On Thu, Sep 4, 2025 at 5:48 PM Blair May via RE-wrenches < [email protected]> wrote:
> I use Cobra X flex and the X Flex 150 wire and have found it to be great > to work w/ and it offers larger ampacity ratings. XFlex150 #6AWH is ~150A > > Note that the ampacity of Cobra X flex for NEC applications would not be 150 amps or the 118 amps Cobra lists in the specifications. For NEC purposes it is a MTW or THW type. THW type would be rated for 65 amps at a 75 degree C termination temperature. There are different sets of rules that wire ampacity has to play by. NEC is very conservative. When the same wire is used as appliance wiring material (AWM) is where you can sometimes get those really high ampacities. But for hooking up batteries and inverters and building wiring and the like ... you only get 65 amps (more or less). This is a pretty common sales tactic that you will see on a lot of wires. Ampacities advertised under AWM conditions and not NEC conditions.
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org