William,

It seems this question needs to be addressed: What is the intended meaning of 
“installed in one system” in 2014? If you have separate “systems”, they should 
not be governed by 705.12. So, at what point does a “system” begin and end? PV 
modules to the disconnect? ...to the load panel? ...to the service entrance?

Larry


On Feb 25, 2019, at 10:42 PM, William Miller <will...@millersolar.com> wrote:

August:
 
The 2014 code, which the AHJ for this project is using, states the following:
 
(1) Dedicated Overcurrent and Disconnect. The source
interconnection of one or more inverters installed in one
system shall be made at a dedicated circuit breaker or fusible
disconnecting means.
 
Note that the language says, “The source interconnection…” (singular), and “at 
a dedicated circuit breaker…”(again singular).  This makes it obvious to me 
that the language says that the outputs of multiple inverters need to be 
aggregated and connected via one OCPD.  I think the other wrenches missed this 
point.
 
Your input is valuable by contrasting the language of the 2014 code with that 
of the 2017 version.  The inclusion of the phrase “Each source…” in the 2017 
code completely changes the meaning.  Some AHJs will look to future code 
versions for clarity even if they are not yet adopted.  I think this is a good 
thing, and I really appreciate you bringing up the new language.
 
The article from AEIA magazine ratifies the conclusion I drew from the 2014 
code.  Fortunately the AHJ is misinterpreting the section to allow the more 
liberal interpretation, the one that the 2017 code reflects.  I find it best to 
contact the plan checker directly, which I did, and we are approved for 
multiple OCPDs.  By the way, I think that article is well written and I have 
book marked it.
 
I don’t know if the 2014 language was a mistake corrected in 2107, or what the 
thinking was of the authors.  Regardless, we live by the language, not the 
intent.
 
Thank you as well to all who responded.
 
William Miller
 
 
 
 
From: August Goers [mailto:aug...@luminalt.com <mailto:aug...@luminalt.com>] 
Sent: Monday, February 25, 2019 9:07 AM
To: William Miller; RE-wrenches
Subject: Re: [RE-wrenches] Multiple inverters
 
Hi William - 
 
In this case, it is helpful to look forward to the 2017 NEC for guidance:
 
<image001.png>
 
I believe it's perfectly fine to have multiple inverter breakers in your main.
 
August
Luminalt
 
 
On Mon, Feb 25, 2019 at 8:42 AM William Miller <will...@millersolar.com 
<mailto:will...@millersolar.com>> wrote:
> Friends:
>  
> I have an NEC code question on an upcoming project.  It is a home that has an 
> existing 8 kW ground-mounted grid-tied system.  The owner wants to add 
> another 10 kW of grid-tied PV.  My question is about 705.12, point of 
> connection.  Specifically section (D)(1).  That section states: 
>  
> The source interconnection of one or more inverters installed in one system 
> shall be made at a dedicated circuit breaker or fusible disconnecting means.
>  
> So if there are going to be two inverters on premise, do the outputs have to 
> be aggregated to connect via one circuit breaker?  This might be difficult to 
> do as the exiting inverter is connected via a different sub-panel than the 
> one that is planned to receive the new inverter output.
>  
> This article 
> <https://iaeimagazine.org/magazine/2014/01/16/load-side-pv-connections/> 
> addresses the question.
>  
> I would be very grateful if any of you can share any experience you might 
> have in interpreting this section of the code.
>  
> Thanks in advance.
>  
> William
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org 
> <http://www.members.re-wrenches.org/>_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to