We've been using manual transfer switches with the Midnite AIO's

On Fri, Jan 17, 2025 at 7:29 AM Stuart Kriendler via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Many thanks again Mac and Wrenches,
>
> This is now put to bed with confirmation the only listed 200A ATS that
> will work without a 12V switching controller that I could find around the
> $1k mark is indeed the Kohler RDT series.
> (All currently manufactured Generac, Briggs & Stratton and Cummins ATS
> options require a controller to talk to the same name brand gene to
> switch/transfer, or a Mcgiver move.)
>
> I found a supplier in Florida who gave a slight volume discount and seems
> solid.
> Here is a link to the product, pricing, specs and manual through them:
>
> https://bnhgenerators.com/product/kohler-200-amp-rdt-ats-rdt-cfnc-0200a-qs7/
>
> And another supplier option with similar pricing, and the 100A version
> readily available in case helpful:
>
> https://www.electricgeneratorsdirect.com/Kohler-RDT-CFNC-0200A-QS7/p2202.html
>
> Best to all and thanks again.
>
> Sunniest regards,
> Stuart
> 441 599 2105
>
>
> On Tue, 14 Jan 2025 at 21:02, Mac Lewis <maclew...@gmail.com> wrote:
>
>> Hi Stuart,
>>
>> The Kohler RDT switch is a much better switch for what you are doing; it
>> is a power seeking switch with no accessory device communication needed.
>> It is more expensive than the RXT switch because it has its own brain
>> board.  A Kohler tech can adjust the delays for you if needed but the
>> defaults are good.  We have a few of them out there with no issues.    They
>> have them available as service entrance rated/indoor/outdoor etc.
>>
>> Good Luck!
>>
>> On Tue, Jan 14, 2025 at 2:55 PM August Goers via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> Hi Stuart,
>>>
>>> Got it, now I see you're working with the MidNite AIO. This ATS topic
>>> came up not too long ago and I posted that we used to have success with
>>> Briggs & Stratton ATS units back when we were installing SMA Sunny Island
>>> systems. The Briggs unit does not need a control from an external source,
>>> it just switches over automatically (with a few second delay) once utility
>>> power is lost. We never had a single problem with these transfer switches.
>>>
>>> You might check them out:
>>> https://www.nationwidegenerators.com/briggs-stratton-071270-200-amp-se-rated-120-240v-1ph-ats/?srsltid=AfmBOorCds2ktOcsHUf3GWmX5ba70K-ynjOcm1iizzIW6X-9OkSVpfHA
>>>
>>> I know that Briggs went through a bankruptcy a few years ago, but maybe
>>> they're still alive and kicking now.
>>>
>>> August
>>>
>>>
>>> On Tue, Jan 14, 2025 at 1:29 PM Stuart Kriendler <
>>> stuartkriend...@gmail.com> wrote:
>>>
>>>> Much appreciated August,
>>>>
>>>> Yes, that fancy Enphase System Controller is a nice piece of kit,
>>>> overseen a few of those and it is nice they pass through the grid power if
>>>> there is an issue, most of the time.
>>>> ;-)
>>>> I'm in love with the MN AIO, the build quality is impressive and great
>>>> value for money, with the CBI breakers and features mentioned earlier etc.
>>>> all built in.
>>>> Now seen an engineering sample do the business in an rugged off-grid
>>>> scenario for a few months and feel confident it will be a great GT hybrid
>>>> option, one catch is the need for a 3rd party ATS though.
>>>> (Hoping Midnite will make one of their own in time, as well as a
>>>> wireway to marry the PowerFlo 16 and AIO, both such nicely built solid
>>>> equipment).
>>>>
>>>> Hopefully the Kohler RXT or Generac can work to keep the ATS cost below
>>>> $1k!
>>>>
>>>> Sunniest regards,
>>>> Stuart
>>>> 441 599 2105
>>>>
>>>>
>>>> On Tue, 14 Jan 2025 at 16:02, August Goers <aug...@luminalt.com> wrote:
>>>>
>>>>> Hi Stuart -
>>>>>
>>>>> Many grid tied PV/ESS manufacturers (Enphase, SolarEdge, Franklin,
>>>>> Tesla to name a few) now have a Microgrid Interconnect Device (MID) that
>>>>> essentially acts as a smart transfer switch thus eliminating the need for 
>>>>> a
>>>>> 3rd party automatic transfer switch. What brands equipment are you looking
>>>>> at?
>>>>>
>>>>> Best, August
>>>>>
>>>>> On Tue, Jan 14, 2025 at 11:10 AM Stuart Kriendler via RE-wrenches <
>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>
>>>>>> Good day Wrenches,
>>>>>>
>>>>>> 2025 looks to be the year for installing more grid tied (GT) battery
>>>>>> back up hybrid inverters on new and existing GT PV systems in a whole 
>>>>>> house
>>>>>> backup scenario
>>>>>> i.e. Utility - Hybrid Inverter - House Loads
>>>>>>
>>>>>> With these newer GT hybrids so 'sensitive', any fault on the PV side
>>>>>> can cause them to shut down, thus stopping power to the house.
>>>>>> To minimise this it seems sensible to add an ATS to the system such
>>>>>> that if/when the hybrid faults, the ATS w switch to grid power, bypass 
>>>>>> the
>>>>>> hybrid, and power the house.
>>>>>> This could save an emergency truck roll or late night phone call for
>>>>>> installers.
>>>>>>
>>>>>> Anyone have experience on good value-for-money Listed automatic
>>>>>> transfer switches that would do the job, 200A, 120/240V?
>>>>>>
>>>>>> Two name brand options that came up on the less expensive end of the
>>>>>> spectrum are:
>>>>>> - Generac
>>>>>> RXSW200A3 
>>>>>> (https://www.generac.com/residential-products/standby-generator-transfer-switches/automatic/rxsw200a3/)
>>>>>>
>>>>>> - Kohler 200-amp, Service Entrance RXT ATS | RXT-JFNC-200ASEQS4 (
>>>>>> https://www.kohler.com/content/dam/kohler-com-NA/Lifestyle/PDF/PDF-g11152.pdf
>>>>>> )
>>>>>>
>>>>>> However, they each say their ATSs must be used with the corresponding
>>>>>> generator.
>>>>>>
>>>>>> I would imagine a simple 'grid sense' functionality would mean that
>>>>>> if the hybrid's output was connected to the Grid/Normal lugs and the grid
>>>>>> was connected to the Gene/Backup lugs in the ATS it should work.
>>>>>> However I don't want to end up with an expensive surprise in a
>>>>>> relatively remote location where I operate!
>>>>>>
>>>>>> Would appreciate any feedback with experience with the above or other
>>>>>> ATS models or how people are future proofing for this scenario?
>>>>>> To do future maintenance/torque checks etc. in a GT hybrid whole home
>>>>>> backup situation, it would be nice to bypass the inverter and keep the
>>>>>> house powered for safety and homeowner convenience in general.
>>>>>>
>>>>>> Thanks and best.
>>>>>>
>>>>>> Sunniest regards,
>>>>>> Stuart
>>>>>> 441 599 2105
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>>
>>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> There are two list archives for searching. When one doesn't work, try
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>>
>>>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
>>
>> --
>>
>>
>>
>> Mac Lewis
>>
>> *"Yo solo sé que no sé nada." -Sócrates*
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Michael Morningstar


Morningstar Electric Inc

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

CSLB 1116835

mjmornings...@gmail.com
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to