Well, I think if wiring of a ground mounted system looks like a jungle gym, then something is wrong.

On 2/18/2025 11:32 AM, Glenn wrote:
Rarely are AC electrical circuits and equipment placed adjacent to a residence in a cleared field where there may be children thinking it looks like a jungle gym either...

-Glenn

On Feb 18, 2025 11:23, Christopher Warfel via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

    I think the 8' rule for this is a little bizarre. I can have ac
    circuits lower than 8' all through my basement, attic and so
    forth, but this barrier requirement for dc conductors that have
    robust jackets and no exposed live connections has been hard to
    justify.  Christopher Warfel

    On 2/18/2025 12:25 AM, William Miller via RE-wrenches wrote:

        Tyrone:

        You raise an excellent point. Wire guarding is required on
        ground mount arrays
        
<https://millersolar.com/MillerSolar/case_studies/18%20Wire_shielding_on_ground_mounted_PV_arrays/Wire_shielding_on_ground_mounts.html>,
        although the language is vague and the industry does not
        provide many hardware solutions.  Also, in our area the
        enforcement
        
<https://millersolar.com/MillerSolar/case_studies/18%20Wire_shielding_on_ground_mounted_PV_arrays/SLO_County.html>
        of the code on this practice is non-existent.  I suspect this
        is true in many regions.  Improvements need to be made.

        William Miller

        Miller Solar

        17395 Oak Road, Atascadero, CA 93422

        805-438-5600

        www.millersolar.com <http://www.millersolar.com/>

        CA Lic. 773985

        *From:*Tyrone Houck [mailto:tyroneho...@gmail.com]
        *Sent:* Monday, February 17, 2025 8:59 PM
        *To:* will...@millersolar.com; RE-wrenches
        *Subject:* Re: [RE-wrenches] RSS: Is it necessary?

        As far as ground mounted arrays are concerned there is one
        clear protection mandated by the NEC-the requirement for
        protection from physical damage for all conductors under 8'..
        although this isn't as specific or redundant as rapid shutdown
        requirements, it typically means conduit or at least some kind
        of physical barrier with the intention often referenced as
        protection for children or other unqualified personnel. Not
        sure if that fits into the point you were making but it seems
        worth mentioning.

        Sunny Regards,

        Tyrone Houck

        Oregon Solarworks LLC

        CCB #204937 LRT #076

        541-787-1366

        tyr...@oregonsolarworks.com


        On Mon, Feb 17, 2025, 8:42 PM William Miller via RE-wrenches
        <re-wrenches@lists.re-wrenches.org> wrote:

            Rebekah:

            Thank you for your post.

            I have looked at UL3741 over and over.  Here is what I
            have gleaned:  After module level RSS was mandated there
            was a reevaluation of what voltages were actually
            dangerous for firefighters to be exposed to.  It turns out
            80 VDC is not dangerous and, given all of the
            circumstances for firefighters, exposure to voltages that
            are much higher is safe enough.  For some reason I have
            not yet grasped, all of the components need to be matched
            and tested to achieve the hallowed UL3741 rating.

            Module level RSS would have presented a big enough
            upheaval in the industry if the equipment needed to comply
            was safe and reliable. There is evidence that in many
            cases it may not be, and that amplifies the skepticism
            many feel about the current solutions, and frankly, any
            future solutions.

            It appears the code making panel, when writing the
            original module level RSS requirements, may have been a
            bit “chicken little” about the need for RSS.  This
            presents a real credibility issue for code makers.  You
            are seeing that credibility problem reflected in the
            discussions here on this forum.  Given the back-peddling,
            how can we understand and believe what is really necessary?

            Forgive me for being skeptical, but why is it that systems
            with components that have been tested together are
            demonstrably safer than any collection of high quality
            components installed carefully and competently?

            In my mind there is another disconnect here (pun
            intended):  I can put high voltage, arc producing and
            sustaining wiring on a residential roof or free-standing
            rack and not be required to protect that wiring in any
            specific manner.  If I were to install a 240VAC,
            over-current protected and de-energizeable air
            conditioning feeder without conduit, I would be red-tagged
            in a hot second.  It may be that fire-fighters in
            protective clothing can withstand voltage above 80VDC, but
            can children not wearing protective “turn-out” clothing? 
            Children mess around on roofs and underneath ground-mount
            arrays.  Why is the NEC not protecting them by mandating
            specific, listed and tested wire management and guarding
            systems?

            Thank you very much and I look forward to your reply.

            Sincerely,

            William Miller

            Miller Solar

            17395 Oak Road, Atascadero, CA 93422

            805-438-5600

            www.millersolar.com <http://www.millersolar.com/>

            CA Lic. 773985

            *From:*RE-wrenches
            [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
            Behalf Of *Rebekah Hren via RE-wrenches
            *Sent:* Monday, February 17, 2025 10:26 AM
            *To:* RE-wrenches
            *Cc:* Rebekah Hren
            *Subject:* Re: [RE-wrenches] RSS: Is it necessary?

            I read the wrenches post regularly, as does Brian Mehalic.
            We have both been on CMP-4  (responsible for Article 690)
            for the past three code cycles. I believe a few other CMP
            members probably read too. The International Association
            of Firefighters ("largest and most influential labor
            unions in North America") is represented on CMP-4 and yes
            they do have had a lot to say about this issue.

            This is definitely not the first time we have heard that
            certain RS devices are on balance causing more trouble
            than they are curing  - though on the other hand some
            manufacturers have certainly figured out how to make safe
            and effective MLPE.


            I'm a big fan of UL3741, I have been on that UL technical
            committee for about 5 years, and it is the best approach I
            see to expand both off-grid and grid-interactive solutions
            that don't require MLPE for RS. SMA for example is very
            present and working hard at revisions on that standard
            right now. At this point I can't see us having any luck in
            removing 690.12 requirements, except perhaps to replace
            the inside the array boundary voltage limit with only
            option as 3741 listing). So please keep asking
            manufacturers (inverter/rack) to pay attention to UL3741
            and design products to meet the standard.

            Best

            Rebekah

            Licensed Electrical Contractor
            NABCEP Certified Solar PV Installation Professional™ 091209-85

            Tel: 336.266.8800

            On Mon, Feb 17, 2025 at 10:59 AM Amos Post via RE-wrenches
            <re-wrenches@lists.re-wrenches.org> wrote:

                Seems like there has been talk of rescinding RSD
                requirements before on this forum.  It also seems that
                it might gain some traction if a dedicated group of
                installers spoke up to the right people (Code Making
                Panel for instance) and put some time into it.   I
                agree that at the very least we need reliable RSD
                equipment, and my preference would be less vs more.

                Does anybody know if any sort of RSD is being required
                in Europe (not that we follow their electrical
                codes/ideas…just curious)???



                       Amos Post
                   Integrity Energy
                  W 802.763.7023
                   C 802.291.2188
                ienergyVT.com <http://www.ienergyvt.com>

                Facebook
                <https://www.facebook.com/integrityenergyllp?ref=hl>

                On Feb 17, 2025, at 12:30 PM, david quattro via
                RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

                It seems anecdotal until it happens to you.

                    My mention of civil disobedience has been answered
                clearly with a “No” in this forum, and I'm fine to
                hear that.

                   I'll clarify a few points as to why I honestly
                think RSD has been a huge and costly mistake. I
                genuinely think RSD requirements should be terminated
                immediately. If the technology were more robust and if
                it worked consistently I wouldn't protest. But *all*
                the products I've tried have been trouble.

                   William, respectfully your analogy to seat belts is
                not an appropriate comparison to Rapid Shutdown.
                Seat-belts were required in all new cars starting in
                1968 because there was statistical evidence supporting
                their tremendous efficacy in saving human life.
                Currently seat belts save about 15,000 lives per year.

                    Contrasting to RSD: was implemented because of the
                following paranoid fairytale scenario - “A firefighter
                is on a burning solar roof in the daytime, and wearing
                a metal axe at their hip. the poor guy/gal falls into
                live solar glass, and shatters it. The fall is so
                forceful that the heavy-duty fireman’s suit is
                punctured. Electricity conducts through the axe blade,
                through the suit, contacts the skin, and a DC circuit
                is completed through their body.”

                   As far as I know, this has never happened once
                anywhere on earth. Let’s be honest - this scenario has
                an incredibly low chance of ever happening in all the
                future of humanity. So considering that RSD has never
                helped anyone yet, and probably never will... How many
                fires can be attributed to RSD? How much property
                damage has occurred because of these fires?

                The best path to safety for firefighters is by
                preventing fire disasters in the first place.  Fires
                spread. Any fire that happens endangers property
                owners, tenants, business owners, neighbors, shoppers,
                bystanders, nearby forests, etc.  RSD manufacturers
                aren't doing a good job right now, so we are seeing
                low quality unreliable electronics on the roof. I will
                stick my neck out and admit that installers are not
                always perfect. Humans make mistakes - sometimes in
                initial construction, and sometimes during repair and
                maintenance (i.e. when hunting down failed RSD's which
                happens far more than it should).

                   At this time, these devices are not being designed
                to withstand reality. When problems happen,
                manufacturers are quibbling. They ignore you until you
                go away, or until you sue them.

                  This level of "safety" is not important, and in fact
                RSD is causing fires every year.

                On Sat, Feb 15, 2025 at 11:38 AM William Miller
                <will...@millersolar.com> wrote:

                    David, Ray:

                    I have not had any problems with the Tigo RSS
                    equipment I have installed and I have had minimal
                    problems with optimizers and micro-inverters
                    (which are also RSS equipment). Apparently others
                    have had failures. We don’t know statically how
                    serious this problem is—the posts here are purely
                    anecdotal.

                    We also have not heard from the other side of the
                    debate: the fire fighters.

                    Based on lack of verifiable information I can not
                    personally conclude that RSS is all problem and no
                    benefit.

                    To declare that the concept is flawed because the
                    equipment available is not reliable is like saying
                    we should not be required to install airbags
                    because a bad batch of them was manufactured. We
                    are seeing problems with the equipment needed to
                    implement a safety requirement.  That observation
                    does not logically conclude the safety requirement
                    is not valuable.

                    I hesitate to dismiss any safety requirement out
                    of hand.  Safety systems are designed to save
                    lives and protect from injury, and most of them
                    do.  I am glad to have anti-lock brakes, smoke
                    detectors and air bags.   I have also found it
                    quite handy to initiate RSS to allow me to work
                    more safely on solar circuits.

                    Does anyone on this installers forum have contacts
                    in the fire-response community that can comment on
                    the their side of the issue? If RSD is really
                    necessary for safety, then I will do my best to
                    install good equipment properly and hold
                    manufacturers accountable for shoddy solutions. If
                    RSD is not that effective we need to discuss
                    undoing the code requirements.

                    Sincerely,

                    William Miller

                    Miller Solar

                    17395 Oak Road, Atascadero, CA 93422

                    805-438-5600

                    www.millersolar.com <http://www.millersolar.com/>

                    CA Lic. 773985

                    *From:*RE-wrenches
                    [mailto:re-wrenches-boun...@lists.re-wrenches.org]
                    *On Behalf Of *david quattro via RE-wrenches
                    *Sent:* Saturday, February 15, 2025 6:05 AM
                    *To:* RE-wrenches
                    *Cc:* david quattro
                    *Subject:* Re: [RE-wrenches] Tigo inverter experience

                    RSD is the worst thing to happen to solar. Has
                    anyone considered civil disobedience?

                        I wonder what would happen if all the
                    installers banded together and refused, as a
                    united industry ‘brotherhood.’ WE are the ones
                    stuck with the bullshit in the aftermath.

                         I’m not being snarky here , this a genuine
                    question to the group:   Does anyone have _good_
                    experience with RSD?   i.e. you’re really glad RSD
                    was there, and you genuinely feel safer?  you’re
                    glad and happy to comply with this code and you
                    look forward to continuing to use RSD for the rest
                    of your career?

                    On Fri, Feb 14, 2025 at 3:40 PM Ray Walters via
                    RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

                        it seems silly that we are required to install
                        these extra pieces of equipment for added
                        "safety", that are actually a fire hazard on
                        the roof. Just to survey again: how many homes
                        have been saved by RSD? How many fire fighters
                        have actually actuated the RSD system, so that
                        they could hack through the array to vent the
                        roof?

                        I think it should only be required if you have
                        covered so much of the roof with PV, that the
                        fire dept can't access uncovered roof to do
                        their venting.  The whole premise of RSD is
                        flawed.  IMHO, its just another effort to
                        block the wider adoption of solar.

                        When it comes to off grid, RSD causes such a
                        decrease in reliability to amount to a
                        decrease in safety, due to possible loss of
                        communications, water, and heat.  Add the fire
                        hazard and RSD is really not making our
                        customers' lives better.

                        Ray Walters
                        Remote Solar

                _______________________________________________
                List sponsored by Redwood Alliance

                Pay optional member dues here: http://re-wrenches.org

                List Address: RE-wrenches@lists.re-wrenches.org

                Change listserver email address & settings:
                
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                There are two list archives for searching. When one
                doesn't work, try the other:
                https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
                
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                List rules & etiquette:
                http://www.re-wrenches.org/etiquette.htm

                Check out or update participant bios:
                http://www.members.re-wrenches.org

                _______________________________________________
                List sponsored by Redwood Alliance

                Pay optional member dues here: http://re-wrenches.org

                List Address: RE-wrenches@lists.re-wrenches.org

                Change listserver email address & settings:
                
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                There are two list archives for searching. When one
                doesn't work, try the other:
                https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
                
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                List rules & etiquette:
                http://www.re-wrenches.org/etiquette.htm

                Check out or update participant bios:
                http://www.members.re-wrenches.org

            _______________________________________________
            List sponsored by Redwood Alliance

            Pay optional member dues here: http://re-wrenches.org

            List Address: RE-wrenches@lists.re-wrenches.org

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            There are two list archives for searching. When one
            doesn't work, try the other:
            https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            http://www.re-wrenches.org/etiquette.htm

            Check out or update participant bios:
            http://www.members.re-wrenches.org


        _______________________________________________
        List sponsored by Redwood Alliance

        Pay optional member dues here:http://re-wrenches.org

        List Address:RE-wrenches@lists.re-wrenches.org

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        There are two list archives for searching. When one doesn't work, try 
the other:
        https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        http://www.re-wrenches.org/etiquette.htm

        Check out or update participant bios:
        http://www.members.re-wrenches.org

-- Christopher Warfel, PE
    ENTECH Engineering, Inc.
    PO Box 871, Block Island, RI 02807
    (401) 447-5773


--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401) 447-5773
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to