compliance way.
>> Or
>> Not worrying about different cable lengths?
>> Or
>> Adding another conductor to the farthest batteries to compensate for VD
>> Or
>> Making all the cables the same length?
>>
>> Thx
>>
>
Or
> Making all the cables the same length?
>
> Thx
>
> Jay
>
>
>
>
>
>
>
>
>
>
>
>
> On Sep 18, 2023, at 4:37 PM, Michael Morningstar via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>
> Jay,
> I'd like to design
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
>
>
> On Mon, Sep 18, 2023 at 1:14 PM Michael Morningstar via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
I've been asked to build a back up system for a grid connected estate. We
haven't done many of these and I thought it best to ask those who have some
questions before I go about reinventing the wheel.
Here's the existing infrastructure.
1) 400amp Metered Main Distribution Panel with six 200amp fee
ell. You would not want a grid delay
>>> if it were a utility. Still, they should be able to build in that logic I
>>> would think.
>>>
>>> Jason Szumlanski
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Prof
We learned of this major deficiency after an eight unit install. No cool
down is disastrous to modern diesels. Our work around was installing a
400amp contactor and macromatic programmable relay.
On Thu, Sep 14, 2023 at 10:05 PM Jerry Shafer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wro
ly-reduce-life-electronics-half/
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
><http://members.sti.net/offgridsolar/>https://offgridsolar1.com/
> <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>
> e-mai
nd
>> bottom with a required 6" minimum spacing on both the top and bottom.
>>
>> A 12kW Outdoor with 8x8 gutter and 1" offset nipples have worked great
>> for us.
>>
>> Aloha,
>>
>> Lou Russo
>> (808) 345 6762
>>
>>
>>
&
Ditto what William said about those micro-switches. They really need to be
fine tuned
On Wed, Jul 26, 2023 at 4:29 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Mick:
>
> Square D offers a set of auxiliary contacts on the double throw switches.
> It is ordered b
Replacing SE with Conext 600-100😊, Seriously, everything will then play
nice together, and it's only a matter of time before the SE has to go.
On Sat, Jul 22, 2023 at 4:02 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi,
> I was finally able to get to the site
Guarantee you EG4 won't be around in 5 years. Their retailers like
Signature and Sovereign Solar are a joke. Bet you they won't be around long
either. I think you will find more bad experiences than good.
On Thu, Jul 13, 2023 at 4:12 PM Michael Morningstar
wrote:
> If they are going to spend tha
If they are going to spend that kind of money, ditch OB. I've never had an
Outback system, going all the way back, that didn't puke prematurely and
have issues. Discover AES and Schneider for the win. Once they are set up,
they just work.
On Thu, Jul 13, 2023 at 3:20 PM Jay via RE-wrenches <
re-wr
ontrol Panel (SCP)
> <https://solar.se.com/us/en/event/monitoring-with-tablet-solution-and-system-control-panel-scp/>
> solar.se.com
> <https://solar.se.com/us/en/event/monitoring-with-tablet-solution-and-system-control-panel-scp/>
>
>
> Thank you,
>
> Maverick
>
>
Am I missing something? Schneider has come up with a solution to the
discontinued SCP by using a tablet connected to the Insight's ethernet
port. In doing so, by utilizing that port it seems there is no longer a way
to make a wired connection to the internet.
--
Michael Morningstar
Morningstar
My question is: how/why is it that NAZ and the likes sell equipment for
less than what I pay wholesale?
On Thu, May 18, 2023 at 4:15 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Here is how I explain it to customers. Straight out of college, I was a
> financia
I just pulled out an 8048 and replaced it with a 8048A due to the lack of
AC boards for 8048s. I didn't know any better and put in a new 8048A board
and learned the hard way that they aren't cross compatible. Smoked it. If
you think you can find a board for it, it's yours.
On Wed, May 10, 2023 at
Yah, What the heck? The XW Pro/Discover AES pairing makes up 2/3s of our
installs. Right now I have a client who's Insight Home is glitching and
drops out his smartphone connection. Without the SCP He'd be in the dark. I
just purchased an SCP off of Ebay for 700.00 for a system we are building
for
>
> Can you share more about your sprinkler system and the power supply for
> it? Over the years, at least two of my customers have lost their homes
> (and PV arrays) in wild fires.
>
> Ray Walters
> Remote Solar
> On 3/13/2023 2:34 PM, Michael Morningstar via RE-wrenches
WebRelay. I use one to turn off my WEEDS (Wind Enabled Ember Dousing
System) sprinkler system via a 12V solenoid
On Mon, Mar 13, 2023 at 1:22 PM Starlight via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
>
> https://www.amazon.com/Solenoid-Control-Wireless-Contact-T-Mobile/dp/B07Q7PKW5
Yes, many Radian systems with Discover AES and Helios using the Lynk II
gateway. Lynk II takes care of AGS and activating heat pads.
On Tue, Oct 18, 2022 at 12:27 PM Wayne Irwin via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello All,
>
> Has anyone successfully coupled Outback w
Honest Question, what is an MCU board and how to tell what version it is?
On Tue, Oct 4, 2022 at 4:51 PM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi Chris
>
> The 1.1 MCU issue might have been known but they did a horrible job with
> my buddy.
>
> 7 x MCU 1.1 boards
> 1
So, what I’ve been using are ag seed tray heat mats. I have been using
almost exclusively Discover AES or Helios. We use the Lynk II gateway with
all systems and utilize its temperature controlled relays to activate the
mats. The battery calls for heat, Imagine that. With open loop systems we
use t
I"ve been running one of Jerry's delrin turbines for ten years straight. No
signs of wear at all. I've also replaced dozens of Harris turbines with APM
units. They are pretty sweet.
On Thu, Sep 15, 2022 at 4:29 PM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I’d recommend con
cutting fluid? We've had
> better luck with that in softer than steel metals.
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
>
> On 9/11/2022 7:00 PM, Michael Morningstar
We've gotten around needing UL listings for one-off in house fabrication by
running things through a licensed engineer. Right now we are building a
gutter bus which has two 1/2" x 4" x 20' copper bars in a 10" x 10" gutter.
We are using 2" x 9" x 9" UDPM plates with slots routed out for the bars as
We hang a lot of AES on wooden stud walls. Our engineer prescribed the
following: 1-5/8" strut bolted to every stud in the span. AES factory
mounting brackets bolted with 3/8" grade 8 bolts and thick strut cone nuts.
Then a support brace 3-1/4" strut which is (2) welded back to back 1-5/8"
struts (
1st line of defense: Agricultural seed tray heat mats w/ integral T-stat
2nd LOD: Empire wall heater (no electronics) w/ industrial temperature
controlled relay (TCR) (similar to a thermostat) set to 38 degrees
3rd LOD: Battery side of charge controller circuits have TCR controlled
contactors to b
Very Cool. We install on the average about two dozen <15kw generators
annually. Mostly diesel and a few Honda propane. The diesels are a hard
sell for some reason. Would love to see the return of the quality smaller
Kohler/Onans.
On Sat, Jul 2, 2022 at 9:11 AM Dana Orzel via RE-wrenches <
re-wrenc
Wrico International Eugene,Or
Expensive but top tier
On Wed, Jun 29, 2022 at 7:39 AM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello Wrenches,
>
> Does anyone have a recommendation for a small, industrial propane
> generator? Something rated for prime power with reli
We cut out the bottom plate entirely with a die grinder/cut off wheel and
then wrap the raw edge with vinyl "edge wrap" and set the inverters on top
of 10 x 10 x whatever gutters. The layout and sizes of Sol-Arks knock-outs
is screwy. Just need a bonding jumper between both enclosures. This is
comm
Circuit breaker open or closed?
On Mon, Apr 4, 2022 at 9:13 AM Chris Daum via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hey folks:
>
>
>
> We have a problem we just can’t figure out. We have a customer in OK
> with a simple array of eight Trina TSM 310-DD05H(II) modules, four sti
We almost always use the AES brackets. Often mounted to strut. You want
access to the on/off button, so some exposed conductor is inevitable. We
have also fabricated shelves for them to sit on. For 2 or more batteries in
multiples of two, we stack them so that the bottom battery has its
terminals f