IF OFF grid is how you are sizing it, you might look at the Victron Quattro 5kW 
inverter.  100 A pass thru + AC assist,  45-65 hZ
90-140 input range.
> On Apr 20, 2020, at 10:56 AM, Mac Lewis <[email protected]> wrote:
> 
> This is an example of where  some code requirements bump up against logic.  I 
> believe the AC voltage will be quite usable at the site, just not for code 
> requirements of the AHJ, and it may get pretty low during high usage times.  
> They make the electrician size it for 100A minimum for an ADU, even though 
> the loads are pretty minimal, and then require <5% VD from the main service 
> entrance.  That is the requirement for the certificate of occupancy.  
> 
>   Luckily, off-grid buildings don't have these requirements at all.  I'm 
> going to size it as an off-grid and probably tie it in at some point in the 
> future.
> 
> Thanks for the input.
> 
> On Sun, Apr 19, 2020 at 10:20 AM <[email protected] 
> <mailto:[email protected]>> wrote:
> We had a similar situation, and are now feeding a battery bank with a pair of 
> 48 V Iota chargers. Iota can run on very low voltages. We have one Iota on 
> each leg of the the 120/240 split phase to balance the load. It works.
> 
> ---
>  
> 
> 
> On 2020-04-18 21:25, Ray wrote:
> 
>> When doing the volt drop calculation, be sure to correct for temperature, 
>> per the note after table 8, chapter 9 of the NEC.  The table values default 
>> at 167 deg F (75 C).  An underground cable will be operating closer to earth 
>> temperature.   When I run volt drop for a 4/0 copper cable at 60 deg F, I'm 
>> seeing that you could go over 60 amps and maintain a volt drop of 3%. 
>> 
>> Not sure what the requirements for the building are, but that exceeds most 
>> of my off grid systems.  60+ amps at a final voltage of 232 v is almost 
>> 14kW. Is there air conditioning?  What are the calculated loads for this 
>> building?  Is the inspector actually calling this a problem? 
>> 
>> I would do a proof of concept: turn every light on in the place, along with 
>> some typical appliances (hair dryer, microwave) hit a circular saw to really 
>> make the point, with a DMM plugged in.  I found long ago that actual 
>> measured volt drop was not as bad as Chapter 9 first predicts.
>> 
>> 
>> 
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>> On 4/18/20 3:41 PM, Darryl Thayer wrote:
>>> Hi Mac, There are a few questions like is it Al or Cu wire, What makes it 
>>> unusable?  
>>> for Voltage drop, I use Vd=2KIL/CMA for your case the unknown is the 
>>> current.  The installation of an inverter with grid support.  Many 
>>> inverters have this,  you want a multimode inverter such as a Schneider, 
>>> Outback, SolArk and I could name at least 4 more.  A normal house will run 
>>> on 30 amps.  So assume 30 amps, Vd=2x21.6x30x1100/211600 =6.7 volts
>>> So if the main house is at 240 Volts the remote house is at 233 Volts.  The 
>>> multimode inverter could be set at grid support beyond 30 Amps.  For higher 
>>> house loads the inverter can support up to 30 to 50 amps additional.  
>>> (SolArk is 50 amp) I would add a balancing transformer at the end of the 
>>> line to make the 120 loads balance.  (an Autotransformer) such that  120 
>>> volts loads are balanced and the load is shared between 240-Volt 
>>> conductors.  Based on my customers' experiences I would use AGM LA 
>>> batteries, as I expect low usage of the battery and quick recharge, but 
>>> that is the customer's choice.  I had one customer that had 10 years on the 
>>> float-AGM battery set.    
>>> 
>>> On Fri, Apr 17, 2020 at 8:15 AM Mac Lewis <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>> Hi wrenches,
>>>  
>>> I've got a architect client with a sub-optimal power situation on one of 
>>> the projects he is working on.  I'm running through a couple of scenarios 
>>> that may work.  Its a ADU (accessory dwelling unit) that is about 1100' 
>>> from power.  The farmer had taken it upon himself to bury some 4/0 a few 
>>> years ago to run power out there.  Voltage drop is the big issue and its 
>>> not going to pass the AHJ inspection.  We could just ditch the grid and go 
>>> off-grid, but it seems like a shame to not tap into the grid resource.  
>>> Instead of dealing with the voltage drop, I was thinking it may make sense 
>>> to rectify that low AC voltage input and parallel a smallish battery bank 
>>> (size is yet to be determined), then use an off-grid inverter to serve the 
>>> loads at good voltage.
>>>  
>>> I am looking for feedback on this concept.  What do you think?
>>>  
>>> Also, are there any recommendations for good quality rectifiers with wide 
>>> input voltage window?  
>>>  
>>> Thanks in advance for your help
>>>  
>>> -- 
>>>  
>>>  
>>>  
>>> Mac Lewis
>>> 
>>> "Yo solo sé que no sé nada." -Sócrates
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html 
>>> <http://www.mail-archive.com/[email protected]/maillist.html>
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html 
>>> <http://www.mail-archive.com/[email protected]/maillist.html>
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html 
>> <http://www.mail-archive.com/[email protected]/maillist.html>
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html 
> <http://www.mail-archive.com/[email protected]/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> 
> 
> -- 
> 
> 
> 
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> [email protected] 
> <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>  
>              www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to