The code clearly allows a 400A supply (200 main plus 200 solar supply) to a
200A bus if there are no loads on that bus. Or a 300A total supply to a
200A bus with 100A of loads. That's 705.12(D)(2)(3)(c) verbatim.

Better get an insulated wrench.





On Mon, Nov 9, 2020 at 12:53 PM William Miller <will...@millersolar.com>
wrote:

> . Where would 300A of current ever flow?
>
>
>
> What is someone dropped a wrench on the bus?  It would fault with greater
> than 200 amps.  This is and has been the point behind this code section.
>
>
>
> William
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
> <https://mailtrack.io/trace/link/45f3322dcff8c8848aab527a83b7e9721f4281ff?url=http%3A%2F%2Fwww.millersolar.com%2F&userId=1613865&signature=5109dabe048e7da1>
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Jason Szumlanski
> *Sent:* Sunday, November 8, 2020 9:47 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] NEC 2020 - 705.12(B)(6)
>
>
>
> It's a 200A bus.
>
>
>
> 300A "on" the bus doesn't matter. The total of all load and supply devices
> does not exceed the bus rating. This is 705.12(D)(2)(3)(c) in 2014/2017.
>
>
>
> In no way can the total ampacity on the 200A bus exceed 200A as long as
> additional loads are not added, hence the required warning label
>
>
>
> On Sun, Nov 8, 2020, 12:30 PM Jay <jay.pe...@gmail.com> wrote:
>
> Hi Jason
>
>
>
> My question is if it’s 200a in from the main breaker and 100a from PV its
> 300 amps on the buss correct?
>
>
>
> How is that ok with the 125% rule?
>
>
>
> Or is this covered by some other rule as it’s a feed through lug load
> center?
>
>
>
> Jay
>
>
>
>
>
>
>
> On Nov 8, 2020, at 9:46 AM, Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
> 
>
> Maybe this is a better example (attached). I don't see how this would be a
> problem under NEC 2014, 2017, or 2020. No portion of the main bus, feeder
> conductors, or subpanel could possibly be subjected to overcurrent without
> an OCPD stopping it.
>
>
>
> My point is that here we are, 3 code cycles in since feeder taps were
> addressed, and there is still no clarification of intent. AHJs are still
> struggling with this.
>
>
>
> I'm not sure where residential meter/mains with feed through lugs are
> popular. I know they are in Florida and I have heard Hawaii. I'm curious
> what your jurisdictions think of this if you have this scenario. Most of
> the time the subpanel is main lug only, but adding a main circuit breaker
> is usually an easy and cost-effective fix to make this interconnection type
> work.
>
>
>
> Jason Szumlanski
>
>
>
>
>
>
>
>
>
>
>
> On Wed, Oct 28, 2020 at 5:15 PM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
> For further discussion, I don't see how my original scenario is any
> different from this attached scenario, which I think everyone would agree
> is allowed. All conductors and busbars are subject to the same potential
> loads and fault currents.
>
>  (Image attached).
>
>
>
>
>
>
>
> On Wed, Oct 28, 2020 at 5:01 PM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
> Of course the feeder conductors and bus bar could be subjected to a fault.
> But we're not talking about faults here. Fault protection is the job of the
> PV OCPD And primary supply OCPD to protect the downstream busbar and
> feeders. If that wasn't the case, you would need a new OCPD on BOTH the
> load and line side of a solar connection as a feeder tap, not just the load
> side.
>
>
>
> If your interpretation is correct regarding the location of the OCPD, that
> sounds like a sub-feed breaker is the only way to comply, and I haven't
> seen such an animal for a typical residential load center. You can get
> these for NQ panelboards and similar panelboards from other manufacturers
> of course. It doesn't say as close as practicable or anything like that. It
> says that a busbar connection is allowed when there are feeder CONDUCTORS
> connected to feed through LUGS. What does "overcurrent device .. *at* the
> supply end" mean? I emphasize "at." It's unclear how you would implement
> this other than a sub-feed breaker I suppose, but that's not what it says.
> It refers to feeder conductors on lugs on busbars, not feeder conductors on
> load-side terminals of an overcurrent device.
>
>
>
> My point is that 705.12 should have been wrapped up neatly in a bow, but
> the lack of clarity, still, is astonishing. Why add a section about
> feed-through lugs if it's going to be so vague?
>
>
>
> Jason
>
>
>
>
>
>
>
>
>
> On Wed, Oct 28, 2020 at 3:37 PM Brian Mehalic <br...@solarenergy.org>
> wrote:
>
> Hey Jason,
>
> Here's the 2020 text:
>
>
>
> 6) Connections shall be permitted on busbars of panelboards that supply
> lugs connected to feed-through conductors. The feed-through conductors
> shall be sized in accordance with 705.12(B)(1). Where an overcurrent device
> is installed at the supply end of the feed-through conductors, the busbar
> in the supplying panelboard shall be permitted to be sized in accordance
> with 705.12(B)⁠(3)⁠(1) through 705.12(B)(3)(3).
>
>
>
> The OCPD on the supply end of the feed-through conductors would be in the
> form of a sub-feed breaker at the point of supply to those conductors,
> re-establishing overcurrent protection of the conductors (likely at the
> same ampacity as the main breaker in the supplying panel.  The feed-through
> conductors are basically an extension of the busbar in the supplying panel;
> they can either be protected by the main, or in the presence of multiple
> sources of power in the supplying panel (such as a backfed PV system
> breaker) they can be protected based on (B)(3)(1) - "the 125% rule" - or
> they can be protected by a new overcurrent device at their point of supply,
> in which case current on them is limited based on that OCPD size; in this
> latter scenario the busbar in the supplying panel is allowed to be sized
> based on one of (B)(3)(1) - (3) because it is protected downstream at its
> end.
>
>
>
> The theory is pretty much the same as 705.12(B)(1) for feeders - when not
> connecting at the end of the feeder, use the "125% rule" or re-establish
> overcurrent protection for that portion of the feeder subject to multiple
> power sources.
>
>
>
> In your drawing the 200 A feeder conductors, as well as the busbar below
> the PV system breaker, could be subject to > 200 A in the event of a fault
> somewhere along those conductors.
>
>
>
> Brian Mehalic
> NABCEP Certified Solar PV Installation Professional™ R031508-59
>
> National Electrical Code® CMP-4 Member
>
> (520) 204-6639
>
>
>
> Solar Energy International
> http://www.solarenergy.org
> <https://mailtrack.io/trace/link/2603da024a6946c42b34ebf7b2750490f5e01be5?url=http%3A%2F%2Fwww.solarenergy.org&userId=1613865&signature=32a5d3726246f3bd>
>
>
>
> SEI Professional Services
>
> http://www.seisolarpros.com
> <https://mailtrack.io/trace/link/2b1457686471c2ca8a6962c8f5b7342d186c2f85?url=http%3A%2F%2Fwww.seisolarpros.com&userId=1613865&signature=678c2944003a1fb2>
>
>
>
>
>
>
>
> On Wed, Oct 28, 2020 at 10:18 AM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
> Does anyone else think they botched the wording in this section? It's
> still not clear, and we have a ton of meter/main combos with feed-through
> lugs around here.
>
>
>
> Where is it written, "where an overcurrent device is installed at the *supply
> end* of the feed-through conductors," (emphasis added) are they referring
> to the solar backfed breaker on the busbar or another breaker somewhere
> along the feeder circuit? It goes on to state that the loads on the
> supplying busbar can comply with any method in 705.12(B)(3), which
> prescribes an OCPD at the load end of the feeder in 705.12(B)(3)(3), so
> they can't be talking about that. I have to assume it is the solar
> backfed breaker they are referencing.
>
>
>
> See my interpretation of one scenario in the attached image.
>
>
>
> We're a long way off from the 2020 code implementation here, but it can
> help sway plans examiners looking to clarify the intent of the 2014/2017
> code cycles.
>
>
>
>
>
> Jason Szumlanski
>
> *Error! Filename not specified.*
>
> *Error! Filename not specified.*
>
> <Feed Through Lug Interconnection Option (2).pdf>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/67572afcc0f0188575a0af83ef6e0d4830e72877?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=2e6ba8f4b154f88c>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://mailtrack.io/trace/link/25f0591f9a7c9dddbc594d9267bcb3757b6c2173?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=1a783df33f906269>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/a520b5d94d10eca38b0273596db5f595ffdb8d47?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=aea0ff9123d21f43>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/b60a4cc407ec329fcb4f1a4d4c78918a31002913?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8c5ad6d0ee66d1db>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/c16e216fad02514d89220d38a3e5a0d3ae1c0ac1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=d16af447fc4a696d>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/a59cb5c9cb9c9c3efa311107642b3d8587d29159?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=3f2ece62b71f79ff>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://mailtrack.io/trace/link/bb5ad83e7c1dab444824c8d7d377a4092af8a891?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=0f7ac5a2f7cf0e35>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/861ee0631896d9e0a63886c5b181b1be36ef337e?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=93a53dc567bd6968>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/559dca5df44d4753460d286ea92bb45540c173fb?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=462dd186cee1ab44>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/89858bd3b813ad1fd5bb0d96b1e89ab93ff64629?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=56cc6e4b8f2871b7>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/0e974be2b856f2617825d221c66bd477382f870d?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=2b9a6fb5d97000cc>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://mailtrack.io/trace/link/46eb1c5c5b63866dda013ecaa2cf41b2e298f993?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=64b2065044ff0e83>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/abbc9cb88d3ec0535be6edadb1898eb140b25e1f?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=bae7ebdb79da13ec>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/96aee5a364ea7ca39fbba5c477b5c9930f089348?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=22a33d760a8d38b4>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/4ddef3786513e37001929084f71457d2a5c14e63?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=acecd2f8c7426e64>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to