Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
That's a different scenario, as a 100A genny would have a 100A OCPD. I understand that the inverter output rating is limited, but what section of code allows a 200A breaker to protect a #4 wire? On Fri, Apr 15, 2022 at 9:26 PM Jerry Shafer via RE-wrenches < re-wrenches@lists.re-wrenches.org>

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jerry Shafer via RE-wrenches
You must meet all expected source output potentials within the design and operating limits, as long as the distribution panel and connected wiring is rated for the max output of the protected source then you are good. A 200 ATS connected to a 10 kW genny does not require 2/0 as it will never meet t

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Chris Sparadeo via RE-wrenches
Hi Jason, You bring up a valid point….in an off-grid scenario with the 15k do you size the conductors to the continuous capacity, surge capacity or the OCPD of the unit? -Chris On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > P.S. IC

[RE-wrenches] Enphase

2022-04-15 Thread Jay via RE-wrenches
I’ve been following the enphase thread. I’ve used AP systems before and so far reliable and much less expensive. Their new DS3 inverters are much less expensive and larger capacity But to the point of starting voltage MPPT range and watts DS3 voltage range: DS3 S/L 16-60v, DS3 26-60v MPPT ra

[RE-wrenches] Fronius primo grid settings

2022-04-15 Thread Jay via RE-wrenches
I wonder if anyone can tell me which is the correct setting for 240v 60hz w/neutral on a fronius primo. The manual doesn’t have the same options as the inverter. I don’t need California or Hawaii settings. Thanks Jay ___ List sponsored by Redwood A

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
P.S. ICYMI, this inverter has a massive combined AC coupled and DC coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive. On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > I'm not following the wiring diagrams for this new inverter. It

Re: [RE-wrenches] Razors & Removing paint from solar modules

2022-04-15 Thread Mark Downing via RE-wrenches
That would likely happen of the pressure spray were used on the back side of the modules. From: RE-wrenches On Behalf Of Solar Energy Solutions via RE-wrenches Sent: Friday, April 15, 2022 3:12 PM To: RE-wrenches Cc: Solar Energy Solutions Subject: Re: [RE-wrenches] Razors & Removing paint fr

Re: [RE-wrenches] Razors & Removing paint from solar modules

2022-04-15 Thread Solar Energy Solutions via RE-wrenches
We have seen cells shattered…kind of cracked… yet still functioning, when we have heard of clients using pressure washers on panels. Andrew Koyaanisqatsi President Solar Energy Solutions, Inc. The BRIGHT CHOICE Since 1987, helping you and your Portland neighbors move towards an environmentally

Re: [RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Kirk Herander via RE-wrenches
Thanks that is exactly my request to Enphase, that they verify software compatibility. On Fri, Apr 15, 2022 at 12:48 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Kirk, > > We have seen many of the conversion kits not work out of the box. I > believe it is a fi

Re: [RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Jason Szumlanski via RE-wrenches
Kirk, We have seen many of the conversion kits not work out of the box. I believe it is a firmware/software mismatch issue. If you call Enphase, ask them to make sure the Envoy software is compatible with the conversion kit microinverter and update all software. This should resolve the issue. Jas

[RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Kirk Herander via RE-wrenches
I have been dealing with a legacy Enphase system ever since the installation about 11-12 years ago. And I stopped using Enphase after the massive failure rate of these first gen M190 inverters. Almost all of them have been replaced at least once, the good news is I only have about -15- of the origi

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Ray Walters via RE-wrenches
Not to sound like a commercial, but I've had good results with "Tub O'Towels" heavy duty wipes.   Its got a lemon base that seems easy on most surfaces, but it will take paint off with a few seconds of elbow grease.   Hoe Depot has them sometimes, or Northern Tool carries them too.  You'll use

[RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
I'm not following the wiring diagrams for this new inverter. It has 200A pass-through capability with an integrated 200A load disconnect. But then it says the wire gauge for the load out wiring can be #4 to 2/0. In an off-grid scenario where there is no generator, the max continuous output is 62.5

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread George McClellan via RE-wrenches
Tarps work great too! George McClellan | Senior Technical Sales Manager | REC Americas LLC 330 James Way Ste 150 | Pismo Beach, CA 93449 | USA Cell phone +1 805 704 3226 | Fax +1 805 357 6104 www.recgroup.com | george.mcclel...@recgroup.com

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Garrison via RE-wrenches
Hi Mac, I second the isopropyl alcohol (diluted), a soft cloth, and razor blade if needed. Magic erasers would probably work too, but I believe they are made from very hard microscopic crystals. Good luck. Garrison Riegel Celestar Solar LLC > On Apr 15, 2022, at 9:45 AM, Dana Orzel via RE-

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Dana Orzel via RE-wrenches
Also Latex paint come off with Isopropyl Alcohol. Dana Orzel Great Solar Works, Inc. C - 208.721.7003 d...@solarwork.com Idaho Contractor - # 028765 Idaho PV # 028374 NABCEP # 051112-136 www.greatsolarwor

[RE-wrenches] Razors & Removing paint from solar modules

2022-04-15 Thread Dana Orzel via RE-wrenches
If your use a razor only use a fresh razor blades. The moment you feel burrs stop & replace the razor as the burrs will scratch the glass. Also keep the surface always wet with a soapy solution [surfactant] to keep the surface slick & this extends the short life of a razors edge. Use a razor ha

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Chris Mason via RE-wrenches
Just a razor blade. I doubt you can take if off chemically. On Fri, Apr 15, 2022 at 9:01 AM Mac Lewis via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi Wrenches, > > We had some painters try to paint a house in 35 mph winds and (of course) > the overspray got onto some recently ins

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Maverick Brown via RE-wrenches
I’ve had good results from a combo of power washing and the Magic Eraser for paint dust in the texture of the glass. Maverick Brown Off-Grid Solar Commander since 2006 Maverick Solar Enterprises, Inc. • Solar Commander Remote Power • SunFlow Systems Cathodic Protection maver...@mavericksolar.

[RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Mac Lewis via RE-wrenches
Hi Wrenches, We had some painters try to paint a house in 35 mph winds and (of course) the overspray got onto some recently installed solar modules. They were using a latex water-based exterior paint. Are there any mild solvents you might recommend to help clean this up? Or just elbow grease?