Re: [RE-wrenches] Grid overvoltage and undervoltage issues on SMA install

2021-05-20 Thread August Goers
Hi James - Is there a long run between the inverters and the point of interconnection? As others have pointed out, it appears that the symptoms you describe are voltage drop related. If the wire size is too small it will result in voltage at the inverters going up when current starts to flow. The

Re: [RE-wrenches] Grid overvoltage and undervoltage issues on SMA install

2021-05-20 Thread Jerry Shafer
Wrenches Looks like the i verter is doing what it should 269 is out of range, what is the at meter voltage, libe loss or very high output voltage, 41 volts increase looks like resistance issues. More info would help, distance, wire size etc. Jerry Jerry On Thu, May 20, 2021, 9:52 AM James Reismil

Re: [RE-wrenches] OB VFX3524M vs regular VFX

2021-05-20 Thread Ray
Honestly we see pretty steady failures of the old VFX series too.  5 to 10 years, then rebuilds. The rebuild boards do not seem to be as robust either, we just had one fail after a little over a year.  The failure rate definitely seems to correspond to grid tie systems with either large arrays

Re: [RE-wrenches] Grid overvoltage and undervoltage issues on SMA install

2021-05-20 Thread Barton Churchill
You’ll need to either measure or calculate impedance from the inverters up to and ideally including the utility transformer. The most likely culprit are one or both are undersized. From: RE-wrenches on behalf of James Reismiller Sent: Thursday, May 20, 2021 10

Re: [RE-wrenches] SHW?

2021-05-20 Thread Christopher Warfel
We install pv and SHW. It is now about 75% 25% respectively. Actually just commissioned a two collector DB system. After 20 years, it was my first DB.  It is working great as of this late morning. I'd like to look into online monitoring of these.  We have too many customers that are not here en

[RE-wrenches] OB VFX3524M vs regular VFX

2021-05-20 Thread palumbo131m
I'm going to be upgrading on old dual inverter OutBack FX 2524 system to dual VFX3524 inverters and would prefer to not use the new R series as I have heard about problems with them. I have located only one reconditioned VFX3524 so far but I see that there are VFX3524M Marine version's available.

Re: [RE-wrenches] Grid overvoltage and undervoltage issues on SMA install

2021-05-20 Thread Kirpal
Hey James, Line 1 and Line 2 switched in the inverter combiner panel from any of the inverters? ( line 1 connected to line 2 of inverter 2 or 3 or vice versa)? Good luck! Sunny Regards, Kirpal Khalsa Oregon LRT#25 Oregon Solarworks LLC www.oregonsolarworks.com 541-299-0402 On Thu, May 20, 2021 a

[RE-wrenches] Grid overvoltage and undervoltage issues on SMA install

2021-05-20 Thread James Reismiller
Hi Folks, I'm wondering if anybody has ideas on what could be causing grid over/undervoltage errors on an install we did about a year ago that now has these issues. The site is a 24 kW DC ground mount array with (3) SMA SB7.0-1SP-US-40 inverters. I've checked and done the following: 1. Measu