[RE-wrenches] Charge Control in AC coupled system

2010-10-28 Thread Doug Wells


Wrenches,

Howie, good to see you probing this issue.
I have an upcoming system as well that is considering a micro-grid approach.
My question would be, is the Outback not able to sell back and charge  
at the same time.  I understand that with power present on the ac  
output terminal the inverter will try to charge the battery.  But  
doesn't the unit also try to sell back on the AC output terminal.   
Most Outback systems will sell down to the float voltage in a battery  
back up situation that is grid connected.  Does all of the DC  
connected array stop selling back with the Sunny Boys going full steam.
For example.  Lets imagine we have 4 kW connected to an Outback dual  
inverter grid connected battery back up and then add 4 kW connected to  
a Sunny Boy in a micro-grid format.  When the sun is shining---and all  
the loads in the critical panel are being met---that the Sunny Boy  
overpowers the Outbacks and 1. Charges the batteries and 2.(my  
question) overpowers the Outback's ability to sell to grid in its  
traditional format?

As always the guidance of the "List" is greatly appreciated.
Thanks


Doug Wells
The Solar Specialists
www.thesolarspecialists.com
802-498-5856
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Generator for off grid

2011-01-24 Thread Doug Wells


Randy,

I have seen issues with Kohler's as well.  But some of them perform well.
When Kohler changed their warranty I had a meeting with the company  
owner that installs and services their units.
We decided on a middle ground.  Rather than moving all off grid  
systems to a different genset, we install Kohlers in their territory.

They back the Kohler -in house- with one year P @ L and or 2000 hours.
Might be an option for you.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
NABCEP Certified
Solar Heating License

www.thesolarspecialists.com
802-498-5856
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Heavy Duty Modules?

2011-04-13 Thread Doug Wells



Wrenches,

Can anyone recommend a panel that is built with more strength or  
ability to handle greater load.
I am installing on a shallow pitched roof and am concerned about snow  
build up in this particular location.

I know you guys out in the Sierra's get a lot more snow than we do.
What modules are up to the challenge?
Are there any new military spec modules like the old MSX 120's?
Any experience or guidance is appreciated.

Doug Wells
Morrisville, VT 05661
NABCEP Certified PV
Vermont Solar Partner
The Solar Specialists
www.thesolarspecialists.com
802-498-5856
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tall L-feet

2011-04-14 Thread Doug Wells


Jim,

Ecofasteners makes a variety of feet attachments.
At one point they made up to 6" feet.
Worth a shot if your looking for prefab.
http://www.ecofastensolar.com/


Doug Wells
The Solar Specialists
www.thesolarspecialists.com
802-498-5856
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Insulated Roofing Approaches

2011-11-04 Thread Doug Wells
Wrenches,

We have a project that will involve installing arrays on storage units.
The roof is metal, over 1 1/2" rigid insulation, over 2x8 rafters.
We have come up with a couple solutions, but thought it wise to consult here.
Has anybody else installed on this type of roofing?
What was your approach?
Thank you for any insight or experience.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Doug Wells
Ray,

I agree with what you have calculated, but the temp. coef. listed is for a Voc. 
 For voltage sag, the temp. value would be a Vmp value and I don't know how 
much of a difference that makes.   I have seen some manufacturers offer a temp. 
coefficient for Vmp as well as Voc.  Not sure what the difference would be, but 
if it gets down to a few volts with the PE, it is would be worth checking.  

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

On Nov 29, 2011, at 5:55 PM, Ray Walters wrote:

I'm prepping for a class on this very subject tonight, so I'll just wrap up 
everybody's good points:
V min = Vmpp x (1- temp diff x Temp coefficient)

So first, I'd take your ambient temp from ASHRAE Extreme Annual Mean Maximum, 
then add Scott's adder (ie roof mount off 6"  = +30C) so let's say the ASHRAE # 
is 35C, then you have 30 + 35 = 65C cell temp
then, 65C - 25C(STC) = a differential of 40 deg C from standard test conditions

The Aug/ Sept 2010 edition of Solar Pro shows the coefficients for numerous 
modules, 
Solar world for example is -0.33 %/degC

With a 40 degC differential then, the voltage would change by 40 x .33, or 13.2%

So just assuming Vmpp =  35v, the adjustment would be 35v x (100%-13.2%), or 
86.8% of 35v, 
which gives a Volt min of 30.4 v

Somebody please correct my math if I got that wrong.
Also probably more interesting is the actual Power coefficient, which shows the 
total power losses from higher temperatures, not just voltage. The calculation 
would be similar.

Ray

On 11/29/2011 2:07 PM, Darryl Thayer wrote:
> 
> I am on road so I have no texts with me, but the same formula applies about 
> 0.4% per degree (less voltage) or use the module label  voltage coefficent.  
> However you must use the MPPT voltage and the temperature = (temperature 
> ambient (2% high) plus roof temperature warming)  The roof temperature is 
> hard to find good values because it depends upon spacing between roof and 
> module.  I add 15 deg C for most situations.  
>  
> Best I can do from memory.
> DT
> 
> From: Kirk Herander 
> To: RE-wrenches  
> Sent: Tuesday, November 29, 2011 1:48 PM
> Subject: [RE-wrenches] calculating low string voltage
> 
> I am in debate with a PE over calculation of low voltage of a series string 
> on a hot day. He insists that an arbitrary high cell temp is factored in, not 
> just ambient temperature. Could someone please give an accepted formula for 
> this calculation? Thanks. I cannot find a clear reference to low voltage 
> calculation on a hot day (but every reference material is clear on how to 
> calculate high voltage on a cold day).
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified installer Charter Member
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
>  
> 
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> 
> 
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] federal credit clarification

2009-05-04 Thread Doug Wells

Roger,

I don't have any definitives either.  Have been hounding the IRS for a  
while now.

I did hear this weekend that the grant will be 80% of the credit value.
Again, this is not a definitive, just what I hear.
Makes sense I guess.
What this will do is allow some of my clients to get loans for a  
period of one year on the amount of the grant.
They can then pay off that part of the loan next year, and leave the  
balance in a low interest program.

That is if Uncle Sam ever cuts the checks.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] module frame separation

2009-06-24 Thread Doug Wells

William,

I have done the procedure before.
I used RTV silicone.
The hard part was cleaning out some of the old sealant in the frame.
After seeing enough modules that look like they were sealed by  
preschoolers, you might end up with a longer lasting seal than the  
manufacturer.


Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Broken Modules

2009-08-03 Thread Doug Wells

Wrenches,

I am curious what other installers are doing with broken modules?
I know some manufacturers are starting recycling programs.


Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding of hot water collectors

2009-09-21 Thread Doug Wells

Kirk,

What is his logic?
Are you running the circulator with PV mounted on the collectors?
Is the house plumbing grounded?

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NABCEP

2009-11-30 Thread Doug Wells

William,

I agree that the value of NABCEP is mixed.  I would like to think that  
it is still a benchmark.
To me the importance of NABCEP has not been the test, but the  
prerequisites to take the test.
A test is just a test and I have always felt that they have limited  
value.  But experience is different.
When I applied you had to have 3 years of experience installing(in my  
track).  And the jobs that you used had to be lead installs.
Not just, "yeah I was on a crew for a couple jobs.  Or I have "some  
experience" installing.  I feel it important to understand the job  
from beginning to end.

Design, Safety, Installs and Commissioning.
The more they water down the experience component to fast track eager  
installers, the less the certification will mean.


Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] single string of batts: must the interconnects be inverter size cables?

2010-02-20 Thread Doug Wells

I have always used 4/0 through out the bank.
I guess that I have had to replace to many dead batteries at this point.
If you are under sizing the parallel strings, what happens when a cell  
fails?  or 2 cells fail.

Now all the current would be carried by one string.
If you are running equal lengths to a buss bar, it might make sense to  
put a current limiting fuse on each parallel run before the bus.
However, this would pretty much negate any money save on downsizing  
the copper.

So what is really gained?

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SWH - mixing valves

2010-05-19 Thread Doug Wells

Kelly,

I have also seen mixing valves get leaky over time.  Many mixing  
valves are designed for controlled input from a boiler at steady 140  
degree temps.  It is not uncommon for SHW tanks to reach 180+ degrees  
in certain conditions.  If exposed to these higher temps the valves  
can begin to loose accuracy.  Usually they are designed to "fault"  
into the cold position, so the begin to leak in a little cold and the  
client will complain about low temps at the faucet/shower.


Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

On May 19, 2010, at 2:14 AM, Kelly Keilwitz, Whidbey Sun & Wind wrote:


Thermal wrenches,
I'm having an ongoing issue with mixing valves in my own system not  
keeping a steady mix domestic HW temperature as the tank temperature  
varies with solar heating. If I set it for (say) 122˚F mix when the  
tank is 135˚, it seems to hold that differential at all tank temps -  
i.e. when the tank is hotter the mix is too hot (sometimes  
dangerously so), and when colder the mix is too cold for a  
comfortable shower. Thus, I need to change the setting all the time.


I'm now using a Honeywell valve with a 90˚ - 145˚ range. This is a  
replacement for a valve with a wider range that acted the same way.  
Any ideas,  suggestions for better valves, or?


This has me wondering how many of our SWH customers are experiencing  
a similar thing, but just aren't bothered enough to say anything. We  
seem to have encountered many plumbing situations where the mixing  
valve allowed weird backflow or siphoning situations to mess with  
system operation, especially with HW recirculation. I thought I had  
all such causes eliminated on my system, but maybe not.


Thanks for sharing your experience with such matters.
-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
ke...@whidbeysunwind.com
360-678-7131




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org









___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] double-insulated PV wire

2013-08-31 Thread Doug Wells
Marco,

Last we purchased both from USA wire and cable in Austin.
Under $5 per mated pair and pins for oversized MC4.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town, limited time only

2013-12-09 Thread Doug Wells
Richard,

I agree.  I caught part of the streaming as well. 
Thanks for sharing.
Bringing lightning protection into the discussion is a whole other can of worms.
He made a variety of assumptions.
1.  That the auxiliary rods were not bonded.  For instance, I was trained in 
the exact opposite manner for ground mounts and off grid.  Installing a rod at 
each pole mount, inverter and generator.  But then bonding all of these rods 
together, with the intention of keeping all metal, modules, etc in the entire 
system at the same potential.  This approach seems to really be echoing his own 
comments of keeping everything underground bonded.  The important part seems to 
be having the DC electrical bonding, GFI etc and the AC neutral bond in only 
one location.  
2.  Ground lightning strikes will create differences in potential on all 
conductors.  The insulation on most conductors buried in conduit is only good 
to 600 to 1000 volts at best.  If there is a strike creating 100,000's of volts 
then all conductors will surely see current and voltage spikes.  This is why we 
always install Surge Arrestors.
3.  While I can appreciate the physics of lightning protection, I have it on my 
house, I am not so sure about its impact on a large PV array.  I have a hard 
time accepting that a 1-2 foot spike of metal on the roof connected directly to 
ground will handle anything near a direct strike like he showed in the picture. 
 Unfortunately, in that regard you get hit, or you don't.  In fact, some 
lightning folks will admit that lightning protection can encourage the passage 
of some strikes.  But the question here seems to be ---1.  Is 1000 ft2 of 
aluminum rectangles, racking and wire, less conductive than a 2 foot metal 
spike.  And is the extra 20-100 feet that the grounds pass to the rod, really 
enough to resist current in a strike.  2.  If logic holds that a lightning 
protection system has merit, then wouldn't bringing every rail to ground at 
multiple points and then bonding them all together do the same thing.  
I am not saying that this is the way it should be done, but making the point 
that it is essentially the same thing. 
So, I respect Mike and what he is trying to do for many people, which is 
provide clear and accurate training materials.
However, I agree with Richard that I would like to hear from all the voices in 
the industry that have their minds around this as well.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

On Dec 9, 2013, at 9:21 AM, Richard L Ratico wrote:

I watched most of the streaming video of Mike Holt and six PV industry
professionals this weekend. The most interesting aspect of it was Mr. Holt's
very dramatic build up to the Sunday discussion of Article 690.47(D) which
brings back the requirement for an auxiliary grounding electrode for PV arrays.
He used everything short of drum rolls to build anticipation for this part of
the presentation.

Having personally contributed a short piece on this subject for SolarPro
magazine along with Bill Brooks and John Wiles in 2008, I looked forward to this
discussion. Finally, midday Sunday, instead of a discussion of an important and
controversial part of the 2014 code, we received a rant by Mr. Holt demanding an
immediate and unprecedented withdrawal of the article. 

Prior to his remarks, in contrast to the preceding article discussions, Mr. Holt
asked that the guest panel not make any comments that would explain how the
requirement came to return to the code after being eliminated in the 2011
edition, or any comment that might "confuse" the issue. To my very great
surprise and disappointment, they complied, uttering not a single word, nodding
their heads and moving on to the next article.

After all the buildup by Mr. Holt, the "discussion" amounted to his monolog,
which if parsed, though stated to be for safety concerns, seemed primarily an
exercise designed to sell his books, videos and consulting services on
grounding. This was of course expected. The weekend live streaming was
generously offered free of charge, a rare opportunity to hear current PV expert
opinion on the NEC. My concern is that Mr. Holt's control of the process here
inhibited the dialog that should have taken place.

There are significant implications of allowing his opinion to go unchallenged.
Is there, or is there not, any merit in 690.47(D)? Could the language be better?
Could the requirement be modified to make it better rather than simply
discarding it? Does accepting his argument mean all those systems installed
according to the 2008 code are unsafe?

Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better to
carefully think through and discuss the issue, in contrast to what was permitted
on his "show"?

Dick Ratico
Solarwind Electric


--- You

Re: [RE-wrenches] Outback Chargers

2014-02-11 Thread Doug Wells
Kevin,

I am curious about what you are seeing on the Outbacks as well.
Have dozens of these out in the field.  They have been pretty reliable for me.
The biggest issue that I have had with them is when the inverters are 
transferring from generator charging back to inversion.
If you leave this at the factory default, 1 s, you will see light flicker, and 
sensitive electronics will go into error.
This transfer rate can be adjusted down and has cured most of the power quality 
issues with the battery charging.
A different issue than harmonics under load, but it might help.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] DC Fusing/Breakers for Battery Circuits

2014-02-11 Thread Doug Wells
Dan,

Wanted to respond to your comment about wooden battery boxes.
I have many of them in the field and have never had an issue.
Interestingly,  I alway had the perspective, why put something with huge 
current capabilities in a conductive box?
But, I will certainly second the need for series fusing.  
Seems like cheap insurance and I put it in all battery systems both on and off 
grid.
On the fire hazard, I am not so sure.  Hydrogen won't combust until a 
concentration of greater than 4%.
Per NEC, I try to keep hydrogen level below this point.  In recent years I have 
begun installing 2 active vents in all system, in case of failure.
Again... cheap insurance.  This is even on battery banks as small as 700AH.
So, I hear your concern and maybe some kind of firewall would be wise.
But, I don't see wood boxes as any great threat if done well.
Maybe I am slightly numbed after witnessing all of the crazy home brew battery 
set ups in the back woods here.
Have seen some very sketchy off grid battery installations.


Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Watsun problem

2014-09-23 Thread Doug Wells
Jesse,

Have had this happen.
Can be a couple things.
There are little plastic pieces inside the control box that have contacts.  
These can be adjusted.
You will need to get at the control box and open it.
Wattsun can walk you through it.  If not they will send you a new controller. 
Same thing can happen in the N-S place, but it is usually a sign of wear on the 
plastic nut, yes plastic, in the actuator arm.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

On Sep 22, 2014, at 12:30 PM, Solar wrote:

Hello,

I am having an issue with a Watsun dual axis tracker. It is a 24VDC model, run 
of a battery bank that is charged through an outback inverters connection to 
the grid. So the battery voltage is always at 24V. The tracker will run fine 
for a couple days then it will get stuck in the east facing direction. I can 
make it track by switching the control box to "Manual Control Mode" and then 
moving the array in any direction for a second or two and then switching it 
back to "Automatic Control Mode". It will then track for a couple days and get 
stuck in the east direction again. 

Everything is greased regularly, and the voltage at the motors is always where 
it needs to be. I haven't noticed anything binding the tracker in the east 
direction and it seems like to sensor is fine because it tracks after I use the 
steps I described above to move it. 

Any thoughts?

Thanks as always,

Jesse  

Sent from my iPhone
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] 3" Pipe Fittings/Pinning

2015-05-07 Thread Doug Wells
Adam,

We have never pinned the pipe directly.
But we have pinned into ledge with a short but wide sono tube.
Cold Rolled steel rods through the 3" pipes to lock into the pour.
In this case we let pipe condensate drain into small sand bed under the 
concrete pour.
Extremely solid install in windy location on ledge.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Interstate L-16 vs Trojan L-16REB

2012-02-18 Thread Doug Wells
Maverick,

"But you would think after 20 years, inverter manufacturers would make some 
software similar to generator cycling to handle this cycling issue. "

I believe that the XW Inverters have this ability in sell mode.  There is 
traditional sell voltage.  And then there is a setting that puts the batteries 
through a traditional bulk cycle while still "selling" back any excess energy.  
The next question would be, is this better for battery longevity.  Seems like a 
hybrid of the two would be ideal.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Smart grid grid-connected compatibility

2012-07-09 Thread Doug Wells
Kent,

I went through a similar situation with an Enphase system.  With a little 
discussion we decided that the easiest change is on the Utility side.  We 
encouraged the utility to put all solar systems with Smart metering on a 
different schedule.  Now the solar residence is only pinged at night when the 
frequency shift wont cause the inverters to drop out.
I wonder how many string inverters are doing the same thing but go unnoticed.  
The Enlighten graphs make detection of this event very evident as it looks like 
a huge crash every day at the exact same time.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] bubbling Sanyo modules

2012-12-04 Thread Doug Wells
Randy,

We installed Sanyo's for a couple seasons and I have one job with similar 
bubbling.  The bubbles have grown pretty large, but Sanyo feels that it is not 
a warranty claim until the module fails.  I think that one module with this 
issue along the frame will eventually fail.  But we are past the 2 year 
warranty of defects at this point.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

On Dec 4, 2012, at 3:07 PM, Randy wrote:

Hi Wrenches,
I have some Sanyo HIT modules in operation since 2006, that are bubbling in
the back. The bubbles are small perfectly rectangular shapes, smaller than
the cell, a few per module. I put an IR camera on it and didn't see any
additional heat. I also did an IV test and got good results.  Anyone seen
something like this that led to a problem. (question mark) My keyboard
question mark doesn't work after I spilled tea on my keyboard.
Thanks
Randy

Randy Sadewic
Positive Energy

Office: 505 424-1112
Cell:505 570-0137

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] CIS mods

2013-02-18 Thread Doug Wells
Ok so its a reading night.
There are a bunch of very good papers about this effect on all the different 
types of modules.
www1.eere.energy.gov/…dfs/pvmrw2011_p25_tf_dunn.pdf
Best summary of Soaking would be :   controlled exposure to light under 
controlled environmental conditions.
The "soaking" seems to come from exposing the panel to light for --extended-- 
periods.
Thus finding the effects on the panel after it has reached a critical point of 
light exposure.
Like a sponge, the panel has been fully soaked with light.
Then they observe effects.  Some pretty interesting effects in some panels.
Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] CIS mods

2013-02-19 Thread Doug Wells
Carl,

Everything you said is true, but it does not answer the original question fully.
It is more about the variation in electrical output than long term degradation.
If I had to summarize it a different way it would be this.
Flash testing a CIGS module to STC will give you certain voltages and ISC 
results.
However, CIGS take longer to stabilize electrically.  So exposing them to light 
for minutes or hours effects the voltages and current results.
The CIGS don't reach peak levels until the modules have been fully "soaked" in 
light.
The time it takes to soak the modules and the intensity of the effects depends 
not only on the different module types, but specific manufacturing approaches.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] crystalline VS uni-solar and beyond

2008-11-03 Thread Doug Wells

How about the longevity?
This is the one area that has not been tested.
Crystalline cells have proven their longevity for the most part.   
Their weakness seems to be sealants and gaskets more than cell  
longevity.

How will the amorphous panels be producing in 20 years?
Is this why Sanyo has kept its warranty at 20 years for its cell  
design?(and I like their panels)

Thoughts?

Doug Wells
The Solar Specialists
Worcester, VT 05682
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Back feeding battery inverter with grid-tie inverter

2009-01-19 Thread Doug Wells

I was excited about using a new Apollo controller.
Did they ever come up with a listed GFI/breaker setup for that high of  
a voltage?


Doug Wells
The Solar Specialists
Worcester, VT 05682
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sanyo Bi-facial

2009-04-14 Thread Doug Wells

Bill,

I am not going to go off about Sanyo modules, especially the bifacial  
brand.  However I will say this.
I have installed a lot of residential systems with their panels.  I  
installed a system at a retired engineers home last summer and he is  
keeping very close records of production.  We are commonly seeing  
production which is at or above nameplate rating ON THE AC SIDE.  A  
3.6 kW array is producing 3400 to 4,000 watts AC on cold sunny days.   
This is not the norm in PV production in my opinion.

This brings up 2 questions for me
	1.  Why the hell are very intelligent engineers overloading inverters  
with DC production.  I know the easy answer is Nameplate DC rating for  
incentive programs.
	2.  Is the multi-junction Amorphous approach all pumped up the first  
5 years and then going to let go in year 18?


Thoughts experience?  Can't deny the early production in VT.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org