looks like one more failure, once they start there is no going back as the
fuse retainer loses its spring

On Tue, Nov 2, 2021 at 1:38 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:

> Ugh - no joke - we just found another one this morning with a blown fuse.
> Pic attached. It's really a nightmare.
>
> Check out how discolored the top of the left fuse is (again). Always the
> same fault...
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
>
>
> On Mon, Nov 1, 2021 at 8:43 PM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> See attached image. Notice the discoloration on the top of the left fuse.
>> It's always the same thing, same place.
>>
>> Jason
>>
>> On Mon, Nov 1, 2021, 8:30 PM Jason Szumlanski <
>> ja...@floridasolardesigngroup.com> wrote:
>>
>>> I should also mention that it has nothing to do with ambient heat. This
>>> has occured in all seasons and with disconnects in direct sunlight on a
>>> south wall and disconnects in air conditioned garages.
>>>
>>> It's just a garbage product. We switched to Square D for 60A D222NRB
>>> fusible disconnects and are also using their 100A circuit breaker
>>> enclosures which are cost effective. The D223NRB is also a good fusible
>>> disconnect, but pricey.
>>>
>>> Jason
>>>
>>>
>>> On Mon, Nov 1, 2021, 8:24 PM Jason Szumlanski <
>>> ja...@floridasolardesigngroup.com> wrote:
>>>
>>>> It's the disconnect. We had dozens of this subpar disconnect design
>>>> fail on Enphase systems. The 2 Pole has the same issue.
>>>>
>>>> GE gave us some nonsense answer that it's General Duty and not designed
>>>> for continuous high power. Even 40A combined Enphase systems will blow a
>>>> 60A fuse.
>>>>
>>>> What you will find is the fuse will blow on one side and then
>>>> replacements will blow at decreasing intervals until it blows daily. Our
>>>> experience is the left side (of the 2-pole)  is far more problematic for
>>>> some odd reason. It's not the fuse brand either.
>>>>
>>>> I believe the design fault is how the blades only hit a single contact
>>>> on one side when they close. The Square D alternative has the blade
>>>> slipping between two contacts.
>>>>
>>>> Sadly we have had to replace so many of these and most are supply side
>>>> interconnections, which make it tricky and expensive.
>>>>
>>>> Jason Szumlanski
>>>> Florida Solar Design Group
>>>>
>>>>
>>>>
>>>>
>>>> On Mon, Nov 1, 2021, 4:26 PM Dave Tedeyan <d...@sungineersolar.com>
>>>> wrote:
>>>>
>>>>> Hi All,
>>>>>
>>>>> I am servicing a system that keeps blowing fuses on the AC side,
>>>>> although it
>>>>>  appears that everything is sized correctly. It is a SolarEdge
>>>>> SE11400A-US inverter.
>>>>>  Max continuous output current is 47.5A x 1.25 = 59.4A. There is a GE
>>>>> TG3222R
>>>>>  60A AC disconnect, and it is wired up with #6 THHN wire. The
>>>>> terminals were tight
>>>>>  and there was no evidence of arcing or burning in the past. This is
>>>>> indoors, and not
>>>>>  exposed to sunlight. No extra conductors are in the conduit.
>>>>>
>>>>> But they say that they need to replace a fuse roughly once per month.
>>>>> Has anyone
>>>>>  seen this before? Could there be some kind of fault in the inverter
>>>>> itself that
>>>>>  occasionally induces extra current? Is there any way to tweak the
>>>>> settings so that it
>>>>>  actually produces a bit more than 11.4kw? I appreciate your thoughts.
>>>>>
>>>>> Cheers,
>>>>> Dave
>>>>>
>>>>> --
>>>>> [image: Logo] <https://www.sungineersolar.com/>
>>>>> Dave Tedeyan, P.E.
>>>>> Owner | Sungineer Solar
>>>>> p: he | him | his
>>>>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>>>>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>>>>> c: (607) 288-2898
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to