Hi William,

Thank you for your response. I was responding to the question of use off grid 
and Hiltons question about generator use. Jason said, "But Tesla is clear in 
that they do not allow a generator to interact with the Powerwall in any way.” 
This is true.

Powerwall uses AC coupled inverters for off grid charging. If AC from the 
micro-inverters was switched off and the generator provided the 240 Volt to the 
Powerwal inverter inputl, would that not be a temporary solution to the 
generator prohibition? The power wall would see incoming power and sync. Of 
course, the system must be monitored. If the power wall calls for cutback or 
disconnect by raising frequency, the generator should be disconnected, if it 
indeed works like that. If Powerwall provides an internal disconnect, then it 
would be safer for the user. Just trying to think outside the box.

Larry Crutcher
Starlight Solar Power Systems






On Jul 20, 2020, at 12:01 PM, William Miller <will...@millersolar.com> wrote:

Larry:
 
I am not Tesla conversant but allow me to speculate:  If any grid-tied system 
can be fed from a generator it could also feed back to the generator, which may 
damage said generator.  The grid-tied system should therefore be connected 
upstream of any transfer switching, making it ineligible to be charged from the 
generator.
 
William
 
 
 
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of la...@starlightsolar.com
Sent: Monday, July 20, 2020 10:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Tesla Powerwall 2.0 - Experience?
 
Since the Powerwall is AC coupled, how will it know if the power source is a PV 
solar array or a generator if either feed the PV input? It seems simple AC 
switching is all that would be needed. I like to think outside the box but I’m 
not familiar with Powerwall.

Larry Crutcher
Starlight Solar Power Systems

 
 
On Jul 20, 2020, at 9:53 AM, Jason Szumlanski 
<ja...@floridasolardesigngroup.com> wrote:
 
The Powerwall 2 is now supported by Tesla in an off-grid configuration from 
what I heard. It is AC coupled. It cannot interact with generators whatsoever. 
You can't charge the battery with a generator and you can't AC couple a 
generator to it. If you want a generator, you put a transfer switch on the load 
side of the gateway device. If the battery dies, the generator starts. The 
generator powers loads, but does not recharge the battery because it becomes 
isolated via the transfer switch. The big downside I see with that is there 
would be a loss of power to the loads until the generator fires up. I don't see 
a way around that.
 
I'm not a Tesla certified installer, but I have seen some of these batteries 
out in the wild and that's just the way it is - it's an integrated unit. I'd 
call it an "AC Battery," kind of like an AC PV Module. To answer another point 
in this thread, if the battery reaches its LBCO it can only recharge with PV in 
an off-grid scenario. It reserves battery capacity to turn on occasionally to 
see if there is PV input. At least that's how I understand it to work. I don't 
know what would happen if the battery actually reached 0%. Seems risky. I'm not 
sure how you would "jump start" it. Publicly available details seem scant on 
this, but there are a few system owners talking about it if you dig deep on the 
Interwebs.
 
It will be interesting to see what Enphase comes up with. There are generator 
inputs on their Ensemble system, but no software support for this yet. The 
concept is very similar to Tesla in that there is a gateway device, essentially 
a transfer switch with battery controls inside. The Gateway acts as the AC 
point of coupling for everything to tie in together. 
 
I'm not sure why you couldn't use a generator to charge the Powerwall battery 
the same way you would charge with the grid. However, you would need a way to 
disable PV AC coupling when the generator is running. I can see how Enphase 
would be able to do this pretty easily. But Tesla is clear in that they do not 
allow a generator to interact with the Powerwall in any way.
 
Jason Szumlanski
 
 
On Sun, Jul 19, 2020 at 11:43 AM Hilton Dier III <hiltond...@gmail.com> wrote:
> Greetings, Wrenches,
> I have an off-grid client who has been reading the buzz about the Tesla 
> Powerwall 2.0. I have been reading the data sheets and manual for it and it 
> appears to be AC coupled only. There was talk of a DC input version, but 
> apparently that fell by the wayside. I try to be agnostic about technology, 
> and I'd be willing to subcontract a Tesla-approved installer if, in fact, 
> this was the best solution.
> Does anybody have experience using the Powerwall 2.0 in an off grid PV 
> system? Is it AC coupled only? Can it take generator power without barfing? 
> What is the lead time on these?
> Many Thanks,
> Hilton
> -- 
> Hilton Dier III
> Missisquoi River Hydro
> Renewable Energy Design
 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to