I have always used 4/0 through out the bank.
I guess that I have had to replace to many dead batteries at this point.
If you are under sizing the parallel strings, what happens when a cell
fails? or 2 cells fail.
Now all the current would be carried by one string.
If you are running equal lengths to a buss bar, it might make sense to
put a current limiting fuse on each parallel run before the bus.
However, this would pretty much negate any money save on downsizing
the copper.
So what is really gained?