You’ll need to either measure or calculate impedance from the inverters up to 
and ideally including the utility transformer. The most likely culprit are one 
or both are undersized.

________________________________
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of 
James Reismiller <ja...@abundantsolar.com>
Sent: Thursday, May 20, 2021 10:52:06 AM
To: re-wrenches@lists.re-wrenches.org <re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Grid overvoltage and undervoltage issues on SMA install


Hi Folks,

I’m wondering if anybody has ideas on what could be causing grid 
over/undervoltage errors on an install we did about a year ago that now has 
these issues. The site is a 24 kW DC ground mount array with (3) SMA 
SB7.0-1SP-US-40 inverters. I’ve checked and done the following:

  1.  Measured voltage min/max at inverter terminals and AC combiner. Min – 
228VAC (with no inverter output) Max - 269 VAC (when inverter trying to 
connect)!
  2.  Had utility check service and transformer with load meter (with no PV 
running). No issues found and utility engineer stated he thinks it’s on our 
side.
  3.  Checked all AC connections including neutral (seemed like neutral issue) 
from inverters back to supply-side tap (fused disco).
  4.  Changed SMA upper voltage window in grid guard settings to 272V max and 
264V reconnection. This helped for a while but now is faulting again.



Have any of you ran into this issue and how did you solve it? Or what’s the 
next thing to check?



Thanks in advance!



Be Well,

James Reismiller

He/Him/His

NABCEP Certified Solar PV Installer®

Abundant Solar

541-231-8072  xt. 3

CCB#175919

[cid:image002.png@01D74D5D.CA065970]

www.abundantsolar.com<https://us-west-2.protection.sophos.com?d=abundantsolar.com&u=aHR0cDovL3d3dy5hYnVuZGFudHNvbGFyLmNvbS9hYnVuZGFudHNvbGFyL0hvbWUuaHRtbA==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=UlRoM0ZoK3IzYnVOempNMktCUE5mRHpIU25SdTczdmlXZEFHU1p4dmJTND0=&h=3abbc334e64d4897a91541320d5af142>



"Don't get me wrong: I love nuclear energy! It's just that I prefer fusion to 
fission. And it just so happens that there's an enormous fusion reactor safely 
banked a few million miles from us. It delivers more than we could ever use in 
just about 8 minutes. And it's wireless!"



~William McDonough


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to