Of course the feeder conductors and bus bar could be subjected to a fault.
But we're not talking about faults here. Fault protection is the job of the
PV OCPD And primary supply OCPD to protect the downstream busbar and
feeders. If that wasn't the case, you would need a new OCPD on BOTH the
load and line side of a solar connection as a feeder tap, not just the load
side.

If your interpretation is correct regarding the location of the OCPD, that
sounds like a sub-feed breaker is the only way to comply, and I haven't
seen such an animal for a typical residential load center. You can get
these for NQ panelboards and similar panelboards from other manufacturers
of course. It doesn't say as close as practicable or anything like that. It
says that a busbar connection is allowed when there are feeder CONDUCTORS
connected to feed through LUGS. What does "overcurrent device .. *at* the
supply end" mean? I emphasize "at." It's unclear how you would implement
this other than a sub-feed breaker I suppose, but that's not what it says.
It refers to feeder conductors on lugs on busbars, not feeder conductors on
load-side terminals of an overcurrent device.

My point is that 705.12 should have been wrapped up neatly in a bow, but
the lack of clarity, still, is astonishing. Why add a section about
feed-through lugs if it's going to be so vague?

Jason




On Wed, Oct 28, 2020 at 3:37 PM Brian Mehalic <br...@solarenergy.org> wrote:

> Hey Jason,
> Here's the 2020 text:
>
> 6) Connections shall be permitted on busbars of panelboards that supply
> lugs connected to feed-through conductors. The feed-through conductors
> shall be sized in accordance with 705.12(B)(1). Where an overcurrent device
> is installed at the supply end of the feed-through conductors, the busbar
> in the supplying panelboard shall be permitted to be sized in accordance
> with 705.12(B)⁠(3)⁠(1) through 705.12(B)(3)(3).
>
>
> The OCPD on the supply end of the feed-through conductors would be in the
> form of a sub-feed breaker at the point of supply to those conductors,
> re-establishing overcurrent protection of the conductors (likely at the
> same ampacity as the main breaker in the supplying panel.  The feed-through
> conductors are basically an extension of the busbar in the supplying panel;
> they can either be protected by the main, or in the presence of multiple
> sources of power in the supplying panel (such as a backfed PV system
> breaker) they can be protected based on (B)(3)(1) - "the 125% rule" - or
> they can be protected by a new overcurrent device at their point of supply,
> in which case current on them is limited based on that OCPD size; in this
> latter scenario the busbar in the supplying panel is allowed to be sized
> based on one of (B)(3)(1) - (3) because it is protected downstream at its
> end.
>
> The theory is pretty much the same as 705.12(B)(1) for feeders - when not
> connecting at the end of the feeder, use the "125% rule" or re-establish
> overcurrent protection for that portion of the feeder subject to multiple
> power sources.
>
> In your drawing the 200 A feeder conductors, as well as the busbar below
> the PV system breaker, could be subject to > 200 A in the event of a fault
> somewhere along those conductors.
>
> Brian Mehalic
> NABCEP Certified Solar PV Installation Professional™ R031508-59
> National Electrical Code® CMP-4 Member
> (520) 204-6639
>
> Solar Energy International
> http://www.solarenergy.org
> <https://mailtrack.io/trace/link/86b5841c6230a1049a6fd06f2085b233a0593f23?url=http%3A%2F%2Fwww.solarenergy.org&userId=1613865&signature=9fd3dbba7d87587d>
>
> SEI Professional Services
> http://www.seisolarpros.com
> <https://mailtrack.io/trace/link/9d97577f8c6b7e825f5e4c332a4cd891a9425e17?url=http%3A%2F%2Fwww.seisolarpros.com&userId=1613865&signature=8e111ea91bebc146>
>
>
>
> On Wed, Oct 28, 2020 at 10:18 AM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> Does anyone else think they botched the wording in this section? It's
>> still not clear, and we have a ton of meter/main combos with feed-through
>> lugs around here.
>>
>> Where is it written, "where an overcurrent device is installed at the *supply
>> end* of the feed-through conductors," (emphasis added) are they
>> referring to the solar backfed breaker on the busbar or another breaker
>> somewhere along the feeder circuit? It goes on to state that the loads on
>> the supplying busbar can comply with any method in 705.12(B)(3), which
>> prescribes an OCPD at the load end of the feeder in 705.12(B)(3)(3), so
>> they can't be talking about that. I have to assume it is the solar
>> backfed breaker they are referencing.
>>
>> See my interpretation of one scenario in the attached image.
>>
>> We're a long way off from the 2020 code implementation here, but it can
>> help sway plans examiners looking to clarify the intent of the 2014/2017
>> code cycles.
>>
>>
>> Jason Szumlanski
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/130753fb849e9f11381008286c4c87ffd4a5a809?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=2185ebc1ce345ffd>
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> <https://mailtrack.io/trace/link/cef820e47f23c1fec1fbfa39bed8b05453e3092c?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=187099448a58b12f>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/8a2cdf70dcbd34b7b1effe8ef51658114b46c002?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b7a6192c15071196>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/ecfb5f1216394c98fac152786437dc2d55be0587?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=cd10b9983f4e212c>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/dcde46d76272a1ff3f38913e4ee8e43aa814b1a8?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=fdbbc0f5ab824504>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/7c86a345189eda48cec29704ff256df0abbf7be7?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=d6afc2ea347b596c>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://mailtrack.io/trace/link/a1491a579a497bdc2bf338612558df520df33ae0?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=b8ea72f2c6c09920>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/7ad81a79c7abfcc43dc797543542ec4ec3ebc17c?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=7da802e6403daf72>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/066150ddcdc47a1593ee604afc11c40a9d480c81?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=cd44e50b27ad2d75>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/98e4cf8a66034f938d3b9fe4b03732a04cb9b9b1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4e73ef34cdd4ad1b>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to