SolarEdge inverters have an export control function if you install an external 
meter to them. They can be programmed to prevent any net energy export, or to 
limit that export to a specific amount (if you had a large system with a 
relatively smaller utility transformer for example).

 

Here is a link to their system: 
http://www.solaredge.com/sites/default/files/export_limitation_application_note_NA.pdf
 

 

It would limit export power in real time, not energy over time, so if the dump 
load is to prevent a net monthly export of kWh… then I have no clue.

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Kristopher Schmid
Sent: Wednesday, September 07, 2016 2:31 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Grid tie with dump load?

 

REWs,

I have a client that asked me if i can install a battery free grid tied system 
and have a dump load activate when it is overproducing.  I am at a loss, here.  
Anyone have ideas?  A CT on the line side that would activate a relay while 
current is flowing to the utility?

Thanks,

Kris



-- 

Shine On!

Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
www.legacysolar.com <http://www.legacysolar.com> 
715-653-4295
NABCEP Certified PV Installer
Licensed Wisconsin Master Electrician
BSEE

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to