Re: [RE-wrenches] Midnite solar Charge controllers

2014-02-17 Thread Jerry Shafer
This is good to know thanks On Feb 17, 2014 8:30 PM, "b...@midnitesolar.com" wrote: > > All CC's have their problems and MidNite has had their share, but losing > or forgetting their programming has not > been one of them that I'm aware of. > > If it is a standard Classic with MNGP display, don't

Re: [RE-wrenches] Midnite solar Charge controllers

2014-02-17 Thread Ray Walters
Volatile memory was a pet peeve of mine with the Trace SW inverters. I quit even trying to program them, because they would always end up getting reset anyway. However, I've tested this feature on the Midnite Classics and I could not get them to drop programming. I used the computer app, set

Re: [RE-wrenches] Midnite solar Charge controllers

2014-02-17 Thread b...@midnitesolar.com
All CC's have their problems and MidNite has had their share, but losing or forgetting their programming has not been one of them that I'm aware of. If it is a standard Classic with MNGP display, don't forget to press ENTER after setting parameters so that the Classic remembers those setting

[RE-wrenches] Midnite solar Charge controllers

2014-02-17 Thread Jerry Shafer
Has anyone had an issue with Midnite solar Charge controllers loosing programming. I have had Out back FM 80 do this and it was an software issue they fixed it. Now I have the same thing with midnite either that or the customer is messing with it and this is also a good possibility but before I go

Re: [RE-wrenches] AC Back feed from Radian.

2014-02-17 Thread Chris Mason
I'm a Generac service tech and have some experience installing gaseous generators (their term). I don't have any experience with freezing, being in the Caribbean. Virtually every installation not designed by a tech will have fuel piping that is too small. The 20KW Generac Guardian needs a minimum 3

Re: [RE-wrenches] AC Back feed from Radian.

2014-02-17 Thread Ray Walters
Wow, so would you need a small expansion tank to dampen that out? IS that even allowed on LPG? What was the cure? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 2/17/2014 4:19 PM, toddc...@finestplanet.com wrote:

Re: [RE-wrenches] California State Fire Marshal's "Solar Photovoltaic Installation Guidelines

2014-02-17 Thread Solar Energy Solutions
Dear Esteemed Colleagues, The purpose of this email is to start sharing solutions to the roof top access issue.  I am not an expert in fire fighting.  However, one of our best clientele demographic is firefighters.  I have learned the following from them.   1) Firefighters avoid jumping on roofs

Re: [RE-wrenches] AC Back feed from Radian.

2014-02-17 Thread toddcory
to further complicate things, i have seen "regulator oscillation" problems with 2 in series. todd On Monday, February 17, 2014 2:30pm, "Ray Walters" said: Alot of these generator setups need 2 regulators, so usually the regular one stays at the tank, size the pipe for t

Re: [RE-wrenches] wrenches] AC Backfeed from Radian.

2014-02-17 Thread john
Thanks for the feedback. Turned out to be 3 separate issues. The AC backfeed turned out to be mostly caused by a missing neutral to ground bond. With that corrected, the backfeed dropped from 30 volts to 2 volts on one leg only... still a puzzle. Other issues were a snow and ice covered reg

Re: [RE-wrenches] AC Back feed from Radian.

2014-02-17 Thread Ray Walters
Alot of these generator setups need 2 regulators, so usually the regular one stays at the tank, size the pipe for the flow rate ( just like wire and amps;-) .) and put the 2nd regulator right at the generator. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master E

Re: [RE-wrenches] AC Back feed from Radian.

2014-02-17 Thread Larry Crutcher, Starlight Solar Power Systems
Ditto Tom, seen this too often in Mexico. I carry a manometer to make check the pressure at the LP input to the generator with the engine running. Make sure it is at/above 11" WC when it starts to act up. If the regulator is at the tank, long vapor runs can cause too much pressure loss. Larry

Re: [RE-wrenches] AC Backfeed from Radian.

2014-02-17 Thread Jerry Shafer
If you disconnect the leads to the Benny from at the inverter do you still have this condition. I had a battery charged supply (ac) in the same conduit as the remote start and the transient voltage would be enough to signal z start up. Your issue is a little different but it might still be transien

Re: [RE-wrenches] AC Backfeed from Radian.

2014-02-17 Thread Chris Worcester
Hi John, If this is the LPG unit, I have had really long cold days here in Truckee, diagnosing erratic engine behavior, trying all sorts of motor diagnostics, as we could get her running when we arrived after the sub zero nights, waiting a bit for the sun to warm up enough to hold a wrench with

Re: [RE-wrenches] Spacing between ground mounted sub-arrays at 48.5 degrees N latitude

2014-02-17 Thread Chris Mason
If you are using Sketchup for solar, you should be using the Skelion plugin. It will compute and draw the solar modules on any surface based on your preferred module, tilt angle and azimuth. We do all our quotes this way. ___ List sponsored by Home Power

Re: [RE-wrenches] Spacing between ground mounted sub-arrays at 48.5 degrees N latitude

2014-02-17 Thread Jason Szumlanski
Here's the Sketchup animation output from the same model with three arrays at 35'6" spacing from 8am - 3pm. http://www.youtube.com/watch?v=ofBmpk1tQ7Q Jason Szumlanski On Sun, Feb 16, 2014 at 7:26 PM, Jason Szumlanski wrote: > I would never present something like this to a customer, but this

Re: [RE-wrenches] AC Backfeed from Radian.

2014-02-17 Thread dan
Have the genny guy check the valves. and control fuse (and holders) for intermittent contact.Dan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44 Original Message Subject: Re: [RE-wrenches] AC Backfeed from Radian. From: Tump

Re: [RE-wrenches] AC Backfeed from Radian.

2014-02-17 Thread Tump