When doing the volt drop calculation, be sure to correct for temperature, per the note after table 8, chapter 9 of the NEC. The table values default at 167 deg F (75 C).  An underground cable will be operating closer to earth temperature.   When I run volt drop for a 4/0 copper cable at 60 deg F, I'm seeing that you could go over 60 amps and maintain a volt drop of 3%.

Not sure what the requirements for the building are, but that exceeds most of my off grid systems.  60+ amps at a final voltage of 232 v is almost 14kW. Is there air conditioning?  What are the calculated loads for this building?  Is the inspector actually calling this a problem?

I would do a proof of concept: turn every light on in the place, along with some typical appliances (hair dryer, microwave) hit a circular saw to really make the point, with a DMM plugged in.  I found long ago that actual measured volt drop was not as bad as Chapter 9 first predicts.


Ray Walters
Remote Solar
303 505-8760

On 4/18/20 3:41 PM, Darryl Thayer wrote:
Hi Mac, There are a few questions like is it Al or Cu wire, What makes it unusable? for Voltage drop, I use Vd=2KIL/CMA for your case the unknown is the current.  The installation of an inverter with grid support.  Many inverters have this,  you want a multimode inverter such as a Schneider, Outback, SolArk and I could name at least 4 more.  A normal house will run on 30 amps.  So assume 30 amps, Vd=2x21.6x30x1100/211600 =6.7 volts So if the main house is at 240 Volts the remote house is at 233 Volts.  The multimode inverter could be set at grid support beyond 30 Amps.  For higher house loads the inverter can support up to 30 to 50 amps additional.  (SolArk is 50 amp) I would add a balancing transformer at the end of the line to make the 120 loads balance.  (an Autotransformer) such that  120 volts loads are balanced and the load is shared between 240-Volt conductors. Based on my customers' experiences I would use AGM LA batteries, as I expect low usage of the battery and quick recharge, but that is the customer's choice.  I had one customer that had 10 years on the float-AGM battery set.

On Fri, Apr 17, 2020 at 8:15 AM Mac Lewis <[email protected] <mailto:[email protected]>> wrote:

    Hi wrenches,

    I've got a architect client with a sub-optimal power situation on
    one of the projects he is working on.  I'm running through a
    couple of scenarios that may work.  Its a ADU (accessory dwelling
    unit) that is about 1100' from power.  The farmer had taken it
    upon himself to bury some 4/0 a few years ago to run power out
    there.  Voltage drop is the big issue and its not going to pass
    the AHJ inspection.  We could just ditch the grid and go off-grid,
    but it seems like a shame to not tap into the grid resource. 
    Instead of dealing with the voltage drop, I was thinking it may
    make sense to rectify that low AC voltage input and parallel a
    smallish battery bank (size is yet to be determined), then use an
    off-grid inverter to serve the loads at good voltage.

    I am looking for feedback on this concept.  What do you think?

    Also, are there any recommendations for good quality rectifiers
    with wide input voltage window?

    Thanks in advance for your help

--


    Mac Lewis

    *

    "Yo solo sé que no sé nada." -Sócrates

    *
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to