Chris,
I also found Kirk's response to capture what I would've checked first.
Ray is correct about multiple neutral-ground bonds, but there's a point
that I think has been missed. You didn't identify the generator, and I'm
going to assume that it's a portable gasoline unit. They have GFCIs on
the AC output because they're almost never connected to a solid ground,
and that's the safest they can make the output - they internally bond
neutral to the chassis of the gennie and run the output through a GFCI.
When they're connected to an off grid home there's always going to be a
ground loop in a correctly wired installation, because the Powercenter
is the first point of disconnect and is thus where the overall system
neutral-ground bond should be made.
In my experience there is no fully Code-compliant solution to this. At
least, I never came up with one, and many years ago neither could John
Wiles when I discussed it with him. You don't want to disconnect the
bond in the E-Panel because if the gennie is the only bond point and
it's disconnected (by unplugging it) your system ground becomes
unbonded. Stationary generators generally separate the bond, or at least
allow it to be separated (small Kohler units always allowed this),
because of this very issue - for prime power (non-solar) applications
the bond is made at the source, but where it's a secondary source it
needs to be separated. Portable generators don't give this option.
The best solution John and I came up with is to treat the gennie as a
separately derived system: ground it to its own rod; put it far enough
from the home that you can't touch it and anything grounded in the home
at the same time; bond normally in the E-Panel; and eliminate or
disconnect and tie off the bonding conductor between the gennie and the
PV system. Only by treating it as a separately derived system can you
get around the requirement that all service equipment must be bonded.
And if the gennie has a separable neutral-ground bond that's been
opened, I have no idea how to solve your issue... 😉
Allan
--
*Allan Sindelar*
al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>
(Former) NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
Founder (Retired), Sindelar Solar
*505 780-2738 cell*
On 12/16/2022 12:44 PM, Ray Walters via RE-wrenches wrote:
Undoing the N-G bond at the E panel may not do it either. Are you
sure neutral isn't also bonded in the main distribution panel? It
usually is bonded at the generator, so you definitely have to unbond
there. I'd say 60 to 70% of off grid systems are not bonded correctly
that I've seen. Just what Kirk said: it should only be bonded N-G at
one and only one spot. Check sub panels too. My record was seven N-G
bonds on one site. It caused the shower to be energized; the customer
thought that was normal....(don't touch the shower head!?!).....That
site even had a N-G bond in the well pump wiring! Took 3 days of
unF***ing that wiring to finally get it.
It ain't safe, until it's right. The GFCI is doing its job, and so is
the Magnum. Now the electrician has to do his job. Unless you wired
the whole house, you're On to fix it. Especially off grid, I see an
amazing bunch of DIY garbage. Find out who did the original wiring.
Probably not a pro.
Ray Walters
Remote Solar
On 12/16/2022 11:35 AM, Kirk Herander via RE-wrenches wrote:
You may have neutral and ground connected at more than 1 location,
meaning at the genset and in house panel, which means the ground is
carrying current back to the generator in parallel with the neutral.
I remember with some Honda portables we had to float the neutral at
the genset or the inverter would trip the generator's GFI when trying
to charge the batteries.
On Fri, Dec 16, 2022 at 1:16 PM Dave Angelini Offgrid Solar via
RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:
The easy answer is try another genset ! You have to be more
specific, did it ever work? Is it new? etc. Good Luck !
*Dave Angelini Offgrid Solar "we go where powerlines don't"
http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net
text 209 813 0060*
On 2022-12-16 10:04 am, Chris Daum via RE-wrenches wrote:
Hi folks:
We have a new Magnum MS4024 mounted on an E-Panel using a
MidNite Classic 150 and Whiz-Bang JR with power coming from an
array of Trina TSM365-De06X-05(II) (three strings of three) with
the ME-RC50 and a HUP SolarOne 6-85-14/24 battery.
When we attempt to use the PFC (Power Factored Charger), the Gen
Set’s GFCI outlets trip. Thus far we have verified the
connections are secure, assured that the gen set is grounded,
disconnected the jumper within the E-Panel between the ground
buss and neutral, checked AC voltages, removed the MNSPD’s from
the buss(s)… Stumped now on what an appropriate next step
should be. How do we get the PFC to function properly? What
are we missing?
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't
work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
--
*Kirk Herander / **kirkh@vermont.solar*
*Owner|Principal, VT Solar, LLC*
*/Celebrating our 31^st Anniversary 1991-2022!!/*
*www.vermont.solar*
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
dba Vermont Solar Engineering
802.863.1202
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org