I also don't understand requiring 100 amps for an auxillary dwelling. 230.79 requires a minimum service of 100 amps for a single family dwelling, but that is a service requirement, not a requirement for a feeder to another building.  Even 230.79(D) says all other buildings only require a 60 amp service.    I think we'd all like to know where the AHJ is getting these requirements.  Is it local amendments that were added, or is it just a possible misinterpretation?

I suggest possibly reviewing with the AHJ the article 100 definitions of Service (connection to the Utility) and Feeder. Article 230 covers Services and does Not apply to feeders.   The ADU would only need 100 amps if it had its own service meter.

Ray Walters
Remote Solar
303 505-8760

On 4/21/20 10:05 AM, [email protected] wrote:

The voltage drop recommendations in the code are actually not requirements, but recommendations. Some locations make them requirements, but if the AHJ is following the NEC without amendment, the 2% and 3% recommended drops are only recommendations.

---


On 2020-04-20 10:56, Mac Lewis wrote:

This is an example of where  some code requirements bump up against logic.  I believe the AC voltage will be quite usable at the site, just not for code requirements of the AHJ, and it may get pretty low during high usage times.  They make the electrician size it for 100A minimum for an ADU, even though the loads are pretty minimal, and then require <5% VD from the main service entrance.  That is the requirement for the certificate of occupancy.   Luckily, off-grid buildings don't have these requirements at all.  I'm going to size it as an off-grid and probably tie it in at some point in the future.
Thanks for the input.

On Sun, Apr 19, 2020 at 10:20 AM <[email protected] <mailto:[email protected]>> wrote:

    We had a similar situation, and are now feeding a battery bank
    with a pair of 48 V Iota chargers. Iota can run on very low
    voltages. We have one Iota on each leg of the the 120/240 split
    phase to balance the load. It works.

    ---


    On 2020-04-18 21:25, Ray wrote:

        When doing the volt drop calculation, be sure to correct for
        temperature, per the note after table 8, chapter 9 of the
        NEC.  The table values default at 167 deg F (75 C).  An
        underground cable will be operating closer to earth
        temperature.   When I run volt drop for a 4/0 copper cable at
        60 deg F, I'm seeing that you could go over 60 amps and
        maintain a volt drop of 3%.

        Not sure what the requirements for the building are, but that
        exceeds most of my off grid systems.  60+ amps at a final
        voltage of 232 v is almost 14kW. Is there air conditioning? 
        What are the calculated loads for this building?  Is the
        inspector actually calling this a problem?

        I would do a proof of concept: turn every light on in the
        place, along with some typical appliances (hair dryer,
        microwave) hit a circular saw to really make the point, with
        a DMM plugged in.  I found long ago that actual measured volt
        drop was not as bad as Chapter 9 first predicts.


        Ray Walters
        Remote Solar
        303 505-8760

        On 4/18/20 3:41 PM, Darryl Thayer wrote:

            Hi Mac, There are a few questions like is it Al or Cu
            wire, What makes it unusable?
            for Voltage drop, I use Vd=2KIL/CMA for your case the
            unknown is the current.  The installation of an inverter
            with grid support.  Many inverters have this,  you want a
            multimode inverter such as a Schneider, Outback, SolArk
            and I could name at least 4 more.  A normal house will
            run on 30 amps.  So assume 30 amps,
            Vd=2x21.6x30x1100/211600 =6.7 volts
            So if the main house is at 240 Volts the remote house is
            at 233 Volts.  The multimode inverter could be set at
            grid support beyond 30 Amps.  For higher house loads the
            inverter can support up to 30 to 50 amps additional.
            (SolArk is 50 amp) I would add a balancing transformer at
            the end of the line to make the 120 loads balance.  (an
            Autotransformer) such that  120 volts loads are balanced
            and the load is shared between 240-Volt conductors. 
            Based on my customers' experiences I would use AGM LA
            batteries, as I expect low usage of the battery and quick
            recharge, but that is the customer's choice.  I had one
            customer that had 10 years on the float-AGM battery set.

            On Fri, Apr 17, 2020 at 8:15 AM Mac Lewis
            <[email protected] <mailto:[email protected]>> wrote:

                Hi wrenches,
                I've got a architect client with a sub-optimal power
                situation on one of the projects he is working on. 
                I'm running through a couple of scenarios that may
                work.  Its a ADU (accessory dwelling unit) that is
                about 1100' from power.  The farmer had taken it upon
                himself to bury some 4/0 a few years ago to run power
                out there.  Voltage drop is the big issue and its not
                going to pass the AHJ inspection.  We could just
                ditch the grid and go off-grid, but it seems like a
                shame to not tap into the grid resource.  Instead of
                dealing with the voltage drop, I was thinking it may
                make sense to rectify that low AC voltage input and
                parallel a smallish battery bank (size is yet to be
                determined), then use an off-grid inverter to serve
                the loads at good voltage.
                I am looking for feedback on this concept.  What do
                you think?
                Also, are there any recommendations for good quality
                rectifiers with wide input voltage window?
                Thanks in advance for your help
-- Mac Lewis

                "Yo solo sé que no sé nada." -Sócrates

                _______________________________________________
                List sponsored by Redwood Alliance

                List Address: [email protected]
                <mailto:[email protected]>

                Change listserver email address & settings:
                
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                List-Archive:
                
http://www.mail-archive.com/[email protected]/maillist.html

                List rules & etiquette:
                www.re-wrenches.org/etiquette.htm
                <http://www.re-wrenches.org/etiquette.htm>

                Check out or update participant bios:
                www.members.re-wrenches.org
                <http://www.members.re-wrenches.org>


            _______________________________________________
            List sponsored by Redwood Alliance

            List Address:[email protected]  
<mailto:[email protected]>

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

            Check out or update participant bios:
            www.members.re-wrenches.org  <http://www.members.re-wrenches.org>


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


--
Mac Lewis

"Yo solo sé que no sé nada." -Sócrates


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] <mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to