Trust me when I tell you that all of the line side conductors and taps are
likely fine. It is unequivocally the switch contacts that are the issue.
That said, I usually replace the conductors when there is any indication of
overheating near the terminals. I have seen discolored copper, but it never
gets bad enough to melt insulation.

Jason


On Tue, Nov 2, 2021, 12:28 PM Dave Tedeyan <d...@sungineersolar.com> wrote:

> It is always the left fuse! Thanks all for the pointers. I'll double check
> the monitoring, but am thinking that I will be replacing the switch with a
> SQD, and replacing the taps and AC wires as well while I'm at it.
> Cheers,
> Dave
>
> On Mon, Nov 1, 2021, 9:13 PM Jerry Shafer <jerrysgarag...@gmail.com>
> wrote:
>
>> Bad switch
>>
>>
>> On Mon, Nov 1, 2021 at 5:44 PM Jason Szumlanski <
>> ja...@floridasolardesigngroup.com> wrote:
>>
>>> See attached image. Notice the discoloration on the top of the left
>>> fuse. It's always the same thing, same place.
>>>
>>> Jason
>>>
>>> On Mon, Nov 1, 2021, 8:30 PM Jason Szumlanski <
>>> ja...@floridasolardesigngroup.com> wrote:
>>>
>>>> I should also mention that it has nothing to do with ambient heat. This
>>>> has occured in all seasons and with disconnects in direct sunlight on a
>>>> south wall and disconnects in air conditioned garages.
>>>>
>>>> It's just a garbage product. We switched to Square D for 60A D222NRB
>>>> fusible disconnects and are also using their 100A circuit breaker
>>>> enclosures which are cost effective. The D223NRB is also a good fusible
>>>> disconnect, but pricey.
>>>>
>>>> Jason
>>>>
>>>>
>>>> On Mon, Nov 1, 2021, 8:24 PM Jason Szumlanski <
>>>> ja...@floridasolardesigngroup.com> wrote:
>>>>
>>>>> It's the disconnect. We had dozens of this subpar disconnect design
>>>>> fail on Enphase systems. The 2 Pole has the same issue.
>>>>>
>>>>> GE gave us some nonsense answer that it's General Duty and not
>>>>> designed for continuous high power. Even 40A combined Enphase systems will
>>>>> blow a 60A fuse.
>>>>>
>>>>> What you will find is the fuse will blow on one side and then
>>>>> replacements will blow at decreasing intervals until it blows daily. Our
>>>>> experience is the left side (of the 2-pole)  is far more problematic for
>>>>> some odd reason. It's not the fuse brand either.
>>>>>
>>>>> I believe the design fault is how the blades only hit a single contact
>>>>> on one side when they close. The Square D alternative has the blade
>>>>> slipping between two contacts.
>>>>>
>>>>> Sadly we have had to replace so many of these and most are supply side
>>>>> interconnections, which make it tricky and expensive.
>>>>>
>>>>> Jason Szumlanski
>>>>> Florida Solar Design Group
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> On Mon, Nov 1, 2021, 4:26 PM Dave Tedeyan <d...@sungineersolar.com>
>>>>> wrote:
>>>>>
>>>>>> Hi All,
>>>>>>
>>>>>> I am servicing a system that keeps blowing fuses on the AC side,
>>>>>> although it
>>>>>>  appears that everything is sized correctly. It is a SolarEdge
>>>>>> SE11400A-US inverter.
>>>>>>  Max continuous output current is 47.5A x 1.25 = 59.4A. There is a GE
>>>>>> TG3222R
>>>>>>  60A AC disconnect, and it is wired up with #6 THHN wire. The
>>>>>> terminals were tight
>>>>>>  and there was no evidence of arcing or burning in the past. This is
>>>>>> indoors, and not
>>>>>>  exposed to sunlight. No extra conductors are in the conduit.
>>>>>>
>>>>>> But they say that they need to replace a fuse roughly once per month.
>>>>>> Has anyone
>>>>>>  seen this before? Could there be some kind of fault in the inverter
>>>>>> itself that
>>>>>>  occasionally induces extra current? Is there any way to tweak the
>>>>>> settings so that it
>>>>>>  actually produces a bit more than 11.4kw? I appreciate your thoughts.
>>>>>>
>>>>>> Cheers,
>>>>>> Dave
>>>>>>
>>>>>> --
>>>>>> [image: Logo] <https://www.sungineersolar.com/>
>>>>>> Dave Tedeyan, P.E.
>>>>>> Owner | Sungineer Solar
>>>>>> p: he | him | his
>>>>>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>>>>>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>>>>>> c: (607) 288-2898
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>>
>>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> There are two list archives for searching. When one doesn't work, try
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>>
>>>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to