I should note that if you are on NEC 2014 the 60 OCPD is not the correct
figure to use in the 120% rule. It would be 125% of the Inverter Output
Circuit rated current.

It's probably a moot point in this case, but it is an important distinction.



On Thu, May 9, 2019 at 3:06 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:

> Calc loads and see if you can replace the main with a 175A breaker if it
> exists, or even 150A. This main breaker downsizing has been a go-to
> exercise for us for existing meter-mains. It's frustrating being limited to
> 40A on the load side. That doesn't even get to 10kWdc with Enphase IQ7+,
> which is becoming a pretty small system these days around here. I tell
> every home builder I see to avoid meter-main combos but they keep putting
> them in.
>
> Sadly our utility accepts NONE of the "solar ready" panels on the market.
> That's another snag we run into.
>
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
>
>
> On Thu, May 9, 2019 at 2:50 PM Sarah Ray <sarahm...@gmail.com> wrote:
>
>> Hi Wrenches,
>>
>> Does anyone have a recommendation for a meter main with a 225A bus and
>> pass through lugs? Eaton and SquareD make meter mains with a 225A bus, but
>> no pass-through lugs, so they don't work well for most retrofit
>> applications.
>>
>> We would like to connect our inverter output to a feeder that is fed by
>> the pass through lugs in the existing 200A meter main (which is located at
>> another building.) The inverter output has a 60A OCPD, so the 200A meter
>> main bus is not sufficient.
>>
>> Any suggestions you have would be greatly appreciated!
>>
>> Thank you,
>>
>> Sarah Ray
>>
>> OnSite Energy, Inc.
>> 619 N Church Ave, Suite 4
>> Bozeman, MT 59715
>> Cell: (406) 579-6512
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/d413296e828a0e208b2d0ff5432ecc5b908495fe?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=64bdd88fc0bbb783>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> <https://mailtrack.io/trace/link/45219de793b9098a8d5ffcc67ca9f44b071c0d48?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=6149e0d8a0774b09>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/8be75159e5a0c4a3889df5150d9b70bf4ea0d604?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=54b4c005f0a209b3>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/cd63071172203220e2b175dbbda003eef34fdc00?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=48d52634fc25b5da>
>>
>>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to