August,

One quick note about your last sentence. I know you are talking about
swapping black and red on an Enphase branch circuit, which is not a
problem. However, landing L1 from string 1 with L2 from string 2 on a
2-pole breaker and vice-versa does matter. For correct OCPD operation, you
need to land the pairs on the right breakers. I have seen this mistake
before. Circuits that were expected to be de-energized still had one hot
leg. Not good...


On Fri, Jul 24, 2020 at 12:20 PM August Goers <aug...@luminalt.com> wrote:

> We've installed lots of Enphase, SolarEdge, and the various string
> inverters over the years. As far as Enphase goes, our experience is not too
> far from what Jason described - we had thousands of the M190/M210
> generation installed and experienced a very high failure rate. Our failure
> rate on those older systems seems to have stabilized. I think we're doing
> maybe one Enphase micro replacement site call per month or so, which is
> quite manageable. I do expect to continue to have a trickle of failures,
> but they are now not too far out of line compared to our string inverter
> failure rates (SMA/Fronious/ABB/Xantrex/Etc).
>
> We've been installing SolarEdge on our small and medium commercial system
> for the past few years with success. I don't think we've had a single
> failure, but we don't do a ton on commercial, we have 20 sites in our
> SolarEdge portfolio.
>
> I think it's good to focus on features, price, reliability, service,
> bankability, etc and continually reevaluate the companies and products on
> the market. We have certainly stopped installing Enphase back in 2013 when
> were seeing peak failures which was a good decision. But the newer
> equipment has been solid. SMA, which had classically been our go-to string
> inverter choice, just hasn't kept up with the market and their choices are
> too complicated compared to the SunPower AC modules (with Enphase micros
> built in) we're now installing. I'm sort of over DC systems for residential
> projects, especially if thinking about the KISS model of trying to keep
> everything as simple as possible. The wiring on an AC system is just
> getting basically as simple as it gets - just two hots to wire up and it
> doesn't even matter if you mix up the phasing.
>
> Good luck out there everyone!
>
> August
> Luminalt
>
>
> On Fri, Jul 24, 2020 at 8:37 AM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> Enphase's early failure rate was ridiculous, but we are finding that once
>> the faulty M190's were swapped after the first few years, the ones that
>> didn't fail have been relatively solid. In other words, let's say
>> (unscientifically) 30% of the M190's on a job installed 10 years ago failed
>> in the first 3 years. After that, we had a VERY low failure rate on that
>> system. I can't remember the last time I replaced an M190, and we have a
>> lot of them floating around out there. In each successive generation (M215,
>> M250, IQ6, IQ7) we have seen progressively lower failure rates in the first
>> 1, 2, and 3 years, which points to a dramatic increase in initial
>> reliability. If history is a guide, the IQ series looks like 10 years from
>> now we will be calling it a huge success. Of course, only time will tell.
>>
>> Micro replacements are a nuisance, for sure, but we haven't 'lost' much
>> money on replacements. I have lost lots of money struggling through string
>> inverter replacements due to unknown complications (physical, electrical,
>> monitoring, etc). A micro swap is a known entity and minimal complexity. I
>> can send a minimally trained (lower cost) individual to handle it and deal
>> with the administrative (monitoring) part in the office.
>>
>> The bottom line is that I am doing far FEWER micro replacements today
>> than I did 6-7 years ago when I was maintaining less than 1/3 of the units
>> I have now under supervision. My impression is that if micro is going to
>> fail, it's going to fail early on. Let's hope I'm right.
>>
>> One last point... despite a couple of bumps in the road with service hold
>> times and warranty replacement waits, Enphase's customer service has been
>> second to none over the course of the last decade. Their front-line staff
>> are well trained and knowledgeable, and access to second-tier support has
>> been phenomenal. SE gives you the same runaround as Fronius (don't get me
>> started on IGs) and other string inverter manufacturers when an HD Wave
>> goes down (have to be on site, provide a bunch of mostly irrelevant voltage
>> readings, check fuses, looks for signs of burned components, and so on to
>> get warranty satisfaction).
>>
>> Jason
>>
>>
>> On Thu, Jul 23, 2020 at 7:21 PM Kirk Herander <vtso...@icloud.com> wrote:
>>
>>> I gave up on Enphase a long time ago for the same reasons many of you
>>> are dumping on SE now. High replacement rate etc. Any of you in this biz
>>> longer than ten years knows how horrible the first several generations of
>>> Enphase was. So should I trust Enphase over SE now? Will you trust SE years
>>> from now if this board finds them acceptable again(over Enphase)? Just
>>> sayin'
>>>
>>> On 7/23/2020 6:30:29 PM, Jason Szumlanski <
>>> ja...@floridasolardesigngroup.com> wrote:
>>> Not to sounds like a Fanboy, but Enphase in a small commercial setting
>>> is a real option. Owners love the monitoring aspect, the serviceability,
>>> the warranty, etc. There is a good safety argument to be made. Replacing
>>> micros on a flat roof is usually a cakewalk if necessary. Dealing with
>>> roof-mounted equipment shading issues makes micros a good option if
>>> optimizers are off the table.
>>>
>>> I'm adding an 80kW Enphase IQ array to an existing M-series 70kW system
>>> very soon. Here's Phase 1: https://www.youtube.com/watch?v=EvXyGiUlALw
>>> <https://mailtrack.io/trace/link/e621215add968f0948515658225581e82c26a3dc?url=https%3A%2F%2Fwww.youtube.com%2Fwatch%3Fv%3DEvXyGiUlALw&userId=1613865&signature=f16f16a5c6e710f0>
>>>
>>> This one is 208Y/120. For 480V you're looking at a transformer, which
>>> changes the calculus.
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>>
>>>
>>>
>>> On Thu, Jul 23, 2020 at 5:06 PM AE Solar <autonomousenerg...@gmail.com>
>>> wrote:
>>>
>>>> interested to know if folks are having issues with specific models or
>>>> it's all across the board? if it's all across the board, i (like jay) would
>>>> be interested to know what people are moving on towards. especially for
>>>> smaller commercial 3phase projects.
>>>> adam
>>>>
>>>>
>>>> On Thu, Jul 23, 2020 at 11:57 AM MiJo Nels <spaceshipnels...@gmail.com>
>>>> wrote:
>>>>
>>>>> We also, have found this to be the case. Now I feel like I'm in a bad
>>>>> marriage with them. We consistantly wait longer than we are told for
>>>>> replacement product, constantly hearing the same repetitious verbiage from
>>>>> them "just wait a little longer, we'll be able to control your coffee 
>>>>> maker
>>>>> with your inverter soon".. or the old "Q1 Q2 Q3" promises for equipment or
>>>>> to get thru beta testing.. .. I too. . .  am "Done". . .
>>>>>
>>>>> Joe Nelson
>>>>>
>>>>> Project Manager C-46/C-10
>>>>> Sustainable Energy Group Inc., A California Corporation
>>>>>
>>>>> CSL# 868816
>>>>> www.SustainableEnergyGroup.com
>>>>> <https://mailtrack.io/trace/link/6b7b0262fe824d4a60142b89f3ef035f2777a24e?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=0719ace1f988001d>
>>>>> 530-273-4422 (Office)
>>>>>
>>>>> 530-217-8385 (Cell)
>>>>>
>>>>> 
>>>>>
>>>>>    
>>>>>
>>>>>
>>>>> ------------------------------
>>>>> *From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on
>>>>> behalf of Jay <jay.pe...@gmail.com>
>>>>> *Sent:* Thursday, July 23, 2020 7:47:31 AM
>>>>> *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
>>>>> *Subject:* Re: [RE-wrenches] Solar Edge...continuous saga of 181/183
>>>>> hardware failures...moving on to another inverter.
>>>>>
>>>>> Hi Scot and others
>>>>>
>>>>> I’ve heard these horror stories about SE
>>>>>
>>>>> What is the best replacement for SE at this point?
>>>>>
>>>>> Thanks
>>>>>
>>>>> Jay
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> On Jul 23, 2020, at 5:57 AM, scot.a...@solarcentex.com wrote:
>>>>>
>>>>> 
>>>>>
>>>>> Time has finally come to move on from SolarEdge.
>>>>>
>>>>>
>>>>>
>>>>> Now replacing the THIRD inverter for one customer alone that has the
>>>>> infamous 181/183 hardware failure error code again.  First one replaced in
>>>>> Sept 2019. Second failure and RMA July 6th 2020, and now this third
>>>>> failure on that replacement inverter.
>>>>>
>>>>>
>>>>>
>>>>> We have had 24 total RMAs at quick count and it is eating into our
>>>>> credibility.
>>>>>
>>>>>
>>>>>
>>>>> Solar Edge provided a briefing to me about two months ago
>>>>> acknowledging that their manufacturing quality control issues bordered on 
>>>>> a
>>>>> recall, but opted to stay silent and let the installers keep suffering for
>>>>> their materiel and design issues. I was advised that the batch of 
>>>>> deficient
>>>>> inverters and their manufacture time frame meant I just needed to get
>>>>> through this summer…perhaps but not another summer ever like this.
>>>>>
>>>>>
>>>>>
>>>>> No more. Au revoir, Solar Edge.
>>>>>
>>>>>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to